Dimmer switch with 2 red wires & earth

All electrical lighting questions in here please. Including outside lighting and light switch / dimmer questions.

Moderator: Moderators

Post Reply
SRJDIY
Newly registered Member
Posts: 29
Joined: Sun May 02, 2021 3:47 pm
Has thanked: 0
Been thanked: 0

Dimmer switch with 2 red wires & earth

Post by SRJDIY »

I have a dimmer switch that recently stopped working, so I'm hoping to replace it with a new one.

This is the only switch that controls the light in question, so based on my googling I expected to see one red or brown live wire and one black or blue switched live wire going into the switch. However, both wires going in are red.

My understanding is that I need to attach the live wire to common and the switched live to L1 on the new switch, but I'm not sure how to do this as I'm not sure if both red wires are live or if only one is and the other's been mislabelled.

Adding to the confusion, the label on the old switch says 'connect either way around', but one terminal has a red dot underneath it and the other doesn't, suggesting there is a difference.

Does anyone know what's going on please? Is this something with a simple answer I just don't know, or is it time to call an electrician in?

I've also attached a picture if it helps. The label says "Connect wires either way around, 1 way 250w, 200-250v, suppressed to BS800, Pats 1514161 & 2063573''.

Thank you!
Attachments
Dimmer switch.png
Dimmer switch.png (4.05 MiB) Viewed 2417 times
User avatar
Someone-Else
Senior Member
Posts: 14709
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 47 times
Been thanked: 2590 times

Dimmer switch with 2 red wires & earth

Post by Someone-Else »

You can never go by the colours, since it always depends on how who ever installed it, chose to do it.
Normal twin and earth does have (as you say) Brown and blue OR Black and red. In either case the switched wire should be marked as such, so Brown sleeving on the blue wire OR red sleeving on the black wire. BUT who ever wired your house actually used the correct cable. You really should use twin red (Twin brown from 2004) for the cable to the light switch.

To answer your question, it does not matter which way round you connect your new light switch.
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
User avatar
arco_iris
Senior Member
Posts: 2285
Joined: Sat Apr 19, 2014 5:27 pm
Location: SW Wales
Has thanked: 184 times
Been thanked: 535 times

Dimmer switch with 2 red wires & earth

Post by arco_iris »

:welcomeuhm:

"Connect either way round" means that, it doesn't matter which wire goes to which terminal.

(In this case - there may be circumstances when it could matter, but not here).

The switch point has been wired with two reds (equivalent modern installations in last 18-20 years would be two browns) so that Switched Live is the correct colour when it gets to the lamp. Whoever installed it originally exhibited good practice - black+red or brown+blue, though acceptable (especially if a sleeve is used) is really a cheat using standard, conventional cable.

S-E was typing faster than me!
SRJDIY
Newly registered Member
Posts: 29
Joined: Sun May 02, 2021 3:47 pm
Has thanked: 0
Been thanked: 0

Dimmer switch with 2 red wires & earth

Post by SRJDIY »

Someone-Else wrote: Sun May 02, 2021 5:31 pm To answer your question, it does not matter which way round you connect your new light switch.
arco_iris wrote: Sun May 02, 2021 5:40 pm "Connect either way round" means that, it doesn't matter which wire goes to which terminal.

(In this case - there may be circumstances when it could matter, but not here).
Thanks for the responses! I'm still curious though. I understand the logic of having the switched live wire be red because it can be live if the switch is on. But if it doesn't matter which wire I connect to common and which to L1 then why is this please? Sorry to be a pain; I just want to make sure I fully understand what's actually happening when I wire the new switch up!
User avatar
Someone-Else
Senior Member
Posts: 14709
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 47 times
Been thanked: 2590 times

Dimmer switch with 2 red wires & earth

Post by Someone-Else »

It's the way the switch is designed.
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
Post Reply

Return to “Lighting”