13amp Fuse Blows On Initial Start Up

Post by Robert »

:shock: I have a new AL-KO 3Kw Log Splitter supplied with a standard 13amp plug. When I plug it into my ring main the 13amp Fuse
blows. If I then immediately replace the fuse, I can switch it on and off with out any problem during the period I am using it. The next time that I "start up" after leaving it a day, the same thing happens and I have to go through the fuse replacement sequence again. I understand that a 3Kw motor is quite hefty. I have contacted the manufacturer, they say once the machine has been "run in" the problem should stop - but this has not happened yet. I use the cable supplied with the machine and do not use any extension cable. Has any one got any suggestions to remedy this problem please?
Robert
User avatar
big-all
Pro Carpenter
Posts: 23591
Joined: Sat Dec 16, 2006 10:11 pm
Location: redhill surrey an auld reekie laddie
Has thanked: 735 times
Been thanked: 2339 times

Post by big-all »

start up currents can be very high
i wonder if replacing the fuse with a 15amp would cure the problem assuming it didnt constitute a danger to the wiring!!!!! :scratch:
we are all ------------------still learning
unclek
Newly registered Member
Posts: 89
Joined: Mon May 07, 2007 3:48 pm
Has thanked: 0
Been thanked: 0

Post by unclek »

See if you can get some time lag 13A fuses. They normally have a "T" on them. These will allow the motor to draw a larger current when starting and not blow.
User avatar
stevelusky
Senior Member
Posts: 118
Joined: Sat Nov 03, 2007 7:51 pm
Has thanked: 0
Been thanked: 1 time

Post by stevelusky »

My friend had a sliding mitre saw which had the same problem, although it was tripping the breaker in the fuseboard everytime he started it, then it would run fine after it was reset. I suggested that he used a r.c.d. Image thinking that it would be easier to reset this at the plug rather than have to walk to the fuseboard everytime, but since he started using it it has not tripped out at all. Dunno if ithas some sort of cusioning effect ? I did some insulation tests on the saw and its safe enough, maybe try the same thing, they only cost 5-10 quid and tbh you should be using one anyway.
Robert
Newly registered Member
Posts: 3
Joined: Sun Jan 20, 2008 12:02 pm
Location: Pembrokeshire
Has thanked: 0
Been thanked: 0

The answer

Post by Robert »

:grin: Thank You stevelusky, that is the answer. I used my R.C.D. plug in the socket and now my Wood Splitters on/off switches work all the time without blowing the fuse!

Super,
Robert
User avatar
Wood Magnet
Senior Member
Posts: 3659
Joined: Tue Feb 07, 2006 9:29 pm
Location: sunderland
Has thanked: 0
Been thanked: 3 times

Post by Wood Magnet »

:thumbright: Nice one Robert, and a good call Steve. :thumbright:
People forget how fast you did a job - but they remember how well you did it.

I no longer skinny dip, i chunky dunk these day's.
User avatar
stevelusky
Senior Member
Posts: 118
Joined: Sat Nov 03, 2007 7:51 pm
Has thanked: 0
Been thanked: 1 time

Post by stevelusky »

Glad it worked, I dont know why it should, Would be interested to know why though, If it blows a fuse in the plug it should have tripped the R.C.D. i would of thought ???
User avatar
leckylecturer
Newly registered Member
Posts: 6
Joined: Sat Feb 09, 2008 9:58 pm
Location: Sunderland
Has thanked: 0
Been thanked: 0

RCD tripping

Post by leckylecturer »

Here is the technical answer

RCDs respond to a difference in current between the live and neutral.
Circuit breakers and fuses respond to a high current and will fail if their operating value is exceeded. SO, an RCD will not trip due to a high inrush current. And a fuse will not respond to an earth fault of 30mA, but an RCD will. Two different devices for two kinds of protection. The RCD would operate if your log splitter had a fault to earth.

When a motor starts, it can pull up to eight times its normal operating current.

As to why fitting an RCD will make a difference?
The circuit of an RCD has a pair of coils wrapped around a magnetisable core. This detects an imblalance and trips the circuit. Now, we use coils (inductors) in electronics to dampen changes in current. For example, surge protectors for PCs. Perhaps (and dont quote me on this, i will have to experiment), the coil in the rcd dampens the in-rush current when the motor starts.

Inductors work a bit like a capacitor. I am sure you know that a capacitor will charge and discharge much like a battery and will hold energy as voltage. A coil (or inductor) will hold energy as current! It will also charge and discharge like a capacitor and so will absorb and release energy into a circuit as the current changes.

OK, science lesson over. Hope this doesnt raise more questions.

And finally, just to be rude, if you need an electric log splitter, i suggest you get some roughage! :oops:
A clever electrician is someone who has only been electrocuted once. Oh, and lived to tell the tale!
User avatar
stevelusky
Senior Member
Posts: 118
Joined: Sat Nov 03, 2007 7:51 pm
Has thanked: 0
Been thanked: 1 time

Post by stevelusky »

^^ good answer, sort of thought it was because of coils in the RCD, just nice to know why !
log splitter line made me chuckle :lol:
User avatar
Wood Magnet
Senior Member
Posts: 3659
Joined: Tue Feb 07, 2006 9:29 pm
Location: sunderland
Has thanked: 0
Been thanked: 3 times

Post by Wood Magnet »

Whoo Hoo! Another Mackem with toilet humour. :thumbright: :lol: :lol: :lol:
People forget how fast you did a job - but they remember how well you did it.

I no longer skinny dip, i chunky dunk these day's.
User avatar
leckylecturer
Newly registered Member
Posts: 6
Joined: Sat Feb 09, 2008 9:58 pm
Location: Sunderland
Has thanked: 0
Been thanked: 0

Mackem indeed!

Post by leckylecturer »

For the record, I just live in Sunderland. I was born and bred on Tyneside. Waht do you mak of that!
A clever electrician is someone who has only been electrocuted once. Oh, and lived to tell the tale!
User avatar
Wood Magnet
Senior Member
Posts: 3659
Joined: Tue Feb 07, 2006 9:29 pm
Location: sunderland
Has thanked: 0
Been thanked: 3 times

Post by Wood Magnet »

*Infiltrator Alert* :lol:
People forget how fast you did a job - but they remember how well you did it.

I no longer skinny dip, i chunky dunk these day's.
Post Reply

Return to “Tool Talk”