Changing from / to a dimmer light switch
All electrical lighting questions in here please. Including outside lighting and light switch / dimmer questions.
Moderator: Moderators
Navbloke
- Andrew
- Senior Member
- Posts: 965
- Joined: Wed Aug 16, 2006 4:38 pm
- Location: Sunny Southend!
- Has thanked: 3 times
- Been thanked: 3 times
Here's a question which relates to this post: Why is it that dimmers are rated in watts (on the packaging at Homebase!) but light switches just say 10amp?
Say I had three hundred-watt bulbs running off one switch (which I don't), I take it that that 250w dimmer should not be used. What about the normal 10amp switch?
Does that question even make any sense? You can guess I'm not yet a qualified sparky.
Also, the 250w dimmer I've just got has connections for live and "switched live". Thats got to be the black cable / neutral, but why is it called a switched live and do I need to put sleeving on to indicate that? If so, would a piece of electrical tape suffice?
One more question - I've just taken the dimmer out the packet, and it makes a definite clicking noise when turning it. Is that usual, or should they be silent? The one that was already in the flat when I moved in is quiet. It doesn't sound "broken", just noisy.
Cheers dudes!
Say I had three hundred-watt bulbs running off one switch (which I don't), I take it that that 250w dimmer should not be used. What about the normal 10amp switch?
Does that question even make any sense? You can guess I'm not yet a qualified sparky.
Also, the 250w dimmer I've just got has connections for live and "switched live". Thats got to be the black cable / neutral, but why is it called a switched live and do I need to put sleeving on to indicate that? If so, would a piece of electrical tape suffice?
One more question - I've just taken the dimmer out the packet, and it makes a definite clicking noise when turning it. Is that usual, or should they be silent? The one that was already in the flat when I moved in is quiet. It doesn't sound "broken", just noisy.

Cheers dudes!
Andrew
- sparkydude
- Senior Member
- Posts: 2253
- Joined: Sat Aug 13, 2005 7:11 pm
- Location: Staffordshire
- Has thanked: 2 times
- Been thanked: 149 times
Post by sparkydude »
Question 1
As the dimmer is an electronic device it has various component parts that are rated for a specific loading, and size, as if for example you wanted a 1kw dimmer the thing is huge, normally the size of a double socket , this is also because to dim a lamp the electronics need to dissipate the heat generated by lowering the voltage to the lamp. The normal switch would be fine as it is simply a set of contacts that are broken and made, and these contacts can take the higher currents hence rated for 10A
Question 2
It is called a switched live as thats what it is, a live that is switched, and not a permanent live such as you connect to the common of the dimmer/switch. Yes the black or now blue , needs to be sleeved/taped sleeving is best as it wil not fall off when the adhesive on insulation tape dries it normally falls off.
Question 3
Nothing wrong with your dimmer, some click some push , some are rotary on off, some are push on off, maafacturers vary
Nick
As the dimmer is an electronic device it has various component parts that are rated for a specific loading, and size, as if for example you wanted a 1kw dimmer the thing is huge, normally the size of a double socket , this is also because to dim a lamp the electronics need to dissipate the heat generated by lowering the voltage to the lamp. The normal switch would be fine as it is simply a set of contacts that are broken and made, and these contacts can take the higher currents hence rated for 10A
Question 2
It is called a switched live as thats what it is, a live that is switched, and not a permanent live such as you connect to the common of the dimmer/switch. Yes the black or now blue , needs to be sleeved/taped sleeving is best as it wil not fall off when the adhesive on insulation tape dries it normally falls off.
Question 3
Nothing wrong with your dimmer, some click some push , some are rotary on off, some are push on off, maafacturers vary
Nick
If it isnt broke dont bloody touch it until it bloody well is and if it is broke then make drawing of the connections before you remove the broken one and replace with a new one LoL
sparkydude
- Andrew
- Senior Member
- Posts: 965
- Joined: Wed Aug 16, 2006 4:38 pm
- Location: Sunny Southend!
- Has thanked: 3 times
- Been thanked: 3 times
Sorry to drag up such an old thread, but I just need a little piece of clarification:
I know that metal light switches need a joining piece of earth wire from the metal box to the switch, in addition to the cable earth terminating at one of these two places. However, does it matter if you use the core from either 1mm or 1.5mm twin and earth to do this, or should I just cover myself and go with 1.5mm? (for example, what if the circuit is 1mm cable?).
Also, for both sockets and switches - if the back box is plastic (ala drywall box) but the switch / socket is metal, it's okay just to terminate the earth onto the plate and nothing more (obivous I guess, but always best to ask!).
Many thanks for your help and support.
I know that metal light switches need a joining piece of earth wire from the metal box to the switch, in addition to the cable earth terminating at one of these two places. However, does it matter if you use the core from either 1mm or 1.5mm twin and earth to do this, or should I just cover myself and go with 1.5mm? (for example, what if the circuit is 1mm cable?).
Also, for both sockets and switches - if the back box is plastic (ala drywall box) but the switch / socket is metal, it's okay just to terminate the earth onto the plate and nothing more (obivous I guess, but always best to ask!).
Many thanks for your help and support.

