Is type 3 and Type C the same
Moderator: Moderators
-
- Senior Member
- Posts: 327
- Joined: Thu Jan 27, 2011 10:17 am
- Has thanked: 39 times
- Been thanked: 3 times
Is type 3 and Type C the same
I need a Type C MCB at the fuse box for my compressor.
Existing is a Dorman Smith LLR 32T3
I read on an ebay advert, that Type 3 was the Old Type C. I cannot find anything to support that.
Please could you advise if Type 3 has replaced Type C?
thank you
glassescase
Existing is a Dorman Smith LLR 32T3
I read on an ebay advert, that Type 3 was the Old Type C. I cannot find anything to support that.
Please could you advise if Type 3 has replaced Type C?
thank you
glassescase
- arco_iris
- Senior Member
- Posts: 2285
- Joined: Sat Apr 19, 2014 5:27 pm
- Location: SW Wales
- Has thanked: 184 times
- Been thanked: 535 times
Is type 3 and Type C the same
Not qualified to advise but thought your question worth googling and found this:
So looks like 'yes'.B types - 3 to 5x In
C types - 5 to 10x In
D types - 10 to 20x In
where as the old types:
type 1 - 2.7 to 4x In
type 2 - 4 to 7x In
type 3 - 7 to 10x In
-
- Senior Member
- Posts: 327
- Joined: Thu Jan 27, 2011 10:17 am
- Has thanked: 39 times
- Been thanked: 3 times
Is type 3 and Type C the same
thank you arco_iris
I took the chance and started the compressor, did not trip the "fuse". Now wondering if 32amp is too big, maximum start up current is 30 amp and running amperage is 20.
Off to recheck paper work
thanks again
glassescase
I took the chance and started the compressor, did not trip the "fuse". Now wondering if 32amp is too big, maximum start up current is 30 amp and running amperage is 20.
Off to recheck paper work
thanks again
glassescase
-
- Senior Member
- Posts: 1311
- Joined: Mon May 03, 2021 1:36 pm
- Has thanked: 117 times
- Been thanked: 214 times
Is type 3 and Type C the same
The circuit breaker is to protect the cable, not the appliance. What size is the cable AND be aware that unless you verify the Zs use of a type 3 or C type isn’t a great ideaglassescase wrote: ↑Sun Mar 20, 2022 2:27 pm thank you arco_iris
I took the chance and started the compressor, did not trip the "fuse". Now wondering if 32amp is too big, maximum start up current is 30 amp and running amperage is 20.
Off to recheck paper work
thanks again
glassescase
-
- Senior Member
- Posts: 327
- Joined: Thu Jan 27, 2011 10:17 am
- Has thanked: 39 times
- Been thanked: 3 times
Is type 3 and Type C the same
Type C is in the instructions. what is Zs? 6mm cable should doNeelix wrote: ↑Sun Mar 20, 2022 5:43 pmThe circuit breaker is to protect the cable, not the appliance. What size is the cable AND be aware that unless you verify the Zs use of a type 3 or C type isn’t a great ideaglassescase wrote: ↑Sun Mar 20, 2022 2:27 pm thank you arco_iris
I took the chance and started the compressor, did not trip the "fuse". Now wondering if 32amp is too big, maximum start up current is 30 amp and running amperage is 20.
Off to recheck paper work
thanks again
glassescase
glassescase
- wine~o
- Senior Member
- Posts: 26279
- Joined: Sat Jan 10, 2009 3:49 pm
- Location: hants/dorset border
- Has thanked: 1414 times
- Been thanked: 4019 times
Is type 3 and Type C the same
glassescase, Zs is a measurement of sorts, Loop impedance and resistance. Not summat that the above average DIYer can measure. Just because electrics work doesn't mean it's safe.
Verwood Handyman
_____________________________________________________________________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :
http://www.donnasdreamhouse.co.uk
_____________________________________________________________________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :
http://www.donnasdreamhouse.co.uk
-
- Approved Electrician
- Posts: 3117
- Joined: Sun Apr 24, 2011 6:01 pm
- Location: South Yorkshire
- Has thanked: 225 times
- Been thanked: 662 times
Is type 3 and Type C the same
The OSG gives maximum lengths for different cable sizes according to what size/type of MCB is used/type of supply to the house/RCD or no RCD protection.
OK so it's only a rule of thumb but could be used to help out the OP.
-
- Senior Member
- Posts: 327
- Joined: Thu Jan 27, 2011 10:17 am
- Has thanked: 39 times
- Been thanked: 3 times
Is type 3 and Type C the same
OSG?
