Glow Worm Flexicom 15HX - F25 roughly every 24 hrs
Hi,
I have a Glowworm Flexicom 15HX which I am getting an F25 (Circulation fault) about once a day. Once it's reset it seems to work ok for about 24 hrs before the fault arises again.
I've tried bleeding all of the radiators and none of them seemed to have any air in them. Is there anywhere else I should be looking to bleed it? I've looked at the manual and googled around but haven't found anything helpful.
Grateful for any help with fixing this.
Thanks,
Jim
I have a Glowworm Flexicom 15HX which I am getting an F25 (Circulation fault) about once a day. Once it's reset it seems to work ok for about 24 hrs before the fault arises again.
I've tried bleeding all of the radiators and none of them seemed to have any air in them. Is there anywhere else I should be looking to bleed it? I've looked at the manual and googled around but haven't found anything helpful.
Grateful for any help with fixing this.
Thanks,
Jim
- thescruff
- Senior Member
- Posts: 49685
- Joined: Mon Mar 10, 2008 12:46 am
- Location: Bath
- Has thanked: 360 times
- Been thanked: 3735 times
- moderator2
- UHM Super Moderator
- Posts: 4569
- Joined: Fri Jan 27, 2006 10:54 pm
- Has thanked: 155 times
- Been thanked: 566 times
- thescruff
- Senior Member
- Posts: 49685
- Joined: Mon Mar 10, 2008 12:46 am
- Location: Bath
- Has thanked: 360 times
- Been thanked: 3735 times
Re: Glow Worm Flexicom 15HX - F25 roughly every 24 hrs
You'll probably hear it running or feel it if you stick a hand on it. (May be very Hot)
What motorized valves do you have.
Does it fault in the hot water mode or heating mode, or both
Perhaps a pic or 2 around the cylinder
What motorized valves do you have.
Does it fault in the hot water mode or heating mode, or both
Perhaps a pic or 2 around the cylinder
-
- Newly registered Member
- Posts: 10
- Joined: Thu Jan 22, 2015 5:34 pm
- Has thanked: 1 time
- Been thanked: 0
Re: Glow Worm Flexicom 15HX - F25 roughly every 24 hrs
The pump feels quite hot now. The boiler has stayed on this evening, so haven't been able to check what's happening when it faults.
The valve is a Honeywell V4043H 1056
I think it's the heating mode that's the problem as it seems to go wrong when the heating turns back on (either in the evening or morning). Hot water is on constant.
A few photos in case it helps...
The valve is a Honeywell V4043H 1056
I think it's the heating mode that's the problem as it seems to go wrong when the heating turns back on (either in the evening or morning). Hot water is on constant.
A few photos in case it helps...
- Razor
- Senior Member
- Posts: 8760
- Joined: Wed Nov 14, 2007 10:21 pm
- Location: Northampton
- Has thanked: 483 times
- Been thanked: 1251 times
Re: Glow Worm Flexicom 15HX - F25 roughly every 24 hrs
The pictures aren't clear enough really. We need to know what happens to the pipe under the pump. It goes to an upside down tee which splits to go to two, two port valves (the silver boxes). Are there any other pipes tee'd off between the pump and the valves?
There isn't a bypass in your pictures. That would cause overheating when both valves are shut
BTW
There isn't a bypass in your pictures. That would cause overheating when both valves are shut
BTW
I think I'll take two chickens...
- thescruff
- Senior Member
- Posts: 49685
- Joined: Mon Mar 10, 2008 12:46 am
- Location: Bath
- Has thanked: 360 times
- Been thanked: 3735 times
Re: Glow Worm Flexicom 15HX - F25 roughly every 24 hrs
Yes you need to zoom right out so we have more detail
Sent from my SM-G900F using Tapatalk
Sent from my SM-G900F using Tapatalk
- thescruff
- Senior Member
- Posts: 49685
- Joined: Mon Mar 10, 2008 12:46 am
- Location: Bath
- Has thanked: 360 times
- Been thanked: 3735 times
Re: Glow Worm Flexicom 15HX - F25 roughly every 24 hrs
The red plastic knob in the 2nd pic is there a name on it anywhere.
Looking like the MV for the heating is playing up if it works ok in the dhw mode. Thats the lower one
Looking like the MV for the heating is playing up if it works ok in the dhw mode. Thats the lower one
- thescruff
- Senior Member
- Posts: 49685
- Joined: Mon Mar 10, 2008 12:46 am
- Location: Bath
- Has thanked: 360 times
- Been thanked: 3735 times
Re: Glow Worm Flexicom 15HX - F25 roughly every 24 hrs
You could remove the actuator and check the shaft is turning 1/4turn either way without resistance or use of tools
-
- Newly registered Member
- Posts: 10
- Joined: Thu Jan 22, 2015 5:34 pm
- Has thanked: 1 time
- Been thanked: 0
Re: Glow Worm Flexicom 15HX - F25 roughly every 24 hrs
I've not yet removed the actuator, but have just checked the manual lever on the lower MV and it feels stiff. The lever on the other MV feels loose when the power is on.
Is this likely to indicate some issue with the lower MV, before I try anything more drastic like pulling it apart?!
Also, the boiler had an F25 again during the day. I note that when I reset it the temperature reading quickly rises to 83, but every so often it drops to 40ish and quickly climbs back to 83 again.
Is this likely to indicate some issue with the lower MV, before I try anything more drastic like pulling it apart?!
Also, the boiler had an F25 again during the day. I note that when I reset it the temperature reading quickly rises to 83, but every so often it drops to 40ish and quickly climbs back to 83 again.
- thescruff
- Senior Member
- Posts: 49685
- Joined: Mon Mar 10, 2008 12:46 am
- Location: Bath
- Has thanked: 360 times
- Been thanked: 3735 times
Re: Glow Worm Flexicom 15HX - F25 roughly every 24 hrs
When the htg is on there should be no resistance on the lever
Sent from my SM-G900F using Tapatalk