Worcester greenstar keep shutting down
Hello want to pick the brains of heating engineers on here.
Got a Worcester bosch greenstar 30si combi boiler about 12 years old. Not had a single problem with it in 12 years.
Until this week. It keeps shutting down no hot water and no hot rads. Go to the boiler to find orange reset button flashing and blue oval light flashing.
I press the reset button and the boiler tries to reset but sometimes it doesn't and a 2nd time pressing reset will work and the boiler goes back to full function. but 2/3 hours later it shuts again and i have to go through the reset process again.
I've checked the condenser pipe and looks OK. I drained the condenser trap which was a bit grey but that's all clear now. The boiler pressure is fine between 1 and 1.5bars
Any ideas what the problem would be so I know what to expect when I find a plumber to come out.
Thanks
Got a Worcester bosch greenstar 30si combi boiler about 12 years old. Not had a single problem with it in 12 years.
Until this week. It keeps shutting down no hot water and no hot rads. Go to the boiler to find orange reset button flashing and blue oval light flashing.
I press the reset button and the boiler tries to reset but sometimes it doesn't and a 2nd time pressing reset will work and the boiler goes back to full function. but 2/3 hours later it shuts again and i have to go through the reset process again.
I've checked the condenser pipe and looks OK. I drained the condenser trap which was a bit grey but that's all clear now. The boiler pressure is fine between 1 and 1.5bars
Any ideas what the problem would be so I know what to expect when I find a plumber to come out.
Thanks
- Someone-Else
- Senior Member
- Posts: 14709
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 47 times
- Been thanked: 2590 times
Worcester greenstar keep shutting down
Not wishing to be pedantic, but you want a heating engineer, NOT a plumber, they are different. Also I would suggest when you ring round, ask are they familiar with your boiler, and when they get there, show them what happens, (Make a video now while it doesn't work) never tell a tradesman what you think is wrong, that really upsets us. (I am NOT a plumber or heating engineer, nothing worse than being told how to do your job)KSProperty wrote: ↑Sun Mar 12, 2023 6:53 pmAny ideas what the problem would be so I know what to expect when I find a plumber to come out
- These users thanked the author Someone-Else for the post:
- Neelix (Mon Mar 13, 2023 8:37 am)
- Rating: 7.14%
Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
- Razor
- Senior Member
- Posts: 8760
- Joined: Wed Nov 14, 2007 10:21 pm
- Location: Northampton
- Has thanked: 483 times
- Been thanked: 1251 times
Worcester greenstar keep shutting down
Your need to see what the flashing means. There is a list in your manual as to whether it’s mostly on but flashing off or mostly off but flashing on etc.
Most installers are familiar with WB boilers
Most installers are familiar with WB boilers
I think I'll take two chickens...
- aeromech3
- Senior Member
- Posts: 3598
- Joined: Fri Feb 26, 2010 11:16 am
- Location: Ash Surrey
- Has thanked: 177 times
- Been thanked: 665 times
Worcester greenstar keep shutting down
As per Razor you need a list similar to this post 2009 Greenstar exaample.
Was the trap ever full and overflow or signs of water leakage?
Was the trap ever full and overflow or signs of water leakage?
- Attachments
-
- Flash.png (200.13 KiB) Viewed 485 times
-
- Senior Member
- Posts: 157
- Joined: Tue Nov 18, 2014 6:01 pm
- Has thanked: 30 times
- Been thanked: 6 times
Worcester greenstar keep shutting down
Thanks for replies.
I would say the blue light looks like it's off flashing on type
I would say the blue light looks like it's off flashing on type
- wine~o
- Senior Member
- Posts: 26293
- Joined: Sat Jan 10, 2009 3:49 pm
- Location: hants/dorset border
- Has thanked: 1415 times
- Been thanked: 4024 times
Worcester greenstar keep shutting down
flashing on what ?KSProperty wrote: ↑Mon Mar 13, 2023 5:08 pm I would say the blue light looks like it's off flashing on type
Verwood Handyman
_____________________________________________________________________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :
http://www.donnasdreamhouse.co.uk
_____________________________________________________________________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :
http://www.donnasdreamhouse.co.uk
- Razor
- Senior Member
- Posts: 8760
- Joined: Wed Nov 14, 2007 10:21 pm
- Location: Northampton
- Has thanked: 483 times
- Been thanked: 1251 times
Worcester greenstar keep shutting down
In that case you will need a decent registered gas bod. It's not going to be DIYable. Armed with the info from the light they will sort it out pretty quicklyKSProperty wrote: ↑Mon Mar 13, 2023 5:08 pm Thanks for replies.
I would say the blue light looks like it's off flashing on type
I think I'll take two chickens...
-
- Senior Member
- Posts: 157
- Joined: Tue Nov 18, 2014 6:01 pm
- Has thanked: 30 times
- Been thanked: 6 times
Worcester greenstar keep shutting down
Update. Boiler fixed. Gas engineer been out and said its an ignition lockout and changed the electrodes. And a service.
Thanks
Thanks
- Razor
- Senior Member
- Posts: 8760
- Joined: Wed Nov 14, 2007 10:21 pm
- Location: Northampton
- Has thanked: 483 times
- Been thanked: 1251 times
Worcester greenstar keep shutting down
Thanks for the update. Bet it’s not lighting with a bang anymore