Wiring bathroom extractor/light off isolator switch fed by socket circuit
All your electrical questions regarding electrics from within the United Kingdom
Moderator: Moderators
-
- Newly registered Member
- Posts: 17
- Joined: Wed Oct 19, 2016 11:35 am
- Has thanked: 6 times
- Been thanked: 0
Wiring bathroom extractor/light off isolator switch fed by socket circuit
Hi,
Need to install a new bathroom extractor and light, which would usually be simple enough, but the current extractor and light are fed by an isolator switch off of the socket circuit instead of the upstairs lighting.
Is it acceptable to go ahead and replace the extractor and light using the same feed isolator from the socket circuit or does it have to be changed so its being fed off the lighting circuit with just the extractor isolated separately.
thanks
Need to install a new bathroom extractor and light, which would usually be simple enough, but the current extractor and light are fed by an isolator switch off of the socket circuit instead of the upstairs lighting.
Is it acceptable to go ahead and replace the extractor and light using the same feed isolator from the socket circuit or does it have to be changed so its being fed off the lighting circuit with just the extractor isolated separately.
thanks
TheDoug
- Someone-Else
- Senior Member
- Posts: 14855
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 48 times
- Been thanked: 2608 times
Wiring bathroom extractor/light off isolator switch fed by socket circuit
Post by Someone-Else »
Does it have a fused connection unit?
- FCU.jpg (22.59 KiB) Viewed 2335 times
Doesn't have to be this colour or switch. (or this big)
Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section

Someone-Else
-
- Newly registered Member
- Posts: 17
- Joined: Wed Oct 19, 2016 11:35 am
- Has thanked: 6 times
- Been thanked: 0
Wiring bathroom extractor/light off isolator switch fed by socket circuit
Yeah, that's what I meant by isolation switch, the flex goes into the loft to a junction box that then has cables going to the pull cord, light and extractor.Someone-Else wrote: ↑Sat Dec 18, 2021 6:47 pmDoes it have a fused connection unit?
FCU.jpg
Doesn't have to be this colour or switch. (or this big)
- Attachments
-
- 20211218_194447.jpg (138.31 KiB) Viewed 2327 times
TheDoug
-
- Newly registered Member
- Posts: 17
- Joined: Wed Oct 19, 2016 11:35 am
- Has thanked: 6 times
- Been thanked: 0
Wiring bathroom extractor/light off isolator switch fed by socket circuit
Assuming that its fine to run the extractor and light from that feed, would i still need to have a 3 pole isolator switch between the JB and extractor, even though both the light and extractor can just be isolated at the fused switch from the feed?
TheDoug
- Someone-Else
- Senior Member
- Posts: 14855
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 48 times
- Been thanked: 2608 times
Wiring bathroom extractor/light off isolator switch fed by socket circuit
Post by Someone-Else »
You are supposed to.
The fan has to be easy to isolate, so the 3 pole isolator is supposed to be near the fan, but if that FCU is not far away..............
The fan has to be easy to isolate, so the 3 pole isolator is supposed to be near the fan, but if that FCU is not far away..............
- These users thanked the author Someone-Else for the post:
- TheDoug (Sat Dec 18, 2021 11:37 pm)
- Rating: 7.14%
Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section

Someone-Else
Neelix
- aeromech3
- Senior Member
- Posts: 3598
- Joined: Fri Feb 26, 2010 11:16 am
- Location: Ash Surrey
- Has thanked: 177 times
- Been thanked: 665 times
Wiring bathroom extractor/light off isolator switch fed by socket circuit
Surely a 3 pole is necessary when a permanent live is fed to the fan for the run on timer?
Granted the Op has not stated it as a timer fan.
Granted the Op has not stated it as a timer fan.
aeromech3
-
- Senior Member
- Posts: 1368
- Joined: Mon May 03, 2021 1:36 pm
- Has thanked: 118 times
- Been thanked: 219 times
Wiring bathroom extractor/light off isolator switch fed by socket circuit
There is absolutely no necessity for an isolator for an extractor fan .......
Neelix
-
- Approved Electrician
- Posts: 3132
- Joined: Sun Apr 24, 2011 6:01 pm
- Location: South Yorkshire
- Has thanked: 225 times
- Been thanked: 664 times
Wiring bathroom extractor/light off isolator switch fed by socket circuit
Interesting. Now is because the fused spur provides the required isolation?
Or the minimum wattage rule? Or as I suspect not required at all.
OnlyMe
-
- Senior Member
- Posts: 1368
- Joined: Mon May 03, 2021 1:36 pm
- Has thanked: 118 times
- Been thanked: 219 times
Wiring bathroom extractor/light off isolator switch fed by socket circuit
In this case the fan is spurred off the socket and fused down.
Somewhere in the building regs its "suggested" that for a bathroom or ensuite without windows an isolator is advantageous, but IIRC its not mandatory
Neelix
- ericmark
- Senior Member
- Posts: 4293
- Joined: Tue May 10, 2011 2:43 am
- Location: Mid Wales
- Has thanked: 118 times
- Been thanked: 785 times
Wiring bathroom extractor/light off isolator switch fed by socket circuit
The taking in account of the danger from the failure of a lighting circuit is the reason for the isolator, so should the fan become faulty it can be taken out of service allowing the lights still to be used, the same regulation is why it is often considered two RCD's are not enough, a MCB does not normally switch the neutral, a circuit = An assembly of electrical equipment supplied from the same origin and protected against overcurrent by the same protective device(s). It does not define if this overcurrent is through the circuit or from the circuit to earth (excessive protective conductor currents) so since 2008 we have needed to take into account, it does not say must, only take into account, however the problem is showing it was taken into account once it goes wrong.BS7671:2008 wrote:314.1 Every installation shall be divided into circuits, as necessary, to:
(i) avoid hazards and minimize inconvenience in the event of a fault
(ii) facilitate safe inspection, testing and maintenance (see also Section 537)
(iii) take account of danger that may arise from the failure of a single circuit such as a lighting circuit
(iv) reduce the possibility of unwanted tripping of RCDs due to excessive protective conductor currents produced by equipment in normal operation
(v) mitigate the effects of electromagnetic interferences (EMI)
(vi) prevent the indirect energizing of a circuit intended to be isolated.
