Add single socket to fused spur
I have a fused spur on a bedroom wall, which feeds a security light outside. It's right where I need a socket for a bedside light. Can i convert it into a socket AND fused spur? (A bit like what I have seen for cookers). It is surface mount.
- Someone-Else
- Senior Member
- Posts: 14628
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 47 times
- Been thanked: 2575 times
Add single socket to fused spur
Yes.
You must supply the socket from the fused side of the spur, since the FCU is already a spur.
It will be easier if it is all surface, if you want it flush you can get a double flush box that you can have a socket and an FCU on, side by side.
You must supply the socket from the fused side of the spur, since the FCU is already a spur.
It will be easier if it is all surface, if you want it flush you can get a double flush box that you can have a socket and an FCU on, side by side.
- These users thanked the author Someone-Else for the post:
- hiace_drifter (Sun Feb 06, 2022 7:29 pm)
- Rating: 7.14%
Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
-
- Senior Member
- Posts: 712
- Joined: Fri Jan 25, 2013 10:21 am
- Has thanked: 29 times
- Been thanked: 16 times
Add single socket to fused spur
Just to check:
1. where there is a L out to the security light, I also put a L out to the new socket (dashed red line to show new cable)
2. where there is a N out to the security light, I also put a N out to the new socket (dashed black line to show new cable)
3. there is no fuse in the fused outlet (it was removed when we moved in as we didn't know what it fed). what rating fuse would i need?
4. to connect the new socket and fused spur, do i just place the two surface mount sockets side by side and run a short length of twin and earth between them?
1. where there is a L out to the security light, I also put a L out to the new socket (dashed red line to show new cable)
2. where there is a N out to the security light, I also put a N out to the new socket (dashed black line to show new cable)
3. there is no fuse in the fused outlet (it was removed when we moved in as we didn't know what it fed). what rating fuse would i need?
4. to connect the new socket and fused spur, do i just place the two surface mount sockets side by side and run a short length of twin and earth between them?
- ericmark
- Senior Member
- Posts: 4265
- Joined: Tue May 10, 2011 2:43 am
- Location: Mid Wales
- Has thanked: 117 times
- Been thanked: 783 times
Add single socket to fused spur
Yes I did it hear
used grid switch system, in this case LAP which I think is Screwfix special so fuse holder switch and single socket in one double socket face plate.-
- Senior Member
- Posts: 712
- Joined: Fri Jan 25, 2013 10:21 am
- Has thanked: 29 times
- Been thanked: 16 times
Add single socket to fused spur
Just starting this job. There is no fuse in the fused outlet ... what fuse would I use? thanks.
- arco_iris
- Senior Member
- Posts: 2285
- Joined: Sat Apr 19, 2014 5:27 pm
- Location: SW Wales
- Has thanked: 184 times
- Been thanked: 535 times
Add single socket to fused spur
If it was just an FCU serving a lamp, then either a red 3amp or a black 5 amp.
But as you are now fitting a socket that might potentially be used for, say, a 3kw heater, then the fuse should be a brown 13A.
But as you are now fitting a socket that might potentially be used for, say, a 3kw heater, then the fuse should be a brown 13A.
- These users thanked the author arco_iris for the post:
- hiace_drifter (Sun Feb 06, 2022 7:29 pm)
- Rating: 7.14%
-
- Senior Member
- Posts: 712
- Joined: Fri Jan 25, 2013 10:21 am
- Has thanked: 29 times
- Been thanked: 16 times
Add single socket to fused spur
Thanks. I have some lengths of grey twin and earth - do they come in more than one thickness? Do I need to check it is thick enough? It's in my daughter's bedroom next to her bed, so being an over cautious father
-
- Senior Member
- Posts: 686
- Joined: Mon Sep 17, 2012 2:40 pm
- Has thanked: 26 times
- Been thanked: 174 times
Add single socket to fused spur
I'm no expert but.... a fuse high enough to cope with the load of the light (if it still going to be used) and whatever appliance you are likely to plug into the socket, but low enough that the wiring is protected and doesn't burn out.
