Upstairs lighting not isolated by any MCB in the consumer unit

All electrical lighting questions in here please. Including outside lighting and light switch / dimmer questions.

Moderator: Moderators

Post Reply
davec56
Newly registered Member
Posts: 5
Joined: Mon Jun 14, 2021 11:13 am
Has thanked: 1 time
Been thanked: 1 time

Upstairs lighting not isolated by any MCB in the consumer unit

Post by davec56 »

Hello,
My daughter has just moved into a house and asked me to fit a new, fancy light fitting in the main bedroom. However, I discovered that none of the MCBs in the consumer unit turn the power off to that bedroom (and one other at the front of the house), despite there being two MCBs that are marked as being for 'Upstairs lighting'!

Is it likely that one of the MCBs has failed (and so won't trip off)? Or is there another likely cause for the problem? I know I can (and should) turn off all the power at the CU but having found this issue I am concerned that she may have a bigger problem to solve.

Many thanks for any suggestions.
User avatar
aeromech3
Senior Member
Posts: 3598
Joined: Fri Feb 26, 2010 11:16 am
Location: Ash Surrey
Has thanked: 177 times
Been thanked: 665 times

Upstairs lighting not isolated by any MCB in the consumer unit

Post by aeromech3 »

:welcomeuhm: Well before an electrician answers, you could do some deduction: are there any MCB's which when in the off position do nothing to any of the house outlets (specific if you want, those marked for lighting) Lighting MCB's can range from 6 to 16 ampere mostly depending on the size of cabling. If a particular MCB does nothing it could be not connected, I have several redundant in my consumer unit, or failed.
These users thanked the author aeromech3 for the post:
davec56 (Mon Jun 14, 2021 11:50 am)
Rating: 7.14%
davec56
Newly registered Member
Posts: 5
Joined: Mon Jun 14, 2021 11:13 am
Has thanked: 1 time
Been thanked: 1 time

Upstairs lighting not isolated by any MCB in the consumer unit

Post by davec56 »

Thanks for the quick reply. I'm not at my daughter's house at the moment, so I'm going from memory, but I believe that all of the MCBs in the CU do turn something off when in the off position, except for one of the MCBs that are labelled as 'Upstairs lighting' - which maybe points to the MCB being faulty? I have no idea how common it is for one to fail in the 'on' state. The only thing that kills the power to the affected bedroom is to turn the main power switch off.
yartin
Senior Member
Posts: 1269
Joined: Fri Jun 09, 2017 11:55 am
Has thanked: 145 times
Been thanked: 129 times

Upstairs lighting not isolated by any MCB in the consumer unit

Post by yartin »

My friend had the same problem few years ago, he had only one fuse box (cu) under staircase, he called an electrician who found another one behind the fridge he had in the same area. You may have something similar?!
davec56
Newly registered Member
Posts: 5
Joined: Mon Jun 14, 2021 11:13 am
Has thanked: 1 time
Been thanked: 1 time

Upstairs lighting not isolated by any MCB in the consumer unit

Post by davec56 »

I don't think that's the case - but I'll double-check next time I'm there.
User avatar
Someone-Else
Senior Member
Posts: 14709
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 47 times
Been thanked: 2590 times

Upstairs lighting not isolated by any MCB in the consumer unit

Post by Someone-Else »

If it is as you say, and there is not another consumers unit somewhere, and you have turned all mcb's off one at a time (Might be labled wrong, unusual for two lighting circuits on the same floor) And the lights are not fed via a fused connection unit, then either it it is wired wrong or there is an mcb problem, so you should get an electrician to look for you, may be worth while getting an EICR done too. (like an MOT for a vehicle)
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
Neelix
Senior Member
Posts: 1333
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 118 times
Been thanked: 215 times

Upstairs lighting not isolated by any MCB in the consumer unit

Post by Neelix »

Hum, before you spend money on a spark ( and yes I’m a spark) turn said light on. Then turn off the circuit breakers one by one and see what happens, the light stays on turn each one off in turn and don’t switch it back on.

Then report back
davec56
Newly registered Member
Posts: 5
Joined: Mon Jun 14, 2021 11:13 am
Has thanked: 1 time
Been thanked: 1 time

Upstairs lighting not isolated by any MCB in the consumer unit

Post by davec56 »

Thanks - I will try that, but it will have to wait until I'm at my daughter's place again (so don't expect a quick update!).
These users thanked the author davec56 for the post:
Neelix (Mon Jun 14, 2021 4:40 pm)
Rating: 7.14%
Neelix
Senior Member
Posts: 1333
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 118 times
Been thanked: 215 times

Upstairs lighting not isolated by any MCB in the consumer unit

Post by Neelix »

davec56 wrote: Mon Jun 14, 2021 3:40 pm Thanks - I will try that, but it will have to wait until I'm at my daughter's place again (so don't expect a quick update!).
No rush, better safe than sorry
Grumps
Senior Member
Posts: 1030
Joined: Wed Jun 13, 2007 7:47 pm
Location: Worcestershire/Warwickshire/Gloucestershire (ish)
Has thanked: 51 times
Been thanked: 152 times

Upstairs lighting not isolated by any MCB in the consumer unit

Post by Grumps »

Mmm. This could turn into one of those that we had a few years ago. Daughter had a problem but Father lived in London. When prompted, it was disclosed that the Daughter lived Barnsley?

A member Lecky covered that area and solved the problem.

Link here.

viewtopic.php?t=58806

Blimey. Was it really that long ago. - 2012 :shock:
davec56
Newly registered Member
Posts: 5
Joined: Mon Jun 14, 2021 11:13 am
Has thanked: 1 time
Been thanked: 1 time

Upstairs lighting not isolated by any MCB in the consumer unit

Post by davec56 »

Tewkesbury and Worcester - so not that far apart! Hopefully I've got the electrician that I use coming to have a look on Thursday, so I'm sure he will sort it out.
User avatar
ericmark
Senior Member
Posts: 4276
Joined: Tue May 10, 2011 2:43 am
Location: Mid Wales
Has thanked: 118 times
Been thanked: 783 times

Upstairs lighting not isolated by any MCB in the consumer unit

Post by ericmark »

Neelix wrote: Mon Jun 14, 2021 2:19 pm Hum, before you spend money on a spark ( and yes I’m a spark) turn said light on. Then turn off the circuit breakers one by one and see what happens, the light stays on turn each one off in turn and don’t switch it back on.

Then report back
This is also what I would do, I have had it where two MCB's control the same circuit, at some point in the past the circuits had been split, so two lighting circuits, then they were linked again. In fact had it in my own house, a 4 switch plate controlled hall, landing, and two sets of outside lights, two independent supplies, one for landing light, and one for other three, and some how they had go mixed up. Found went went to all RCBO consumer unit.

My house the split is side to side for sockets, and up/down for lights one middle and upper floor, and lower floor independent RCBO's for lights and sockets, grouped upper two floors on left of consumer unit and lower floor to right. But easy to mix up and it took me 2 months to find out where one supply went, turned out to be a FCU likely originally outside socket. Rear outside lights are switched from hall at middle level, in spite of middle level not extending to rear that far, lower floor originally just a garage.