Radial or badly wired ring?
Hello,
The situation:
1. Double socket wired with two cable runs via conduit into the floor, but ALSO has a third cable run (surface mounted, this time) running to a series of single socket, single socket, double socket- where it terminates.
2. The floor is solid- I can't examine to see where the conduit cables go.
3. The cables are 2.5mm T&E and serviced by a 30A TYPE 2 MCB switch at the Consumer Unit.
Is this a Radial circuit or a badly wired ring circuit? A ring circuit should presumably only allow one spur but a radial would use 4mm cable, right?
Any help would be much appreciated.
The situation:
1. Double socket wired with two cable runs via conduit into the floor, but ALSO has a third cable run (surface mounted, this time) running to a series of single socket, single socket, double socket- where it terminates.
2. The floor is solid- I can't examine to see where the conduit cables go.
3. The cables are 2.5mm T&E and serviced by a 30A TYPE 2 MCB switch at the Consumer Unit.
Is this a Radial circuit or a badly wired ring circuit? A ring circuit should presumably only allow one spur but a radial would use 4mm cable, right?
Any help would be much appreciated.
-
- Senior Member
- Posts: 376
- Joined: Sun Jul 17, 2005 11:38 am
- Location: Newcastle
- Has thanked: 0
- Been thanked: 0
- ultimatehandyman
- Site Admin
- Posts: 24425
- Joined: Sat Jul 16, 2005 7:06 pm
- Location: Darwen, Lancashire
- Has thanked: 1012 times
- Been thanked: 918 times
Sometimes when you start looking you find all kinds of unbelievable things especially with electrics and plumbing!
I once went out with a girl that had an electric shower in her bathroom, but it did not work!
She asked if I would take a look at it, and so I did.
Her previus ex-boyfriend had wired it up using 2.5mm twin core and earth and had connected it to the lighting circuit in the loft space ?
I once went out with a girl that had an electric shower in her bathroom, but it did not work!
She asked if I would take a look at it, and so I did.
Her previus ex-boyfriend had wired it up using 2.5mm twin core and earth and had connected it to the lighting circuit in the loft space ?
-
- Gas/Heating Expert
- Posts: 4382
- Joined: Mon Jan 16, 2006 9:40 pm
- Location: Bournemouth
- Has thanked: 0
- Been thanked: 9 times
- ultimatehandyman
- Site Admin
- Posts: 24425
- Joined: Sat Jul 16, 2005 7:06 pm
- Location: Darwen, Lancashire
- Has thanked: 1012 times
- Been thanked: 918 times
-
- Electrician
- Posts: 272
- Joined: Mon Jan 16, 2006 10:02 pm
- Location: Darlington
- Has thanked: 0
- Been thanked: 0
- Contact:
- Gadget
- Jack Of All Trades
- Posts: 8004
- Joined: Sun Dec 18, 2005 9:23 pm
- Location: Whitley Bay
- Has thanked: 344 times
- Been thanked: 342 times
Jesus [xxxxing] hell....(censored by the moderator)...ultimatehandyman wrote:Sometimes when you start looking you find all kinds of unbelievable things especially with electrics and plumbing!
I once went out with a girl that had an electric shower in her bathroom, but it did not work!
She asked if I would take a look at it, and so I did.
Her previus ex-boyfriend had wired it up using 2.5mm twin core and earth and had connected it to the lighting circuit in the loft space ?
By eck! ©
-
- Gas/Heating Expert
- Posts: 4382
- Joined: Mon Jan 16, 2006 9:40 pm
- Location: Bournemouth
- Has thanked: 0
- Been thanked: 9 times
-
- Electrician
- Posts: 272
- Joined: Mon Jan 16, 2006 10:02 pm
- Location: Darlington
- Has thanked: 0
- Been thanked: 0
- Contact:
Yep that will do. Okay no high load items but it's to protect the cable just in case.jclloydy wrote:Gadget- just to clarify:
Run the original double socket to a 13A FCU, then to series of single, single and double socket, where it terminates.
There will be two computers running off of the chain, but no high load items.
Many thanks.
Somebody could plug in convector heaters, paint strippers or the light and cause all sorts of trouble so best to safe than sorry!
-