Ceiling rose to spot lights
All electrical lighting questions in here please. Including outside lighting and light switch / dimmer questions.
Moderator: Moderators
-
- Senior Member
- Posts: 311
- Joined: Sun May 11, 2014 7:30 pm
- Has thanked: 0
- Been thanked: 2 times
Ceiling rose to spot lights
Post by AndyBaldock »
Good evening,
I have installed spot lights before from the end of a circuit and it was very easy because I had one wire to work with. I have now got to install ceiling lights but there is currently a ceiling rose with 3 wires meeting. The switch wire is clearly indicated and the ceiling is down so I can see everything.
My preferred method is wagos but I was just wondering how I go from 3 wires to spot lights.
Happy to get an electrician but my curiosity is getting the better of me and I will want to know regardless. I’m thinking I need to get three of the wires to begin the spot lights and daisy chain it along but which 3. Any thoughts greatly received. Like I say, I’ll probably get an electrician eventually but I’d like to know either way.
Many thanks
I have installed spot lights before from the end of a circuit and it was very easy because I had one wire to work with. I have now got to install ceiling lights but there is currently a ceiling rose with 3 wires meeting. The switch wire is clearly indicated and the ceiling is down so I can see everything.
My preferred method is wagos but I was just wondering how I go from 3 wires to spot lights.
Happy to get an electrician but my curiosity is getting the better of me and I will want to know regardless. I’m thinking I need to get three of the wires to begin the spot lights and daisy chain it along but which 3. Any thoughts greatly received. Like I say, I’ll probably get an electrician eventually but I’d like to know either way.
Many thanks
AndyBaldock
- Someone-Else
- Senior Member
- Posts: 14827
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 48 times
- Been thanked: 2604 times
Ceiling rose to spot lights
Post by Someone-Else »
Yes, wagos in a box is the way to go.
One cable is feed in (From previous light or Consumers unit)
One cable is feed out (To next set of lights)
One cable is switch cable (Guess where it goes)
Once this has been done you add a 4th cable that goes to the first downlight, then loops to the other downlights.
One cable is feed in (From previous light or Consumers unit)
One cable is feed out (To next set of lights)
One cable is switch cable (Guess where it goes)
Once this has been done you add a 4th cable that goes to the first downlight, then loops to the other downlights.
Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section

Someone-Else
-
- Senior Member
- Posts: 311
- Joined: Sun May 11, 2014 7:30 pm
- Has thanked: 0
- Been thanked: 2 times
Ceiling rose to spot lights
Post by AndyBaldock »
Thank you for your response. From the diagram attached, if the spotlights are double insulated and don’t need an earth, do I just attach twin core? That’s a shame because I’ve got lots of twin core and earth in the shed.
- Attachments
-
- IMG_8528.jpeg (243.82 KiB) Viewed 932 times
AndyBaldock
-
- Senior Member
- Posts: 311
- Joined: Sun May 11, 2014 7:30 pm
- Has thanked: 0
- Been thanked: 2 times
Ceiling rose to spot lights
Post by AndyBaldock »
Tried it on one light as a test. Works fine, thanks very much. Would everyone recommend 1mm cable for 4 down lights or is 1.5mm better? I have both.
AndyBaldock
- Someone-Else
- Senior Member
- Posts: 14827
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 48 times
- Been thanked: 2604 times
Ceiling rose to spot lights
Post by Someone-Else »
You must have an earth at each light and 1mm T & E is fine
Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section

Someone-Else
-
- Senior Member
- Posts: 311
- Joined: Sun May 11, 2014 7:30 pm
- Has thanked: 0
- Been thanked: 2 times
Ceiling rose to spot lights
Post by AndyBaldock »
Thank you but the lights only have live and neutral. There is no terminal for earth.Someone-Else wrote: ↑Sun Apr 07, 2024 10:52 am You must have an earth at each light and 1mm T & E is fine
AndyBaldock
- Someone-Else
- Senior Member
- Posts: 14827
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 48 times
- Been thanked: 2604 times
Ceiling rose to spot lights
Post by Someone-Else »
As I said, you must have an earth at each light. Suppose next week you change them to a different light that does have an earth, what will you do?
Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section

Someone-Else
-
- Senior Member
- Posts: 311
- Joined: Sun May 11, 2014 7:30 pm
- Has thanked: 0
- Been thanked: 2 times
Ceiling rose to spot lights
Post by AndyBaldock »
Thank you. All done and installed. Will get an electrician to check when sockets get checked before a new kitchen goes in. Thanks for your help.
AndyBaldock
- Someone-Else
- Senior Member
- Posts: 14827
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 48 times
- Been thanked: 2604 times
Ceiling rose to spot lights
Post by Someone-Else »

Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section

Someone-Else
Jump to
- Ultimate Handyman DIY forum
- ↳ Welcome to the Ultimate Handyman DIY Forum
- WELCOME
- ↳ WELCOME
- ↳ About the forums
- UltimateHandyman Discounts
- ↳ Ultimatehandyman Discounts
- ULTIMATE HANDYMAN COMPETITIONS
- ↳ UHM Forum competitions
- SHOW CASE- A place to show us your work
- ↳ Show Case Gallery
- ↳ Rogues Gallery
- TOOL FORUM
- ↳ Power Tool Reviews
- ↳ Bosch
- ↳ budget power tools
- ↳ Dewalt
- ↳ Festool
- ↳ Hikoki/Hitachi
- ↳ Makita
- ↳ Metabo
- ↳ Milwaukee
- ↳ Ryobi
- ↳ Tool Talk
- ↳ Bargain Tools
- ↳ Hand tool reviews
- ↳ Power Tool Manuals
- ↳ Bosch
- ↳ Dolmar
- ↳ ELEKTRA BECKUM
- ↳ Hitachi
- ↳ Husqvarna
- ↳ Jonsered
- ↳ Makita
- ↳ Stihl
- Other DIY
- ↳ Computers
- ↳ communications and broadband
- ↳ Gardeners World
- ↳ Money Saving
- ↳ Vehicle maintenance & Repair
- ↳ Energy Saving
- DIY Forum/Home improvement
- ↳ General DIY forum
- ↳ Acrylic Forum
- ↳ DIY Disasters
- ↳ Stoves
- ↳ Building Forum
- ↳ Carpentry/Joinery Forum
- ↳ Kitchen Fitting
- ↳ Damp Proofing and Remedial problems
- ↳ Electric Forum UK
- ↳ Lighting
- ↳ Alarm Manuals
- ↳ Painting & Decorating Forum
- ↳ Plastering Forum
- ↳ Plumbing Forum
- ↳ Central Heating & Boilers
- ↳ Boiler Manuals
- ↳ Alpha
- ↳ Ariston
- ↳ ATAG
- ↳ Atmos
- ↳ Baxi
- ↳ Biasi
- ↳ Broag
- ↳ Chaffoteux
- ↳ Ferroli
- ↳ Glow-worm
- ↳ Halstead
- ↳ Ideal
- ↳ Intergas
- ↳ Keston
- ↳ Myson
- ↳ Potterton
- ↳ Protherm
- ↳ Ravenheat
- ↳ Saunier Duval
- ↳ Sime
- ↳ Thorn
- ↳ Vaillant
- ↳ Viessmann
- ↳ Vokera
- ↳ warmflow
- ↳ Worcester Bosch
- ↳ Shower Manuals
- ↳ Tiling Forum
- ↳ Metalworking Forum
- General
- ↳ The Lounge
- ↳ The games corner
- ↳ The Grumpy corner
- ↳ The Sport corner
- ↳ The Cookery corner
- ↳ The Music Corner
- ↳ BUY - SELL - FREE