Radial or badly wired ring?

Post by jclloydy »

Hello,

The situation:
1. Double socket wired with two cable runs via conduit into the floor, but ALSO has a third cable run (surface mounted, this time) running to a series of single socket, single socket, double socket- where it terminates.

2. The floor is solid- I can't examine to see where the conduit cables go.

3. The cables are 2.5mm T&E and serviced by a 30A TYPE 2 MCB switch at the Consumer Unit.

Is this a Radial circuit or a badly wired ring circuit? A ring circuit should presumably only allow one spur but a radial would use 4mm cable, right?

Any help would be much appreciated.
honeymonster
Senior Member
Posts: 376
Joined: Sun Jul 17, 2005 11:38 am
Location: Newcastle
Has thanked: 0
Been thanked: 0

Post by honeymonster »

Sounds like a badly wired radial citcuit to me, the "1. Double socket wired with two cable runs via conduit into the floor", does one of these cables run back to the CU or does it run to another socket or sockets?


It sounds like a right balls up :shock:
jclloydy
Newly registered Member
Posts: 17
Joined: Wed Oct 04, 2006 3:41 pm
Has thanked: 0
Been thanked: 0

Post by jclloydy »

The two cables from the socket run into a solid concrete floor, so I cannot tell where they end up. There are other sockets run by the same MCB but they are a fair distance away. Which is what confused me.
User avatar
ultimatehandyman
Site Admin
Posts: 24425
Joined: Sat Jul 16, 2005 7:06 pm
Location: Darwen, Lancashire
Has thanked: 1012 times
Been thanked: 918 times

Post by ultimatehandyman »

Sometimes when you start looking you find all kinds of unbelievable things especially with electrics and plumbing!

I once went out with a girl that had an electric shower in her bathroom, but it did not work!

She asked if I would take a look at it, and so I did.

Her previus ex-boyfriend had wired it up using 2.5mm twin core and earth and had connected it to the lighting circuit in the loft space :??
Hinton Heating
Gas/Heating Expert
Posts: 4382
Joined: Mon Jan 16, 2006 9:40 pm
Location: Bournemouth
Has thanked: 0
Been thanked: 9 times

Post by Hinton Heating »

You'd say anything to slag off an ex boyfriend! :lol:
User avatar
ultimatehandyman
Site Admin
Posts: 24425
Joined: Sat Jul 16, 2005 7:06 pm
Location: Darwen, Lancashire
Has thanked: 1012 times
Been thanked: 918 times

Post by ultimatehandyman »

:bs:





:lol:
markysparky
Electrician
Posts: 272
Joined: Mon Jan 16, 2006 10:02 pm
Location: Darlington
Has thanked: 0
Been thanked: 0
Contact:

Post by markysparky »

Agreed,

Sounds like a badly installed radial. If your worried about it you could have the spur on a 13 amp fused spur to protect the cable from overload. This is perfectly fine and is an easy way of sorting these sorts of problems out.
User avatar
Gadget
Jack Of All Trades
Posts: 8004
Joined: Sun Dec 18, 2005 9:23 pm
Location: Whitley Bay
Has thanked: 344 times
Been thanked: 342 times

Post by Gadget »

ultimatehandyman wrote:Sometimes when you start looking you find all kinds of unbelievable things especially with electrics and plumbing!

I once went out with a girl that had an electric shower in her bathroom, but it did not work!

She asked if I would take a look at it, and so I did.

Her previus ex-boyfriend had wired it up using 2.5mm twin core and earth and had connected it to the lighting circuit in the loft space :??
Jesus [xxxxing] hell....(censored by the moderator)... :grin:
By eck! ©
Hinton Heating
Gas/Heating Expert
Posts: 4382
Joined: Mon Jan 16, 2006 9:40 pm
Location: Bournemouth
Has thanked: 0
Been thanked: 9 times

Post by Hinton Heating »

was it 12kw as well? :lol:
jclloydy
Newly registered Member
Posts: 17
Joined: Wed Oct 04, 2006 3:41 pm
Has thanked: 0
Been thanked: 0

Post by jclloydy »

Gadget- just to clarify:

Run the original double socket to a 13A FCU, then to series of single, single and double socket, where it terminates.

There will be two computers running off of the chain, but no high load items.

Many thanks.
markysparky
Electrician
Posts: 272
Joined: Mon Jan 16, 2006 10:02 pm
Location: Darlington
Has thanked: 0
Been thanked: 0
Contact:

Post by markysparky »

jclloydy wrote:Gadget- just to clarify:

Run the original double socket to a 13A FCU, then to series of single, single and double socket, where it terminates.

There will be two computers running off of the chain, but no high load items.

Many thanks.
Yep that will do. Okay no high load items but it's to protect the cable just in case.

Somebody could plug in convector heaters, paint strippers or the light and cause all sorts of trouble so best to safe than sorry!
markysparky
Electrician
Posts: 272
Joined: Mon Jan 16, 2006 10:02 pm
Location: Darlington
Has thanked: 0
Been thanked: 0
Contact:

Post by markysparky »

Wrong thread! :oops: :lol: