Can't turn heating off
Just moved house and the boiler had been installed within last few months.
Hot water is on a program but when it runs the central heating comes on too. Figured it would be the diverter valve and funnily enough it was in the middle position. Now set to auto mostly all heaters don't come on apart from one which is in the hallway and doesnt have a Thermostatic valve. Why would this one be on with only the hot water running and not the rest?
Sent from my SM-G950F using Tapatalk
Hot water is on a program but when it runs the central heating comes on too. Figured it would be the diverter valve and funnily enough it was in the middle position. Now set to auto mostly all heaters don't come on apart from one which is in the hallway and doesnt have a Thermostatic valve. Why would this one be on with only the hot water running and not the rest?
Sent from my SM-G950F using Tapatalk
- moderator2
- UHM Super Moderator
- Posts: 4569
- Joined: Fri Jan 27, 2006 10:54 pm
- Has thanked: 155 times
- Been thanked: 566 times
- Someone-Else
- Senior Member
- Posts: 14638
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 47 times
- Been thanked: 2578 times
Re: Can't turn heating off
Could it be that the TRV's have all closed, so the water runs the only way it can..........through the rad with no TRV.
As I understand it you are supposed to have one rad with no TRV, but its usually the bathroom one. (Don't worry its not in your case)
What happens if you "open" all the TRV's ?
As I understand it you are supposed to have one rad with no TRV, but its usually the bathroom one. (Don't worry its not in your case)
What happens if you "open" all the TRV's ?
Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
- kevinsmbuk
- Senior Member
- Posts: 793
- Joined: Thu Feb 27, 2014 5:09 pm
- Location: Essex
- Has thanked: 212 times
- Been thanked: 27 times
Re: Can't turn heating off
It's a baxi boiler pic attached. It's a standard ch system not combi
Sent from my SM-G950F using Tapatalk
Sent from my SM-G950F using Tapatalk
- kevinsmbuk
- Senior Member
- Posts: 793
- Joined: Thu Feb 27, 2014 5:09 pm
- Location: Essex
- Has thanked: 212 times
- Been thanked: 27 times
Re: Can't turn heating off
The 3 port valve was in the middle but i moved it to auto. But the hallway rad still comes on with the hot water. The thermostat with the lcd the owner said controls the temp of the rad in the hallway, is that correct?gas4you wrote:My first thought would be the heating zone valve or 3 port valve, is stuck mid position, or letting by.
Sent from my SM-G950F using Tapatalk
-
- Senior Member
- Posts: 7203
- Joined: Mon Apr 13, 2009 7:03 pm
- Has thanked: 419 times
- Been thanked: 900 times
Re: Can't turn heating off
Not quite, the thermostat in the hall controls the air temperature in the hall, not the actual temperature of what the radiator feels to the touch, if that is what you meant.
When the hall thermostat goes off, all the radiators will/should be off.
When it is on then they all should be on and then individually controlled by each thermostatic valve on them.
Did you actually hear the valve go back to HW position and is the man lever 'loose' or 'tight' back when on HW only?
When the hall thermostat goes off, all the radiators will/should be off.
When it is on then they all should be on and then individually controlled by each thermostatic valve on them.
Did you actually hear the valve go back to HW position and is the man lever 'loose' or 'tight' back when on HW only?
- These users thanked the author gas4you for the post:
- kevinsmbuk
- Rating: 7.14%
Dave
- kevinsmbuk
- Senior Member
- Posts: 793
- Joined: Thu Feb 27, 2014 5:09 pm
- Location: Essex
- Has thanked: 212 times
- Been thanked: 27 times
Re: Can't turn heating off
Don't quote me on this, but I think it's working ok now. The radiator in the hall doesn't seem to come on with the hot water anymore, we haven't really done anything different since.
Although my partner did comment the lounge rad was getting hot when the water was on! Will keep an eye on it and repost if the issue continues, but thankyou for all your help so far
Although my partner did comment the lounge rad was getting hot when the water was on! Will keep an eye on it and repost if the issue continues, but thankyou for all your help so far
gas4you wrote:Not quite, the thermostat in the hall controls the air temperature in the hall, not the actual temperature of what the radiator feels to the touch, if that is what you meant.
When the hall thermostat goes off, all the radiators will/should be off.
When it is on then they all should be on and then individually controlled by each thermostatic valve on them.
Did you actually hear the valve go back to HW position and is the man lever 'loose' or 'tight' back when on HW only?