40mm Waste Pipe Through Stud Wall
Moderator: Moderators
-
- Newly registered Member
- Posts: 11
- Joined: Sat Apr 06, 2019 1:07 pm
- Has thanked: 0
- Been thanked: 0
40mm Waste Pipe Through Stud Wall
I am planning to build a 2.6m x 2.4m stud wall with 4x2 (89mmx38mm) and would like to run a 40mm (43mm outer diameter) waste pipe through the length of the wall.
The wall is not load bearing but I am planning to board with waterproof tile backer boards and then tile with large 1200x600mm tiles on both sides of the wall (bathroom on one side, ensuite on the other). Wall hung basin and a mirror cabinet will go on one side of the wall.
Studs will be positioned at 400mm centres and I will need to drill through all studs to run the pipe.
(89mm - 43mm) / 2 = 23mm left on each side of the hole (48% removed).
Would this be acceptable or will the strength of the wall be too compromised for what I want to use it for?
I have seen some suggestions of boarding with OSB to add more strength? Happy to do it but will it help and is it necessary? Is 9mm OSB enough?
Many thanks.
The wall is not load bearing but I am planning to board with waterproof tile backer boards and then tile with large 1200x600mm tiles on both sides of the wall (bathroom on one side, ensuite on the other). Wall hung basin and a mirror cabinet will go on one side of the wall.
Studs will be positioned at 400mm centres and I will need to drill through all studs to run the pipe.
(89mm - 43mm) / 2 = 23mm left on each side of the hole (48% removed).
Would this be acceptable or will the strength of the wall be too compromised for what I want to use it for?
I have seen some suggestions of boarding with OSB to add more strength? Happy to do it but will it help and is it necessary? Is 9mm OSB enough?
Many thanks.
- arco_iris
- Senior Member
- Posts: 2285
- Joined: Sat Apr 19, 2014 5:27 pm
- Location: SW Wales
- Has thanked: 184 times
- Been thanked: 535 times
40mm Waste Pipe Through Stud Wall
Have you considered that (a) 43mm pipe through 43mm hole will be a very tight fit (b) each hole will need to be at a slight angle as the pipe will have a fall on it (c) each hole will need to be a tad lower than the one before. For these reasons, the holes will need to be 50mm to provide tolerance.
And so your studs become even more compromised, to 20mm each side.
So, erect the studs, use a straight edge to mark out the fall/pipe run, notch out the studs from one side only to 44mm (don't bother with holesaw), leaving 45mm at the back, lay in the waste pipe, then OSB or ply the face to provide some strength to support the tiling. Use plenty of screws but DO NOT SCREW THROUGH WHERE THE PIPE RUNS!
18mm board would be better than 9mm IMHO.
Why 40mm waste pipe? Basins only needs 32mm waste, the shower waste will be under the floor.
And so your studs become even more compromised, to 20mm each side.
So, erect the studs, use a straight edge to mark out the fall/pipe run, notch out the studs from one side only to 44mm (don't bother with holesaw), leaving 45mm at the back, lay in the waste pipe, then OSB or ply the face to provide some strength to support the tiling. Use plenty of screws but DO NOT SCREW THROUGH WHERE THE PIPE RUNS!
18mm board would be better than 9mm IMHO.
Why 40mm waste pipe? Basins only needs 32mm waste, the shower waste will be under the floor.
-
- Newly registered Member
- Posts: 11
- Joined: Sat Apr 06, 2019 1:07 pm
- Has thanked: 0
- Been thanked: 0
40mm Waste Pipe Through Stud Wall
Thanks for your reply, makes sense. I thought drilling holes retains more strength Vs notching.
Can I use some steel plates if I notch or is OSB still a better option?
40mm because it will be a ~2.5m run. Apparently regs say 32mm can only be run 1.7m max.
Can I use some steel plates if I notch or is OSB still a better option?
40mm because it will be a ~2.5m run. Apparently regs say 32mm can only be run 1.7m max.
-
- Senior Member
- Posts: 8709
- Joined: Wed Apr 16, 2008 6:49 pm
- Location: south tyneside
- Has thanked: 32 times
- Been thanked: 805 times
40mm Waste Pipe Through Stud Wall
having read it again ha.... id be going maybe 5x2 to be honest and notching one side. drilling holes through would be a reet nightmare and trying to get the pipe in and lined up would be a task and a half. also as above 32mm pipe would be the way to go
-
- Senior Member
- Posts: 16935
- Joined: Fri Jan 20, 2006 5:51 pm
- Location: Essex
- Has thanked: 807 times
- Been thanked: 3496 times
40mm Waste Pipe Through Stud Wall
I never like buried and hidden pipes, you know you will have to rip holes to get to any leak issues and sod's law dictates you will haveto at at some point. Do not have joints inside the wall if you go this way, just a complete pipe run.
DWD
DWD
- arco_iris
- Senior Member
- Posts: 2285
- Joined: Sat Apr 19, 2014 5:27 pm
- Location: SW Wales
- Has thanked: 184 times
- Been thanked: 535 times
40mm Waste Pipe Through Stud Wall
Hidden pipe runs need not be a problem, DWD, as there will be no leaks when properly installed, solvent weld.
Point taken regarding maximum run of 32mm waste, though I *think* you can go longer if an air admittance valve, or a separate breather pipe are installed? And the total length of run is from the basin to the soil stack, not just the length inside the room. It's surely to do with siphonage (volume/weight of water in the pipe) rather than flow?
OP's 4x2 at 89mm x 38mm is CLS, 4x2 (nominal) sawn would give 95mm - Fin's 5x2 (120mm) may be better.
Yes, by all means affix a metal plate, this will protect against putting a screw through the pipe accidentally, but may need letting in so as not to bow the surface boarding.
Point taken regarding maximum run of 32mm waste, though I *think* you can go longer if an air admittance valve, or a separate breather pipe are installed? And the total length of run is from the basin to the soil stack, not just the length inside the room. It's surely to do with siphonage (volume/weight of water in the pipe) rather than flow?
OP's 4x2 at 89mm x 38mm is CLS, 4x2 (nominal) sawn would give 95mm - Fin's 5x2 (120mm) may be better.
Yes, by all means affix a metal plate, this will protect against putting a screw through the pipe accidentally, but may need letting in so as not to bow the surface boarding.
-
- Newly registered Member
- Posts: 11
- Joined: Sat Apr 06, 2019 1:07 pm
- Has thanked: 0
- Been thanked: 0
40mm Waste Pipe Through Stud Wall
Will just be a straight pipe run with no joints, solvent weld reducer at the basin.
I think I will go with 5x2 (125x47) and will add some steel plates.
Thanks everyone.
I think I will go with 5x2 (125x47) and will add some steel plates.
Thanks everyone.