relocating ring wall socket
Hi
I want to relocate a double wall socket on same wall same height shifted by 2m.
can I do this way: Keep existing metal box, use 3 wago connectors for L,N & E to connect existing cable to new cable, place the 3 wagos in the metal box and put blanking plate, run the new cable on the wall with trunking to the required location and connect to socket with surface mount box.
Thanks
I want to relocate a double wall socket on same wall same height shifted by 2m.
can I do this way: Keep existing metal box, use 3 wago connectors for L,N & E to connect existing cable to new cable, place the 3 wagos in the metal box and put blanking plate, run the new cable on the wall with trunking to the required location and connect to socket with surface mount box.
Thanks
-
- Senior Member
- Posts: 1311
- Joined: Mon May 03, 2021 1:36 pm
- Has thanked: 117 times
- Been thanked: 214 times
relocating ring wall socket
Either way is OK but how are you going to test anything?
- Someone-Else
- Senior Member
- Posts: 14628
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 47 times
- Been thanked: 2575 times
relocating ring wall socket
I don't think that is what he meant.
How many cables are feeding the current socket? If it is two, you should use 6 wagos and 2 cables.
Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
-
- Senior Member
- Posts: 1266
- Joined: Fri Jun 09, 2017 11:55 am
- Has thanked: 145 times
- Been thanked: 126 times
relocating ring wall socket
Just one cable going to the socket, must be radial. I need 3 wagos, 2 way lever connectors each.Someone-Else wrote: ↑Mon Aug 30, 2021 6:50 pmI don't think that is what he meant.
How many cables are feeding the current socket? If it is two, you should use 6 wagos and 2 cables.
If it was two cables feeding socket, why not use 3 wagos with three way lever connectors each?
- Someone-Else
- Senior Member
- Posts: 14628
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 47 times
- Been thanked: 2575 times
relocating ring wall socket
Simples (As a certain meerkat says)
If you had 2 cables imagine one is "flow" the other is "return"
To to keep ring integrity both flow and return must be extended.
If you were to join all 3 cables "flow, return & extension" at the same point (i.e. before the extension) you still have the main ring, but the extension is now a spur from that ring, if you did it as I said first, the extension would also be on the ring.
It is simple misunderstandings that cause problems. e.g. using a socket tester and believing it "will do/be ok"
This is NOTHING PERSONAL, so don't take it as such, I look at it that I am correcting your potential error.
Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
-
- Senior Member
- Posts: 1266
- Joined: Fri Jun 09, 2017 11:55 am
- Has thanked: 145 times
- Been thanked: 126 times
relocating ring wall socket
It is allowed to take a spur from a ring main as far as doesn't exceed the limit. Unless taking a spur from a spur which needs fused spur. What is my potential error if I had 2 cables?Someone-Else wrote: ↑Mon Aug 30, 2021 8:13 pm
If you had 2 cables imagine one is "flow" the other is "return"
To to keep ring integrity both flow and return must be extended.
If you were to join all 3 cables "flow, return & extension" at the same point (i.e. before the extension) you still have the main ring, but the extension is now a spur from that ring, if you did it as I said first, the extension would also be on the ring.
- aeromech3
- Senior Member
- Posts: 3598
- Joined: Fri Feb 26, 2010 11:16 am
- Location: Ash Surrey
- Has thanked: 177 times
- Been thanked: 665 times
relocating ring wall socket
. Might be a Spur off a ring, are you sure?
. Only if it is a true radial!
Ok as Neelix answered, yartin was asking to just extend a radial or maybe its a spur but not adding another because he is blanking off the existing position.
Or am I just as confused by all the none relevant side issues?
-
- Senior Member
- Posts: 1266
- Joined: Fri Jun 09, 2017 11:55 am
- Has thanked: 145 times
- Been thanked: 126 times
relocating ring wall socket
Yes it is radial. I turned the rcd off that socket form CU and there is only one other socket on that circuit. I went to each room and all wall sockets, shaver point, immersion, shower pump, boiler, gas fire ignition and all lights were live.
No I can't leave existing socket because I changed door opening and this socket is just by the architrave, so you go into the room to turn the lights as you do and you are in direct contact with the socket, dangerous. So I put a blanking plate and smart wireless Quentic light switch there.
My post was just to ask if using Wagos was the right way to extend the cable and position wall socket on same wall, that's all. I could fill it and paint the wall instead of blanking plate but like it to be serviceable and accessible.
No I can't leave existing socket because I changed door opening and this socket is just by the architrave, so you go into the room to turn the lights as you do and you are in direct contact with the socket, dangerous. So I put a blanking plate and smart wireless Quentic light switch there.
My post was just to ask if using Wagos was the right way to extend the cable and position wall socket on same wall, that's all. I could fill it and paint the wall instead of blanking plate but like it to be serviceable and accessible.
-
- Senior Member
- Posts: 1266
- Joined: Fri Jun 09, 2017 11:55 am
- Has thanked: 145 times
- Been thanked: 126 times
relocating ring wall socket
That's my opinion, if Neelix doesn't like it then up to him. Please do not reply to my posts again, I don't need your input.
Do not rubbish what people say, this is a forum not a pub.
Do not rubbish what people say, this is a forum not a pub.
-
- Senior Member
- Posts: 1311
- Joined: Mon May 03, 2021 1:36 pm
- Has thanked: 117 times
- Been thanked: 214 times
relocating ring wall socket
Mate … you are saying something is dangerous when it’s clearly not
Stop spreading rubbish
-
- Senior Member
- Posts: 1266
- Joined: Fri Jun 09, 2017 11:55 am
- Has thanked: 145 times
- Been thanked: 126 times
relocating ring wall socket
I emailed NICEIC asking about having the socket as in my scenario, their reply was:
"We would recommend that you do consider how the socket outlet is to be used, including any possible trip hazards created by having a socket outlet in such close proximity to a doorway."
So now we know who was uttering rubbish and spreading them.
I hope the mods make note of this as such is not good for the forum.
"We would recommend that you do consider how the socket outlet is to be used, including any possible trip hazards created by having a socket outlet in such close proximity to a doorway."
So now we know who was uttering rubbish and spreading them.
I hope the mods make note of this as such is not good for the forum.