If it were me I'd guess at 3/5a if the socket will only have a bedside lamp / phone charger
7a if it's things like a newish TV / laptop
10a if it's something more powerful. Just remember tho someone may not realise what your intentions were for the socket and go plugging in a hair drier / hair straighteners, iron, kettle (some people just need that morning coffee there and then) which are likely to pull a higher load and activate the fuse. Angry wife trying to Dry wet hair when power goes off is akin to a pit bull chewing on a bumble Bee, in both looks and attitude (well from my experience anyhow)
If it were me I'd guess at 3/5a if the socket will only have a bedside lamp / phone charger
7a if it's things like a newish TV / laptop
10a if it's something more powerful. Just remember tho someone may not realise what your intentions were for the socket and go plugging in a hair drier / hair straighteners, iron, kettle (some people just need that morning coffee there and then) which are likely to pull a higher load and activate the fuse. Angry wife trying to Dry wet hair when power goes off is akin to a pit bull chewing on a bumble Bee, in both looks and attitude (well from my experience anyhow)
- These users thanked the author Scotty001 for the post:
- hiace_drifter (Sun Feb 06, 2022 7:29 pm)
- Rating: 7.14%
-
- Senior Member
- Posts: 686
- Joined: Mon Sep 17, 2012 2:40 pm
- Has thanked: 26 times
- Been thanked: 174 times
Add single socket to fused spur
T&e does come in different thicknesses,hiace_drifter wrote: ↑Sat Jan 29, 2022 12:03 pm Thanks. I have some lengths of grey twin and earth - do they come in more than one thickness? Do I need to check it is thick enough? It's in my daughter's bedroom next to her bed, so being an over cautious father
lighting is normally 1/1.5mm
Sockets 2.5mm
Shiwers and ovens 6mm+
It should be stamped / imprinted on the grey cable sheith wat size the cable is
- These users thanked the author Scotty001 for the post:
- hiace_drifter (Sun Feb 06, 2022 7:29 pm)
- Rating: 7.14%
-
- Senior Member
- Posts: 712
- Joined: Fri Jan 25, 2013 10:21 am
- Has thanked: 29 times
- Been thanked: 16 times
Add single socket to fused spur
Found the size on the twin & earth - 2x2.5mmScotty001 wrote: ↑Sat Jan 29, 2022 12:08 pmT&e does come in different thicknesses,hiace_drifter wrote: ↑Sat Jan 29, 2022 12:03 pm Thanks. I have some lengths of grey twin and earth - do they come in more than one thickness? Do I need to check it is thick enough? It's in my daughter's bedroom next to her bed, so being an over cautious father
lighting is normally 1/1.5mm
Sockets 2.5mm
Shiwers and ovens 6mm+
It should be stamped / imprinted on the grey cable sheith wat size the cable is
Is there a tool to trim back the outer sheath, other than carefully score with a sharp knife? Every so often I nick the inner blue/brown sheathing too, which is a pain.
Also, how much outer sheath do you leave inside the back box?
- arco_iris
- Senior Member
- Posts: 2285
- Joined: Sat Apr 19, 2014 5:27 pm
- Location: SW Wales
- Has thanked: 184 times
- Been thanked: 535 times
Add single socket to fused spur
Forty years ago an electrician cousin (now dec'd, served him right for marrying my ex-gf) taught/showed me........
Gently press a craft knife ("Stanley") blade into the flat side of t&e about 6"/15cm from the end, not too deep, it only needs to be "scored". Turn it over and do the other side in the same place. Do not make any cut on the narrow sides.
Then, put the same blade on the end of the cable next to the central earth core and start to slit it. Very gently hold the knife at a slight angle pointing towards the earth and slit along - the blade slides along the earth without damaging the blue or brown insulation.
On reaching the sideways score, withdraw the knife. Separate the outer sheath from one of the insulated cores, at the end. Pull it downwards, when it meets the score the outer just snaps off cleanly, and straight. Little annoys me more than seeing the outer sheath "torn"!
If you do it often, Knipex 13 86 200 is a great tool, it has a slightly curved cutting blade that does the same job, though not the slitting. Also strips 1.5mm & 2.5mm wires. But they're £40/50.
As for length, anywhere from 25mm - 75mm outer inside the back box is sufficient.
