Noise from Indirect Expansion Unvented Storage Cylinder

Post by iainh »

Hi all,

Looking for some guidance on noise from an unvented cylinder. Due to the water mains pressure being a bit low we went down this route so I'm not sure what to expect noise wise as it's not a system type I'm familiar with.

Hoping someone can advise if this is a 'normal' amount of noise. I couldn't find the detail on Google and the manufacturers data doesn't appear to cover it.

Thanks

Video shared here -
VID-20230130-WA0008.mp4
(7.64 MiB) Downloaded 40 times
And photos of spec
IMG-20230130-WA0005.jpg
IMG-20230130-WA0005.jpg (135.16 KiB) Viewed 297 times
IMG-20230130-WA0006.jpg
IMG-20230130-WA0006.jpg (125.71 KiB) Viewed 297 times
IMG-20230130-WA0007.jpg
IMG-20230130-WA0007.jpg (152.24 KiB) Viewed 297 times
User avatar
Razor
Senior Member
Posts: 8760
Joined: Wed Nov 14, 2007 10:21 pm
Location: Northampton
Has thanked: 483 times
Been thanked: 1251 times

Noise from Indirect Expansion Unvented Storage Cylinder

Post by Razor »

If that's during cylinder reheat it sounds like coil resonance caused by too much flow going through the heating coil. Sometimes you need to add a lockshield valve across the flow and return before the cylinder to alter the flow rate