Andrew
- Jaeger_S2k
- Pro Handyman
- Posts: 3423
- Joined: Sun Nov 19, 2006 4:31 pm
- Location: North West, England, United Kingdom
- Has thanked: 20 times
- Been thanked: 27 times
Post by Jaeger_S2k »
The 'best practice' is to earth with the same.
An earth is better than no earth!
Your guess was correct, earth to the switch.
An earth is better than no earth!
Your guess was correct, earth to the switch.

Jaeger.
Senior Member doesn't mean I'm OLD!
Senior Member doesn't mean I'm OLD!
Jaeger_S2k
Andrew
- Jaeger_S2k
- Pro Handyman
- Posts: 3423
- Joined: Sun Nov 19, 2006 4:31 pm
- Location: North West, England, United Kingdom
- Has thanked: 20 times
- Been thanked: 27 times
Post by Jaeger_S2k »
WARNING - ANSWER TO STUPID QUESTION FOLLOWS.......
One is .5mm squared bigger than the other!
One is .5mm squared bigger than the other!

Jaeger.
Senior Member doesn't mean I'm OLD!
Senior Member doesn't mean I'm OLD!
Jaeger_S2k
Stoday
- Jaeger_S2k
- Pro Handyman
- Posts: 3423
- Joined: Sun Nov 19, 2006 4:31 pm
- Location: North West, England, United Kingdom
- Has thanked: 20 times
- Been thanked: 27 times
Post by Jaeger_S2k »
That's what I meant 
the square root of the thingy

the square root of the thingy

Jaeger.
Senior Member doesn't mean I'm OLD!
Senior Member doesn't mean I'm OLD!
Jaeger_S2k
- Jaeger_S2k
- Pro Handyman
- Posts: 3423
- Joined: Sun Nov 19, 2006 4:31 pm
- Location: North West, England, United Kingdom
- Has thanked: 20 times
- Been thanked: 27 times
Post by Jaeger_S2k »
Yeah, but which one?Stoday wrote:WARNING - ANSWER TO A STUPID ANSWER FOLLOWS
The 1.5mm means 1.5 square mm - it's not the diameter. So one is the square root of 0.5sq mm bigger than the other.Jaeger_S2k wrote:WARNING - ANSWER TO STUPID QUESTION FOLLOWS.......
One is .5mm squared bigger than the other!

Jaeger.
Senior Member doesn't mean I'm OLD!
Senior Member doesn't mean I'm OLD!
Jaeger_S2k
Jump to
- Ultimate Handyman DIY forum
- ↳ Welcome to the Ultimate Handyman DIY Forum
- WELCOME
- ↳ WELCOME
- ↳ About the forums
- UltimateHandyman Discounts
- ↳ Ultimatehandyman Discounts
- ULTIMATE HANDYMAN COMPETITIONS
- ↳ UHM Forum competitions
- SHOW CASE- A place to show us your work
- ↳ Show Case Gallery
- ↳ Rogues Gallery
- TOOL FORUM
- ↳ Power Tool Reviews
- ↳ Bosch
- ↳ budget power tools
- ↳ Dewalt
- ↳ Festool
- ↳ Hikoki/Hitachi
- ↳ Makita
- ↳ Metabo
- ↳ Milwaukee
- ↳ Ryobi
- ↳ Tool Talk
- ↳ Bargain Tools
- ↳ Hand tool reviews
- ↳ Power Tool Manuals
- ↳ Bosch
- ↳ Dolmar
- ↳ ELEKTRA BECKUM
- ↳ Hitachi
- ↳ Husqvarna
- ↳ Jonsered
- ↳ Makita
- ↳ Stihl
- Other DIY
- ↳ Computers
- ↳ communications and broadband
- ↳ Gardeners World
- ↳ Money Saving
- ↳ Vehicle maintenance & Repair
- ↳ Energy Saving
- DIY Forum/Home improvement
- ↳ General DIY forum
- ↳ Acrylic Forum
- ↳ DIY Disasters
- ↳ Stoves
- ↳ Building Forum
- ↳ Carpentry/Joinery Forum
- ↳ Kitchen Fitting
- ↳ Damp Proofing and Remedial problems
- ↳ Electric Forum UK
- ↳ Lighting
- ↳ Alarm Manuals
- ↳ Painting & Decorating Forum
- ↳ Plastering Forum
- ↳ Plumbing Forum
- ↳ Central Heating & Boilers
- ↳ Boiler Manuals
- ↳ Alpha
- ↳ Ariston
- ↳ ATAG
- ↳ Atmos
- ↳ Baxi
- ↳ Biasi
- ↳ Broag
- ↳ Chaffoteux
- ↳ Ferroli
- ↳ Glow-worm
- ↳ Halstead
- ↳ Ideal
- ↳ Intergas
- ↳ Keston
- ↳ Myson
- ↳ Potterton
- ↳ Protherm
- ↳ Ravenheat
- ↳ Saunier Duval
- ↳ Sime
- ↳ Thorn
- ↳ Vaillant
- ↳ Viessmann
- ↳ Vokera
- ↳ warmflow
- ↳ Worcester Bosch
- ↳ Shower Manuals
- ↳ Tiling Forum
- ↳ Metalworking Forum
- General
- ↳ The Lounge
- ↳ The games corner
- ↳ The Grumpy corner
- ↳ The Sport corner
- ↳ The Cookery corner
- ↳ The Music Corner
- ↳ BUY - SELL - FREE