Hello Folks,
I hope this message finds everybody well. I am quite a novice when it comes to Electrics, so please bear with me!
I have recently set up a large Wardrobe containing 4 x 36w T8 Fluorescent Tubes, which I use to dry Varnish on musical instruments (I am a Luthier). I am just about to wire plugs onto each of the 4 Battens. As each tube is only 36w, I changed the Fuses in the plugs from 13 amps to 3 amps.
In regards to the 3 core flex cable I'm thinking of using, would a 0.75mm Flex cable (rated 6 amps) be OK, or would 0.5mm Flex cable (rated 3 amps) be the best in this case?
I then want all of 4 plugs go into a Masterplug SWSRG4210N 4-way plug extension lead (I only have 2 sockets in my wall).
This has a 13 amp fuse. Would it be a good idea to change the fuse on this extension lead to a 3 Amp fuse, so that it is in line with all of the plugs going into it?
All of the lights combined require only 0.6 Amps.
I'm worried that this 13 Amp fuse on the extension lead could be bad for this set up...
I would really appreciate any advice on this!
Thank you for reading.
Changing the Fuse to a different Amp amount in an extension lead...
Moderator: Moderators
-
- Newly registered Member
- Posts: 4
- Joined: Wed Oct 26, 2022 12:07 am
- Has thanked: 0
- Been thanked: 0
-
- Senior Member
- Posts: 1301
- Joined: Mon May 03, 2021 1:36 pm
- Has thanked: 117 times
- Been thanked: 212 times
Changing the Fuse to a different Amp amount in an extension lead...
Either cable is fine AS LONG as the plug for the lights has a 3A fuse in it. The fuse in the extension lead plug is largely irrelevant as long as its the one that was fitted to it when it was bought
- wine~o
- Senior Member
- Posts: 26265
- Joined: Sat Jan 10, 2009 3:49 pm
- Location: hants/dorset border
- Has thanked: 1414 times
- Been thanked: 4015 times
Changing the Fuse to a different Amp amount in an extension lead...
Just to clarify, the fuse is there to protect the cable not the appliance (in this case lights) keep the same fuse in the extension lead.
Verwood Handyman
_____________________________________________________________________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :
http://www.donnasdreamhouse.co.uk
_____________________________________________________________________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :
http://www.donnasdreamhouse.co.uk
-
- Newly registered Member
- Posts: 4
- Joined: Wed Oct 26, 2022 12:07 am
- Has thanked: 0
- Been thanked: 0
Changing the Fuse to a different Amp amount in an extension lead...
Thank you both for your kind responses. I'll leave the Extension cable as it is.
Does it really not matter to use a 0.75m flex that is rated for 6 amps on a 3 amp fuse?
Would it make any difference getting a 0.5mm flex instead, as I have read that is more appropriate for a 3 amp fuse...?
Any advice would be much appreciated.
Thank you
Does it really not matter to use a 0.75m flex that is rated for 6 amps on a 3 amp fuse?
Would it make any difference getting a 0.5mm flex instead, as I have read that is more appropriate for a 3 amp fuse...?
Any advice would be much appreciated.
Thank you
- ericmark
- Senior Member
- Posts: 4260
- Joined: Tue May 10, 2011 2:43 am
- Location: Mid Wales
- Has thanked: 116 times
- Been thanked: 782 times
Changing the Fuse to a different Amp amount in an extension lead...
No problem as long as flex rated over the fuse it is OK.spacebeetle wrote: ↑Thu Oct 27, 2022 1:23 am Does it really not matter to use a 0.75m flex that is rated for 6 amps on a 3 amp fuse?