External RCD Sockets-Drain holes or not?

All your electrical questions regarding electrics from within the United Kingdom

Moderator: Moderators

Post Reply
User avatar
Argyll
Senior Member
Posts: 6158
Joined: Wed Sep 10, 2008 3:58 pm
Has thanked: 1180 times
Been thanked: 580 times

External RCD Sockets-Drain holes or not?

Post by Argyll »

I've installed an external RCD double socket coming from an FCU inside the house. There's a bit of debate about whether I should drill the drain hole or not. Some say as it's coming directly from the house into the back of the RCD socket and it's siliconed there's no need to.

Opinions from sparkies, please?
Neelix
Senior Member
Posts: 1311
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 117 times
Been thanked: 214 times

External RCD Sockets-Drain holes or not?

Post by Neelix »

Always drill a drain hole
User avatar
Someone-Else
Senior Member
Posts: 14628
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 47 times
Been thanked: 2575 times

External RCD Sockets-Drain holes or not?

Post by Someone-Else »

Doesn't matter where it is fed from, it's the fact that it is outside that is the "problem"
You have an "empty box" fixed to a wall outside. But the box is not really empty (Not counting the socket) it is full of air. When the temperature drops the air will condense on the now cold box, give it a few months and the condensate will build up.
Drill 2 holes at the back bottom of the box, (one to the left, one to the right) 1-3 mm will be fine.
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
User avatar
ericmark
Senior Member
Posts: 4265
Joined: Tue May 10, 2011 2:43 am
Location: Mid Wales
Has thanked: 117 times
Been thanked: 783 times

External RCD Sockets-Drain holes or not?

Post by ericmark »

As @Someone-Else says I always drill a hole.