I have a Vokera Excel 29 gas boiler which is losing pressure. I need to drain the boiler in order to repressurise the expansion vessel back to 1 bar. Can anyone explain how to drain this boiler?

Thanks
User avatar
Someone-Else
Senior Member
Posts: 14709
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 47 times
Been thanked: 2590 times

Drain Vokera Excel 29 boiler

Post by Someone-Else »

You don't usually drain the boiler. Are you sure its the expansion vessel at fault? Did water come out of it when you tested it?

As for draining the system look for the lowest point and look for a "drain cock"
dc.jpg
dc.jpg (7.58 KiB) Viewed 751 times
Looks like the one above. You put a hose on it and open the square nut.
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
User avatar
aeromech3
Senior Member
Posts: 3598
Joined: Fri Feb 26, 2010 11:16 am
Location: Ash Surrey
Has thanked: 177 times
Been thanked: 665 times

Drain Vokera Excel 29 boiler

Post by aeromech3 »

The manual does mention the boiler drain valve, see page 5, Fig 4 item #2; in other models this is mentioned as a red knob; it is likely next to the safety valve relief pipe which leads to the outside property safety vent.
https://manualzz.com/doc/54104151/voker ... uctions#p6
thejinkazama
Newly registered Member
Posts: 2
Joined: Sun Feb 05, 2023 9:46 pm
Has thanked: 0
Been thanked: 0

Drain Vokera Excel 29 boiler

Post by thejinkazama »

There’s no air inside the expansion tank. I can’t repressurise it with a pump as there’s water in it so I’m trying to drain the water out.

Thanks for the info regarding the drain valve. How does it work? I know it can be turned but don’t see where the water inside the boiler would drain to.
Attachments
A4B945B4-0861-4D43-B254-03991BE7793E.jpeg
A4B945B4-0861-4D43-B254-03991BE7793E.jpeg (322.49 KiB) Viewed 736 times
User avatar
Someone-Else
Senior Member
Posts: 14709
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 47 times
Been thanked: 2590 times

Drain Vokera Excel 29 boiler

Post by Someone-Else »

If there is water in the expansion cylinder, you are wasting your time. The expansion cylinder is a cylinder (or circle, some are almost square) with a "balloon" in it. If the balloon gets punctured, it lets water in. It needs to be replaced, or another one added.
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
User avatar
aeromech3
Senior Member
Posts: 3598
Joined: Fri Feb 26, 2010 11:16 am
Location: Ash Surrey
Has thanked: 177 times
Been thanked: 665 times

Drain Vokera Excel 29 boiler

Post by aeromech3 »

If you just want to lower the boiler water pressure, then the knob can be turned and I am guessing the water will drain via the relief valve pipe to the outside.
If there is water on the air side of the expansion tank then this is a fault as S-E states and unlikely to drain out by the above method.
Perhaps you should explain the fault you have more precisely?