Gently press a craft knife ("Stanley") blade into the flat side of t&e about 6"/15cm from the end, not too deep, it only needs to be "scored". Turn it over and do the other side in the same place. Do not make any cut on the narrow sides.
Then, put the same blade on the end of the cable next to the central earth core and start to slit it. Very gently hold the knife at a slight angle pointing towards the earth and slit along - the blade slides along the earth without damaging the blue or brown insulation.
On reaching the sideways score, withdraw the knife. Separate the outer sheath from one of the insulated cores, at the end. Pull it downwards, when it meets the score the outer just snaps off cleanly, and straight. Little annoys me more than seeing the outer sheath "torn"!
If you do it often, Knipex 13 86 200 is a great tool, it has a slightly curved cutting blade that does the same job, though not the slitting. Also strips 1.5mm & 2.5mm wires. But they're £40/50.
As for length, anywhere from 25mm - 75mm outer inside the back box is sufficient.
Last edited by arco_iris on Sat Jan 29, 2022 4:54 pm, edited 1 time in total.
- These users thanked the author arco_iris for the post:
- hiace_drifter (Sun Feb 06, 2022 7:29 pm)
- Rating: 7.14%
-
- Senior Member
- Posts: 686
- Joined: Mon Sep 17, 2012 2:40 pm
- Has thanked: 26 times
- Been thanked: 174 times
Add single socket to fused spur
I use a cable / wire stripper like this
It will cut the outer and the inner sheiths.
But mine is a lidl / aldi set which are half the cost but decent quality.
I normally leave a cm or so but it depends on the depth of the backbox
It will cut the outer and the inner sheiths.
But mine is a lidl / aldi set which are half the cost but decent quality.
I normally leave a cm or so but it depends on the depth of the backbox
- These users thanked the author Scotty001 for the post:
- hiace_drifter (Sun Feb 06, 2022 7:29 pm)
- Rating: 7.14%
-
- Senior Member
- Posts: 712
- Joined: Fri Jan 25, 2013 10:21 am
- Has thanked: 29 times
- Been thanked: 16 times
-
- Senior Member
- Posts: 712
- Joined: Fri Jan 25, 2013 10:21 am
- Has thanked: 29 times
- Been thanked: 16 times
Add single socket to fused spur
I think I know what you mean, but will draw a diagram to check!arco_iris wrote: ↑Sat Jan 29, 2022 4:45 pm Forty years ago an electrician cousin (now dec'd, served him right for marrying my ex-gf) taught/showed me........
Gently press a craft knife ("Stanley") blade into the flat side of t&e about 6"/15cm from the end, not too deep, it only needs to be "scored". Turn it over and do the other side in the same place. Do not make any cut on the narrow sides.
Then, put the same blade on the end of the cable next to the central earth core and start to slit it. Very gently hold the knife at a slight angle pointing towards the earth and slit along - the blade slides along the earth without damaging the blue or brown insulation.
On reaching the sideways score, withdraw the knife. Separate the outer sheath from one of the insulated cores, at the end. Pull it downwards, when it meets the score the outer just snaps off cleanly, and straight. Little annoys me more than seeing the outer sheath "torn"!
If you do it often, Knipex 13 86 200 is a great tool, it has a slightly curved cutting blade that does the same job, though not the slitting. Also strips 1.5mm & 2.5mm wires. But they're £40/50.
As for length, anywhere from 25mm - 75mm outer inside the back box is sufficient.
- wine~o
- Senior Member
- Posts: 26279
- Joined: Sat Jan 10, 2009 3:49 pm
- Location: hants/dorset border
- Has thanked: 1414 times
- Been thanked: 4019 times
Add single socket to fused spur
The fuse (in the FCU) is there to protect the cable, not the device. so a socket (whether single or double) run in 2.5mm twin and earth can be protected by a 13 A fuse.
- These users thanked the author wine~o for the post:
- hiace_drifter (Sun Feb 06, 2022 7:29 pm)
- Rating: 7.14%
Verwood Handyman
_____________________________________________________________________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :
http://www.donnasdreamhouse.co.uk
_____________________________________________________________________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :
http://www.donnasdreamhouse.co.uk