Cabling for exterior light

All electrical lighting questions in here please. Including outside lighting and light switch / dimmer questions.

Moderator: Moderators

Post Reply
Father Ted
Senior Member
Posts: 173
Joined: Mon Sep 16, 2013 8:24 pm
Has thanked: 30 times
Been thanked: 2 times

Cabling for exterior light

Post by Father Ted »

Hello

I'm an installing two led lights and a separate pir unit to side of shed to illuminate an alleyway.
I'll need to get 3 glands to pass the cabling through the corrugated tin.
However, I was planning to use 3+e for the pir, but I've been told I need double insulated cable for this and 3+e is not suitable. I don't need a tight seal on the gland for it as it is only intended for mechanical protection when going through the tin - there will be a waterproof junction box used inside shed for all the connections.

Is 3+e okay here or what cabling should I be using?
User avatar
Someone-Else
Senior Member
Posts: 14709
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 47 times
Been thanked: 2590 times

Cabling for exterior light

Post by Someone-Else »

3 core and earth is double insulated, so long as you use a gland with an elongated hole it should be fine.
If you are using a water resistant JB, why not mount it outside, since that is what it is for, and it will probably make life easier.
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
Father Ted
Senior Member
Posts: 173
Joined: Mon Sep 16, 2013 8:24 pm
Has thanked: 30 times
Been thanked: 2 times

Cabling for exterior light

Post by Father Ted »

Someone-Else wrote: Mon Jan 04, 2021 8:54 pm 3 core and earth is double insulated, so long as you use a gland with an elongated hole it should be fine.
If you are using a water resistant JB, why not mount it outside, since that is what it is for, and it will probably make life easier.
I had thought about that initially but decided it would be neater to have it all inside.
Is it difficult to get an elongated insert for the glands?
User avatar
Someone-Else
Senior Member
Posts: 14709
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 47 times
Been thanked: 2590 times

Cabling for exterior light

Post by Someone-Else »

Father Ted wrote: Mon Jan 04, 2021 10:56 pmIs it difficult to get an elongated insert for the glands?
No, you buy the whole gland with elongated hole (Can't think of the right word)
These users thanked the author Someone-Else for the post:
Father Ted (Tue Jan 05, 2021 5:12 pm)
Rating: 7.14%
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
User avatar
ericmark
Senior Member
Posts: 4276
Joined: Tue May 10, 2011 2:43 am
Location: Mid Wales
Has thanked: 118 times
Been thanked: 783 times

Cabling for exterior light

Post by ericmark »

Most cable designed for use outside is black, as it resists UV light better, I have seen flat grey cable used outside, but that does not make it right, and some where it needs to power some thing outside and round profile stuffing glands seal better than oval.