Not my work!
I am fairly new to this and was totally caught out. Customer complained that her shower kept "blowing the fuse". I was totally not expecting to see THIS! What even is that? Computer cable? It is a miracle that it ever operated the shower.
(sorry it is sideways - computer would not allow it the right way up)
Advice please - the customer has the minor works certificate so I know who fitted this. I think that using that wire is not an error as three strands connected to nothing and he should have known it was the wrong cable. Should I contact him? Report him? Or is the protocol that we stick together? That looks downright dangerous to me!
(sorry it is sideways - computer would not allow it the right way up)
Advice please - the customer has the minor works certificate so I know who fitted this. I think that using that wire is not an error as three strands connected to nothing and he should have known it was the wrong cable. Should I contact him? Report him? Or is the protocol that we stick together? That looks downright dangerous to me!
- Someone-Else
- Senior Member
- Posts: 14712
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 47 times
- Been thanked: 2590 times
Not my work!
The cable you see is used for central heating controls / valves.
If it were me I would just change the cable / switches and charge the customer accordingly.
You will spend (waste) more time "reporting" the person who did the job and at the end of the day achieve nothing.
(yes it shouldn't be that way, but it is)
If it were me I would just change the cable / switches and charge the customer accordingly.
You will spend (waste) more time "reporting" the person who did the job and at the end of the day achieve nothing.
(yes it shouldn't be that way, but it is)
- These users thanked the author Someone-Else for the post:
- LadySpark (Wed Nov 06, 2019 1:18 am)
- Rating: 7.14%
Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
- LadySpark
- Newly registered Member
- Posts: 81
- Joined: Wed Sep 11, 2019 11:59 pm
- Has thanked: 85 times
- Been thanked: 17 times
Not my work!
I changed it … but only after giving a fixed price for the job. As I said, I am new to this and got caught out. Plus it was a little old lady and I am a soft touch. However, I hate pulling cables through attics so I was feeling more than grumpy while doing it, hence the above post. I see it is low smoke low odour cable but surely that cable could not power any kind of heating? If I had to guess, I would say it was intended for 3 Amp of 6 Amp max. The finishing touch - with so many colours to choose from, when making the choice of which to use and which to just cut short, he didn't even make a sensible choice of colours.
-
- Senior Member
- Posts: 1172
- Joined: Wed May 27, 2009 6:50 pm
- Has thanked: 83 times
- Been thanked: 24 times
Not my work!
Hello LadySpark, not sure what you mean by: “He didn’t make the right choice of colours”?
I’m no SPARK, but looks like he did make an effort: Red, Blue & Yellow/Green. That’s ok isn’t it?
I’m no SPARK, but looks like he did make an effort: Red, Blue & Yellow/Green. That’s ok isn’t it?
Men will always be kids. Even after they have grown up, they keep trying to go back where they originally came from!
- LadySpark
- Newly registered Member
- Posts: 81
- Joined: Wed Sep 11, 2019 11:59 pm
- Has thanked: 85 times
- Been thanked: 17 times
Not my work!
Old colours: red = live, black = neutralkintangoman wrote: ↑Sat Nov 30, 2019 6:45 pm Hello LadySpark, not sure what you mean by: “He didn’t make the right choice of colours”?
I’m no SPARK, but looks like he did make an effort: Red, Blue & Yellow/Green. That’s ok isn’t it?
New colours: brown = live, blue = neutral
At the end of the day, a wire is a wire whatever colour the sheath but it is normal to put a sleeve of the correct colour over the wire if you have good reason to use the wrong colour. Ideally mixing old and new wiring colours should be avoided and there should be a sticker on the consumer unit if you must do it. He didn't need to do it as the shower had its own line so he could have stuck with the old colours but chose the unusual combination of a mix of old and new.
It isn't a big deal. Using ridiculously thin cable that could have caught fire is a big deal.
-
- Newly registered Member
- Posts: 4
- Joined: Sat Dec 14, 2019 11:19 am
- Has thanked: 0
- Been thanked: 0
Not my work!
If is was tripping out then the cable must have melted somewhere,with such an heavy load would have thought that the cores shown would have melted too, did the Dipstick replace the mcb or added another circuit .
- Razor
- Senior Member
- Posts: 8760
- Joined: Wed Nov 14, 2007 10:21 pm
- Location: Northampton
- Has thanked: 483 times
- Been thanked: 1251 times
Not my work!
That's 0.75mm heat resistant flex. It is used for heating system controls
Remember the FCU on a heating system should be fused down to 3A the loads are very small especially if they have modern induction pumps fitted
Remember the FCU on a heating system should be fused down to 3A the loads are very small especially if they have modern induction pumps fitted
I think I'll take two chickens...
- LadySpark
- Newly registered Member
- Posts: 81
- Joined: Wed Sep 11, 2019 11:59 pm
- Has thanked: 85 times
- Been thanked: 17 times
Not my work!
The shower had its own line with its own MCB, which is correct. I used the dodgy wire to pull the correct wire through the attic. It was pretty dirty with some scuff marks where I had used it to pull the new, thicker cable but I could see no obvious place where it had burnt through. Probably just the sheath to the inner cables had melted, causing a short. Thankfully the MCB worked. I changed the MCB anyway because they are a couple of quid and I wanted the entire line to be my work with nothing from the person who fitted this. Knowing my luck there might be some way to fake the amps on a fuse or something so it was worth a couple of quid to be sure.
- Razor
- Senior Member
- Posts: 8760
- Joined: Wed Nov 14, 2007 10:21 pm
- Location: Northampton
- Has thanked: 483 times
- Been thanked: 1251 times
Not my work!
Absolutely agree LS!
If you was the last person there leave it to your standards not some bodgers
If you was the last person there leave it to your standards not some bodgers
I think I'll take two chickens...