Glassescase
-
- Senior Member
- Posts: 1311
- Joined: Mon May 03, 2021 1:36 pm
- Has thanked: 117 times
- Been thanked: 214 times
Is type 3 and Type C the same
OSG = BS 7671 On Site Guide - used by sparksglassescase wrote: ↑Tue Mar 22, 2022 6:59 pmOSG?
Glassescase
-
- Approved Electrician
- Posts: 3117
- Joined: Sun Apr 24, 2011 6:01 pm
- Location: South Yorkshire
- Has thanked: 225 times
- Been thanked: 662 times
Is type 3 and Type C the same
And it does list some scenarios where the OP may be OK with a 32A C type MCB. And some where it's not
-
- Senior Member
- Posts: 327
- Joined: Thu Jan 27, 2011 10:17 am
- Has thanked: 39 times
- Been thanked: 3 times
Is type 3 and Type C the same
what are the not ones? I dont have a copy but a sparks did my wiring at the other house and used a type c.
Glassescase
-
- Approved Electrician
- Posts: 3117
- Joined: Sun Apr 24, 2011 6:01 pm
- Location: South Yorkshire
- Has thanked: 225 times
- Been thanked: 662 times
Is type 3 and Type C the same
You need to know what type of supply you have to the house. If you do not know what that means it's probably easier to post a photo of your electrical cut out/main incoming fuse etc and I am sure we can tell you. Or a sticker saying PME connection on the main fuse holder usually gives the game away:-)
The worst case is a TN-S supply with no RCD. Any idea of the length of cable from the CU to the compressor? Is it direct from the main CU or from from a garage CU? These questions and their answers do make a difference.
The worst case is a TN-S supply with no RCD. Any idea of the length of cable from the CU to the compressor? Is it direct from the main CU or from from a garage CU? These questions and their answers do make a difference.
-
- Senior Member
- Posts: 1311
- Joined: Mon May 03, 2021 1:36 pm
- Has thanked: 117 times
- Been thanked: 214 times
- ericmark
- Senior Member
- Posts: 4265
- Joined: Tue May 10, 2011 2:43 am
- Location: Mid Wales
- Has thanked: 117 times
- Been thanked: 783 times
Is type 3 and Type C the same
The magnetic part of a MCB/RCBO works in around 0.01 seconds, where the thermal part can take far longer to work, so to ensure the magnetic part can work the prospective short circuit current (PSCC) needs to be high enough, ohms law means we can express it as either PSCC or in impedance, so type C will trip at 10 times rated thermal trip current using magnetic part, we allow for a 5% volt drop, so working on 218.5 volt, so 218.5/320 = 0.68Ω and the DNO supply is normally around 0.35Ω so 0.33Ω for internal wiring, so a 6 mm² cable is around 0.0073Ω per meter, so around a 45 meter limit for the cable, with 4 mm² then 0.011Ω so 30 meter maximum.
Since the Tabulated mV/A/m is affected by temperature there is a Correction factor Ct so not exactly to those figures, but near enough.
This is what it being refereed to when talking about Ze.
Since the Tabulated mV/A/m is affected by temperature there is a Correction factor Ct so not exactly to those figures, but near enough.
This is what it being refereed to when talking about Ze.
- These users thanked the author ericmark for the post:
- glassescase (Tue Mar 22, 2022 9:42 pm)
- Rating: 7.14%
-
- Senior Member
- Posts: 327
- Joined: Thu Jan 27, 2011 10:17 am
- Has thanked: 39 times
- Been thanked: 3 times
Is type 3 and Type C the same
compressor is served from the consumer unit in the garage, a bit over 10 meters may be around 15 meters. The house consumer unit has a 40 amp cct breaker serving the garage. The incoming main goes to a "grey box" that has series 7, type 2b and BS1361 stamped on it. I say 2b, it is roman numerals like a capitol i but I cant type a proper capitol i. From there to a meter and from the meter to a fuse? The consumer unit in the garage did have a fuse location already marked up as compressor. Could not see a sticker.OnlyMe wrote: ↑Tue Mar 22, 2022 7:36 pm You need to know what type of supply you have to the house. If you do not know what that means it's probably easier to post a photo of your electrical cut out/main incoming fuse etc and I am sure we can tell you. Or a sticker saying PME connection on the main fuse holder usually gives the game away:-)
The worst case is a TN-S supply with no RCD. Any idea of the length of cable from the CU to the compressor? Is it direct from the main CU or from from a garage CU? These questions and their answers do make a difference.
glassescase