How bad is the pressure from the network, and maybe it changed and increased and allowed the 1.5bar change and then dropped againJust had this text tho:
Good morning, it's Connor from United Utilities. Just to let you know, we've found the cause of poor pressure in your area to be a technical fault on ourwater network. We're onsite and ready to begin the repairs. Sorry for any inconvenience, we'll have things back to normal as quickly as possible.
Can’t repressurise boiler (low mains pressure)
Moderator: Moderators
- etaf
- Senior Member
- Posts: 948
- Joined: Sat Nov 15, 2008 10:27 am
- Location: West Sussex, on coast
- Has thanked: 38 times
- Been thanked: 151 times
Can’t repressurise boiler (low mains pressure)
Simple DIYer
Wayne
Wayne
-
- Newly registered Member
- Posts: 45
- Joined: Wed Feb 22, 2023 11:19 am
- Has thanked: 9 times
- Been thanked: 0
Can’t repressurise boiler (low mains pressure)
toying with that as feasible… currently awaiting delivery of a pressure gauge (due today) that will hopefully take away some of the guessing!etaf wrote: ↑Sat Dec 30, 2023 11:50 amHow bad is the pressure from the network, and maybe it changed and increased and allowed the 1.5bar change and then dropped againJust had this text tho:
Good morning, it's Connor from United Utilities. Just to let you know, we've found the cause of poor pressure in your area to be a technical fault on ourwater network. We're onsite and ready to begin the repairs. Sorry for any inconvenience, we'll have things back to normal as quickly as possible.
-
- Newly registered Member
- Posts: 45
- Joined: Wed Feb 22, 2023 11:19 am
- Has thanked: 9 times
- Been thanked: 0
Can’t repressurise boiler (low mains pressure)
So whilst waiting on my pressure gauge delivery (cmon Mr.Amazon man!), the plumber popped by an hour ago with his. We are getting 1 bar downstairs (he put his finger over the tap to prove it), so by the time it is getting upstairs, we’re onto a loser.
Meanwhile, United Utilities text me this morning saying there was a new problem in the area. I’ve spoken to them and they will investigate tomorrow. In the meantime, I’ve checked their website and it says the issue has been fixed in the last hour, so about to try again because the pressure looks better (or is it in my head now… I tried to put my finger over the tap and got soaked )
Meanwhile, United Utilities text me this morning saying there was a new problem in the area. I’ve spoken to them and they will investigate tomorrow. In the meantime, I’ve checked their website and it says the issue has been fixed in the last hour, so about to try again because the pressure looks better (or is it in my head now… I tried to put my finger over the tap and got soaked )
-
- Senior Member
- Posts: 17058
- Joined: Fri Jan 20, 2006 5:51 pm
- Location: Essex
- Has thanked: 820 times
- Been thanked: 3519 times
Can’t repressurise boiler (low mains pressure)
Did you bleed the radiators? This might be the issue, start upstairs and systematically bleed the radiators with the fill valve open. Take some kitchen roll to catch the weep when it comes.
DWD
DWD
-
- Newly registered Member
- Posts: 45
- Joined: Wed Feb 22, 2023 11:19 am
- Has thanked: 9 times
- Been thanked: 0
Can’t repressurise boiler (low mains pressure)
Yeah - tried that and made no difference unfortunately. Thanks thodewaltdisney wrote: ↑Sat Dec 30, 2023 4:40 pm Did you bleed the radiators? This might be the issue, start upstairs and systematically bleed the radiators with the fill valve open. Take some kitchen roll to catch the weep when it comes.
DWD
-
- Newly registered Member
- Posts: 45
- Joined: Wed Feb 22, 2023 11:19 am
- Has thanked: 9 times
- Been thanked: 0
- Razor
- Senior Member
- Posts: 8760
- Joined: Wed Nov 14, 2007 10:21 pm
- Location: Northampton
- Has thanked: 483 times
- Been thanked: 1251 times
Can’t repressurise boiler (low mains pressure)
See if your gas guy can pop back in.
He needs to depressurise the expansion vessel then fully fill the system leaving it on 0.3 bar or so.
Then if he pumps up the expansion vessel you will have full pressure.
BTW when the water properly goes back on you need to run the cold tap on it's own for 20 mins or so just in case there's any debris in the pipework. You really don't need anything being pulled in to the boiler
He needs to depressurise the expansion vessel then fully fill the system leaving it on 0.3 bar or so.
Then if he pumps up the expansion vessel you will have full pressure.
BTW when the water properly goes back on you need to run the cold tap on it's own for 20 mins or so just in case there's any debris in the pipework. You really don't need anything being pulled in to the boiler
I think I'll take two chickens...
-
- Newly registered Member
- Posts: 45
- Joined: Wed Feb 22, 2023 11:19 am
- Has thanked: 9 times
- Been thanked: 0
Can’t repressurise boiler (low mains pressure)
So this morning, the water pressure has finally been fixed! Not happy with United Utilities, and haven’t felt like I’ve achieved a lot over the past few days (couldn’t get the boiler working) but I did learn a fair bit. So thanks all.
My plan if it wasn’t sorted today, was to get a water pressure test pump to try and force the water into the system (a bit like this https://www.amazon.co.uk/318927-Install ... 00KBQPMII/ ) but I hadn’t fully thought it thru (and didn’t even know if it would work!)
We’ve gone from 0.7 bar at the boiler to approx 2 bar tho so all is good.
Thanks again
My plan if it wasn’t sorted today, was to get a water pressure test pump to try and force the water into the system (a bit like this https://www.amazon.co.uk/318927-Install ... 00KBQPMII/ ) but I hadn’t fully thought it thru (and didn’t even know if it would work!)
We’ve gone from 0.7 bar at the boiler to approx 2 bar tho so all is good.
Thanks again
-
- Senior Member
- Posts: 17058
- Joined: Fri Jan 20, 2006 5:51 pm
- Location: Essex
- Has thanked: 820 times
- Been thanked: 3519 times
Can’t repressurise boiler (low mains pressure)
Glad you got it sorted, Connor the autobot was useless
DWD
DWD