Earthing New Light Switch

Post by liamus »

Hi - I have just replaced a plastic dimmer switch with a metal one so needed to earth it. There are three earth wires coming out the wall and screwed in to the metal back box. I assumed that both back box and switch need earthing so removed one from the back box and put it on the switch and left two attached to back box? Is that correct?
Thanks in advance!
Neelix
Senior Member
Posts: 1311
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 117 times
Been thanked: 214 times

Earthing New Light Switch

Post by Neelix »

Not ideal. The earth needs to be continuous so the best way is to add a 4th earth to run from the back box connection to the switch
These users thanked the author Neelix for the post:
liamus (Sun Sep 12, 2021 3:34 pm)
Rating: 7.14%
liamus
Newly registered Member
Posts: 55
Joined: Tue Feb 14, 2012 2:21 pm
Has thanked: 4 times
Been thanked: 2 times

Earthing New Light Switch

Post by liamus »

ah, that makes a lot of sense. Thank you will update it
liamus
Newly registered Member
Posts: 55
Joined: Tue Feb 14, 2012 2:21 pm
Has thanked: 4 times
Been thanked: 2 times

Earthing New Light Switch

Post by liamus »

Neelix wrote: Sun Sep 12, 2021 3:30 pm Not ideal. The earth needs to be continuous so the best way is to add a 4th earth to run from the back box connection to the switch
I have some earth wire here but it is multi core - the ones coming out the wall are single core. Does that matter?

I may have the wording wrong - by single core I mean the ones out the wall is a single piece of wire with a loose sheath - the wire I have is stranded when I strip back the insulated cover
User avatar
Someone-Else
Senior Member
Posts: 14628
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 47 times
Been thanked: 2575 times

Earthing New Light Switch

Post by Someone-Else »

What you have is known as multi stranded, what you need is solid core.
Its not so much the fact it is stranded that is the problem, it must be the same size as the existing, which will be 1mm.
Have a look under the floor or in the loft to see if there is an "odd bit" lying there.
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
liamus
Newly registered Member
Posts: 55
Joined: Tue Feb 14, 2012 2:21 pm
Has thanked: 4 times
Been thanked: 2 times

Earthing New Light Switch

Post by liamus »

Someone-Else wrote: Thu Sep 16, 2021 6:44 pm What you have is known as multi stranded, what you need is solid core.
Its not so much the fact it is stranded that is the problem, it must be the same size as the existing, which will be 1mm.
Have a look under the floor or in the loft to see if there is an "odd bit" lying there.
Thank you - I can't find what I am looking for online - all seems to be 1.5mm ? Would you be so kind as to provide a link to what I need to buy?


EDIT - could I but this and cut a length of the earth out?:

https://smile.amazon.co.uk/Core-Round-W ... 81&sr=8-16
Neelix
Senior Member
Posts: 1311
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 117 times
Been thanked: 214 times

Earthing New Light Switch

Post by Neelix »

Someone-Else wrote: Thu Sep 16, 2021 6:44 pm What you have is known as multi stranded, what you need is solid core.
Its not so much the fact it is stranded that is the problem, it must be the same size as the existing, which will be 1mm.
Have a look under the floor or in the loft to see if there is an "odd bit" lying there.
Why does he need solid core?
User avatar
Someone-Else
Senior Member
Posts: 14628
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 47 times
Been thanked: 2575 times

Earthing New Light Switch

Post by Someone-Else »

Neelix wrote: Sat Sep 18, 2021 9:08 amWhy does he need solid core?
If you read it all, I then went on to say
Someone-Else wrote: Thu Sep 16, 2021 6:44 pmIts not so much the fact it is stranded that is the problem, it must be the same size as the existing, which will be 1mm
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
User avatar
Someone-Else
Senior Member
Posts: 14628
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 47 times
Been thanked: 2575 times

Earthing New Light Switch

Post by Someone-Else »

liamus wrote: Sat Sep 18, 2021 6:40 amEDIT - could I buy this and cut a length of the earth out?:
Yes.
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
Neelix
Senior Member
Posts: 1311
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 117 times
Been thanked: 214 times

Earthing New Light Switch

Post by Neelix »

Someone-Else wrote: Sat Sep 18, 2021 9:43 am
Neelix wrote: Sat Sep 18, 2021 9:08 amWhy does he need solid core?
If you read it all, I then went on to say
Someone-Else wrote: Thu Sep 16, 2021 6:44 pmIts not so much the fact it is stranded that is the problem, it must be the same size as the existing, which will be 1mm
So why complicate matters in the first place?
User avatar
Someone-Else
Senior Member
Posts: 14628
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 47 times
Been thanked: 2575 times

Earthing New Light Switch

Post by Someone-Else »

Neelix wrote: Sat Sep 18, 2021 9:56 amSo why complicate matters in the first place?
I don't know why you choose to complicate matters. The OP is happy.
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
liamus
Newly registered Member
Posts: 55
Joined: Tue Feb 14, 2012 2:21 pm
Has thanked: 4 times
Been thanked: 2 times

Earthing New Light Switch

Post by liamus »

Someone-Else wrote: Sat Sep 18, 2021 9:47 am
liamus wrote: Sat Sep 18, 2021 6:40 amEDIT - could I buy this and cut a length of the earth out?:
Yes.
Thank you