Light fitting !!

All electrical lighting questions in here please. Including outside lighting and light switch / dimmer questions.

Moderator: Moderators

Locked
Blueboy4ever
Newly registered Member
Posts: 7
Joined: Sat Oct 14, 2006 11:45 am
Has thanked: 0
Been thanked: 0

Light fitting !!

Post by Blueboy4ever »

Hi Guys hope you can help. I have bought a replacement light fitting and cannot get my head around the wiring. On removing my old light there was;

Black and red cable together
Two reds together
Two blacks together
Three yellow/ green together

On the new fitting there is only two wiring points, two marked neutral and two marked live? Please help.
User avatar
ultimatehandyman
Site Admin
Posts: 24425
Joined: Sat Jul 16, 2005 7:06 pm
Location: Darwen, Lancashire
Has thanked: 1012 times
Been thanked: 918 times

Post by ultimatehandyman »

Hi,

and welcome to the forum.

Is there no earthing point on the light fitting?

What type of light fitting is it? For example is it a fan light etc.

when you say that the wires are together, what exactly do you mean?
Do you mean they were terminated in the same terminal?
markysparky
Electrician
Posts: 272
Joined: Mon Jan 16, 2006 10:02 pm
Location: Darlington
Has thanked: 0
Been thanked: 0
Contact:

Post by markysparky »

The 2 blacks put into the neutrals

the red wire and black wire put into the live

The 2 reds put into a strip connector and that is it. do not connect into the light in any way

Green and yellows go into earth.
markysparky
Electrician
Posts: 272
Joined: Mon Jan 16, 2006 10:02 pm
Location: Darlington
Has thanked: 0
Been thanked: 0
Contact:

Post by markysparky »

I'm assuming that the extra wire for the live is to do another light.

Does the light you are fitting come on with another light by any chance :?:
Blueboy4ever
Newly registered Member
Posts: 7
Joined: Sat Oct 14, 2006 11:45 am
Has thanked: 0
Been thanked: 0

Post by Blueboy4ever »

The light is connected to an extractor fan.
Blueboy4ever
Newly registered Member
Posts: 7
Joined: Sat Oct 14, 2006 11:45 am
Has thanked: 0
Been thanked: 0

Post by Blueboy4ever »

......and the instructions say that the light does not need to be earthed
Blueboy4ever
Newly registered Member
Posts: 7
Joined: Sat Oct 14, 2006 11:45 am
Has thanked: 0
Been thanked: 0

Post by Blueboy4ever »

Have tried what you said MarkySparky, but nothing is happening (no light comes on and the seperate extractor fan is not running).
User avatar
ultimatehandyman
Site Admin
Posts: 24425
Joined: Sat Jul 16, 2005 7:06 pm
Location: Darwen, Lancashire
Has thanked: 1012 times
Been thanked: 918 times

Post by ultimatehandyman »

Is there no instruction manual with it?

Are you sure there are no other markings on the fitting besides 2* neutrals and lives?

Is there no symbol that looks like a switch ___/ ___ or similar?
Blueboy4ever
Newly registered Member
Posts: 7
Joined: Sat Oct 14, 2006 11:45 am
Has thanked: 0
Been thanked: 0

Post by Blueboy4ever »

There are some very brief instructions which state
' If a wiring loop system is used within your home there may be several cables coming out of your ceiling. Before disconnecting your existing light please make a note which cables it is connected to and connect your new fitting to thses wires.'

There are definetly just the four connection points, two Live Terminals and two Neutral terminals.
honeymonster
Senior Member
Posts: 376
Joined: Sun Jul 17, 2005 11:38 am
Location: Newcastle
Has thanked: 0
Been thanked: 0

Post by honeymonster »

It sounds like there is a terminal for the permanent live and switched live on the new light, so that the fan can continue to run once the light is switched off.

The instructions seem very poor!

The terminals in the light fitting-

do the two neutrals wire to the same bit inside of the light or are they definately two individual terminals?
honeymonster
Senior Member
Posts: 376
Joined: Sun Jul 17, 2005 11:38 am
Location: Newcastle
Has thanked: 0
Been thanked: 0

Post by honeymonster »

It may be a good idea to post a picture if possible?
markysparky
Electrician
Posts: 272
Joined: Mon Jan 16, 2006 10:02 pm
Location: Darlington
Has thanked: 0
Been thanked: 0
Contact:

Post by markysparky »

The red and black wire! are they in the same terminal? They are not in seperate terminals by any chance?

If they are seperate put them together into the L terminal and see what happens
Blueboy4ever
Newly registered Member
Posts: 7
Joined: Sat Oct 14, 2006 11:45 am
Has thanked: 0
Been thanked: 0

Post by Blueboy4ever »

Tried to put the red and black wires in the same terminal - still nothing. I am going to rip my hair out soon :!:
Blueboy4ever
Newly registered Member
Posts: 7
Joined: Sat Oct 14, 2006 11:45 am
Has thanked: 0
Been thanked: 0

Post by Blueboy4ever »

Sod it, i have just found a direct replacement for the light that i had originally in my bathroom on Screwfix - so i have ordered it! Can't be doing with that other bloody thing any longer ! Its free to a good home if anybody wants it!
Hinton Heating
Gas/Heating Expert
Posts: 4382
Joined: Mon Jan 16, 2006 9:40 pm
Location: Bournemouth
Has thanked: 0
Been thanked: 9 times

Post by Hinton Heating »

generally a light on a loop circuit will have the following connections

earth - all the earths in a terminal block

Neutral - The loop circuit Neutral (normally 2 blacks) + the bulb Neutral + the fan neural

Perm Live - The loop circuit live (normally 2 reds) + supply to switch (normally red) + live to fan

Switch live - return from light (normally black) + the bulb live + the switch live to fan

There are your 3 terminals on your light! 8-)