How far can fuse box be from meter?
- Has thanked: 39 times
- Been thanked: 3 times
my daughters 1978 house needs rewiring.
How far can the new fuse box be from the electric meter?
We want it to be perhaps 3 or 4 meters away so it is out of the way whilst still being easily accessible.
thank you glassescase
- Someone-Else
- Has thanked: 47 times
- Been thanked: 2601 times
Re: How far can fuse box be from meter?
I believe you will find its 3M
- glassescase
thank you for a quick reply, 3m seems enough to get it out of the way.
thank you
glassescase
thank you
glassescase
- Has thanked: 105 times
- Been thanked: 880 times
if its in the 2-3m range you may need to go up to 25mm tails rather the 16mm - Unless you fit a isolator with in 3m of the meter and run a suitable cable (iirc swa or mineral cable if it complies still)
Just looked it up
4.6 Meter Tails
Standard 25mm2 copper double-insulated conductors (meter tails) from the meter to the cut-out shall be provided and installed by the appointed meter operator.
Standard 25mm2 copper double-insulated conductors shall be provided and installed by the customer from the consumer unit for connection by the meter operator into the outgoing (load side) of the meter.
BS 7671 Regulation 433.2.2 allows a maximum distance of three metres between overload protection devices and their source, therefore the customer shall provide and install an intermediate switch fuse or isolating switch if the distance between the meter and consumer unit is greater than three metres.
The customer should seek professional electrical advice to determine the protection equipment that is appropriate for the customer given the impedance at the cut-out and the design of their installation as UK Power Networks is unable to advise on these aspects.
Meter tails shall not be installed or run inside the cavity wall of a building other than passing directly through the wall.
Tri-rated cables shall not be terminated onto UK Power Networks equipment.
4.6 Meter Tails
- ericmark
- Has thanked: 118 times
- Been thanked: 785 times
Many flats have the meters near entrance and consumer unit in flat up the stairs, however there is normally a limit of 3 meters when using standard tails. However moving a consumer unit would need notifying so down to electrician or inspector what you can have.
thank you I will be using a professional to go from meter to fuse box. 3m is plenty.
There are two sets of tails, one to the fuse box and another set to a single fuse/isolator for the shower.
thank you for the advice, it is appreciated
glassescase
glassescase
- Approved Electrician
- Has thanked: 225 times
- Been thanked: 664 times
ericmark wrote:Many flats have the meters near entrance and consumer unit in flat up the stairs, however there is normally a limit of 3 meters when using standard tails. However moving a consumer unit would need notifying so down to electrician or inspector what you can have.
That will be 3 metres and not 3 meters (unless it is 3 phase supply)
- Someone-Else
OnlyMe wrote:That will be 3 metres and not 3 meters (unless it is 3 phase supply)