CH stays on

Post by purpleglow »

Hello

I have NEST 3rd gen wireless thermostat and Viessmann boiler with a unvented cylinder.
The system has a honeywell mid position valve (v4073a1039) and a two position valve in Y configuration

On the app when if I switch on CH it comes on. However when I turn it off the boiler is still on.

I believe wiring is ok
On app
Both off 1,2,4,5 are live grey to mid posn live
CH on 2,3,4,5 live white/grey live
HW on 1,2,5,6 on none live
Both on 2,3,5,6 live white live

When Ch is switched off I noticed that white has 57 V. The orange wire in the wiring centre also have 57 so this is being fed to boiler. I understand this can happen with Honeywell valves but I don't get why the boiler does not switch off as it is not getting 240v

If I turn HW on and then turn it off the boiler then turn off as orange has zero

Any ideas?
Neelix
Senior Member
Posts: 1333
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 118 times
Been thanked: 215 times

CH stays on

Post by Neelix »

Has it ever worked properly?
User avatar
aeromech3
Senior Member
Posts: 3598
Joined: Fri Feb 26, 2010 11:16 am
Location: Ash Surrey
Has thanked: 177 times
Been thanked: 665 times

CH stays on

Post by aeromech3 »

Thought I'd seen this problem before, dug around and this could be the reason:-
https://diy.stackexchange.com/questions ... -only-mode

The part XEB1201 shows avail pack of 5 for about £7 from RS.