So I am sure a risk assessment can be made and in light of that an isolator is not used. But the statement "There is absolutely no requirements for a 3 pole isolator for the fan" is wrong, as is a statement you must use an isolator. But any circuit altered will need RCD protection, and in a bathroom likely needs registering with the LABC. So in real terms not a DIY job as costs too much to DIY.
ericmark
-
- Newly registered Member
- Posts: 2
- Joined: Tue Jan 04, 2022 4:48 pm
- Has thanked: 0
- Been thanked: 0
Wiring bathroom extractor/light off isolator switch fed by socket circuit
Post by SilverfoxUK »
Hi
chances are you are proposing to wire the fan in a 1.0mm twin and earth. You need to consider how you are going to protect the cable. At the moment the ring main has 2 x 2.5mm² cables serving it and in the event of a short circuit they could withstand many hundreds of amps for the split second it takes to clear the 32A MCB. Your 1.0mm cable will not stand this current. To get around this you would need to install a switched fused spur from the ring main. Change the fuse in this spur to maybe 3A. (needs be no larger) A 3 pole isolating switch is a good idea but again not strictly necessary if you have to trash the fabric of the building to get it in. The fan will be operated by a pull cord in the bathroom ceiling. You can locally isolate the fan at your new switched fuse spur. 3 pole is obviously better but you have achieved electrical isolation and you have protected the cable. Box ticked.
chances are you are proposing to wire the fan in a 1.0mm twin and earth. You need to consider how you are going to protect the cable. At the moment the ring main has 2 x 2.5mm² cables serving it and in the event of a short circuit they could withstand many hundreds of amps for the split second it takes to clear the 32A MCB. Your 1.0mm cable will not stand this current. To get around this you would need to install a switched fused spur from the ring main. Change the fuse in this spur to maybe 3A. (needs be no larger) A 3 pole isolating switch is a good idea but again not strictly necessary if you have to trash the fabric of the building to get it in. The fan will be operated by a pull cord in the bathroom ceiling. You can locally isolate the fan at your new switched fuse spur. 3 pole is obviously better but you have achieved electrical isolation and you have protected the cable. Box ticked.
SilverfoxUK
Jump to
- Ultimate Handyman DIY forum
- ↳ Welcome to the Ultimate Handyman DIY Forum
- WELCOME
- ↳ WELCOME
- ↳ About the forums
- UltimateHandyman Discounts
- ↳ Ultimatehandyman Discounts
- ULTIMATE HANDYMAN COMPETITIONS
- ↳ UHM Forum competitions
- SHOW CASE- A place to show us your work
- ↳ Show Case Gallery
- ↳ Rogues Gallery
- TOOL FORUM
- ↳ Power Tool Reviews
- ↳ Bosch
- ↳ budget power tools
- ↳ Dewalt
- ↳ Festool
- ↳ Hikoki/Hitachi
- ↳ Makita
- ↳ Metabo
- ↳ Milwaukee
- ↳ Ryobi
- ↳ Tool Talk
- ↳ Bargain Tools
- ↳ Hand tool reviews
- ↳ Power Tool Manuals
- ↳ Bosch
- ↳ Dolmar
- ↳ ELEKTRA BECKUM
- ↳ Hitachi
- ↳ Husqvarna
- ↳ Jonsered
- ↳ Makita
- ↳ Stihl
- Other DIY
- ↳ Computers
- ↳ communications and broadband
- ↳ Gardeners World
- ↳ Money Saving
- ↳ Vehicle maintenance & Repair
- ↳ Energy Saving
- DIY Forum/Home improvement
- ↳ General DIY forum
- ↳ Acrylic Forum
- ↳ DIY Disasters
- ↳ Stoves
- ↳ Building Forum
- ↳ Carpentry/Joinery Forum
- ↳ Kitchen Fitting
- ↳ Damp Proofing and Remedial problems
- ↳ Electric Forum UK
- ↳ Lighting
- ↳ Alarm Manuals
- ↳ Painting & Decorating Forum
- ↳ Plastering Forum
- ↳ Plumbing Forum
- ↳ Central Heating & Boilers
- ↳ Boiler Manuals
- ↳ Alpha
- ↳ Ariston
- ↳ ATAG
- ↳ Atmos
- ↳ Baxi
- ↳ Biasi
- ↳ Broag
- ↳ Chaffoteux
- ↳ Ferroli
- ↳ Glow-worm
- ↳ Halstead
- ↳ Ideal
- ↳ Intergas
- ↳ Keston
- ↳ Myson
- ↳ Potterton
- ↳ Protherm
- ↳ Ravenheat
- ↳ Saunier Duval
- ↳ Sime
- ↳ Thorn
- ↳ Vaillant
- ↳ Viessmann
- ↳ Vokera
- ↳ warmflow
- ↳ Worcester Bosch
- ↳ Shower Manuals
- ↳ Tiling Forum
- ↳ Metalworking Forum
- General
- ↳ The Lounge
- ↳ The games corner
- ↳ The Grumpy corner
- ↳ The Sport corner
- ↳ The Cookery corner
- ↳ The Music Corner
- ↳ BUY - SELL - FREE