Compliance certificates

All your electrical questions regarding electrics from within the United Kingdom

Moderator: Moderators

Dxc712
Senior Member
Posts: 351
Joined: Sun Aug 19, 2018 3:42 pm
Has thanked: 165 times
Been thanked: 3 times

Compliance certificates

Post by Dxc712 »

I've recently had an instantaneous water heater installed.

I've asked to be provided with a certificate for the work.

In what cases is a compliance certificate needed and what's the process for judging that the work is granted the certificate?

Thanks
Neelix
Senior Member
Posts: 1310
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 117 times
Been thanked: 213 times

Compliance certificates

Post by Neelix »

Was a new circuit added to your fuseboard / consumer unit ?
These users thanked the author Neelix for the post:
Dxc712 (Sun Aug 11, 2024 12:15 am)
Rating: 7.14%
Dxc712
Senior Member
Posts: 351
Joined: Sun Aug 19, 2018 3:42 pm
Has thanked: 165 times
Been thanked: 3 times

Compliance certificates

Post by Dxc712 »

Neelix wrote: Sat Aug 10, 2024 9:42 pm Was a new circuit added to your fuseboard / consumer unit ?
These photos show the work that was done.
Attachments
This is the consumer unit before the work was done
This is the consumer unit before the work was done
1.jpg (64.16 KiB) Viewed 507 times
This shows the black cable that is now going into the side
This shows the black cable that is now going into the side
2.jpg (108.35 KiB) Viewed 507 times
This is a close up of the new fuse
This is a close up of the new fuse
3.jpg (101.19 KiB) Viewed 507 times
User avatar
ericmark
Senior Member
Posts: 4261
Joined: Tue May 10, 2011 2:43 am
Location: Mid Wales
Has thanked: 116 times
Been thanked: 783 times

Compliance certificates

Post by ericmark »

That is a type AC RCBO and today we normally use type A and the consumer unit seems to be fusebox, but the new RCBO is British General this rings alarm bells to me. Most seems to be wired in mineral insulated cable, only the new circuit is not, and so one wonders why?

It however may be compliant, but the electrician will need to be a scheme member to get that certificate, the other option is to get a completion certificate, it is clearly a new circuit so it will in England or Wales require one.
These users thanked the author ericmark for the post:
Dxc712 (Sun Aug 11, 2024 12:09 pm)
Rating: 7.14%
Dxc712
Senior Member
Posts: 351
Joined: Sun Aug 19, 2018 3:42 pm
Has thanked: 165 times
Been thanked: 3 times

Compliance certificates

Post by Dxc712 »

ericmark wrote: Sun Aug 11, 2024 4:18 am That is a type AC RCBO and today we normally use type A and the consumer unit seems to be fusebox, but the new RCBO is British General this rings alarm bells to me. Most seems to be wired in mineral insulated cable, only the new circuit is not, and so one wonders why?

It however may be compliant, but the electrician will need to be a scheme member to get that certificate, the other option is to get a completion certificate, it is clearly a new circuit so it will in England or Wales require one.
Thanks for your response.

I don't know anything about this. What is that rings alarm bells for you?
OnlyMe
Approved Electrician
Posts: 3116
Joined: Sun Apr 24, 2011 6:01 pm
Location: South Yorkshire
Has thanked: 225 times
Been thanked: 662 times

Compliance certificates

Post by OnlyMe »

That will be a type A RCBO. It's the CUCRB40A (from the Fortress range) not the AC type that would have been labelled CUCR40A.

However it should not be a BG RCBO. The circuit should also be labelled up.

As it's a new circuit you need an electrical installation certificate.
These users thanked the author OnlyMe for the post:
Dxc712 (Sun Aug 11, 2024 9:33 pm)
Rating: 7.14%
Neelix
Senior Member
Posts: 1310
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 117 times
Been thanked: 213 times

Compliance certificates

Post by Neelix »

Mix and match isn’t permitted. Get the muppet ego out that BG junk in the fuseboard back to fit the correct part.

So they owe you an EIC and if you are in England or Wales a part P compliance document
Dxc712
Senior Member
Posts: 351
Joined: Sun Aug 19, 2018 3:42 pm
Has thanked: 165 times
Been thanked: 3 times

Compliance certificates

Post by Dxc712 »

I'm sorry but I don't understand any of these responses as they use technical jargon that I'm not familiar with.
Dxc712
Senior Member
Posts: 351
Joined: Sun Aug 19, 2018 3:42 pm
Has thanked: 165 times
Been thanked: 3 times

Compliance certificates

Post by Dxc712 »

Neelix wrote: Sun Aug 11, 2024 4:17 pm Mix and match isn’t permitted.
Which bit is the mix and match? The cable going into the side of the consumer unit or the new fuse?
Neelix wrote: Sun Aug 11, 2024 4:17 pm Get the muppet ego out that BG junk in the fuseboard back to fit the correct part.
Did you mean to say 'Get the muppet who put that BG junk in the fuseboard back to fit the correct part' ?

What is the correct part that should have been fitted?

I don't understand what the problem is and so I won't be explain it to him. Any answer he gives will be something I can't respond to.

I won't be able to discuss something I don't understand.
Neelix wrote: Sun Aug 11, 2024 4:17 pm So they owe you an EIC and if you are in England or Wales a part P compliance document
I live in England. Will anyone providing these documents have to come back to access the work first?
Dxc712
Senior Member
Posts: 351
Joined: Sun Aug 19, 2018 3:42 pm
Has thanked: 165 times
Been thanked: 3 times

Compliance certificates

Post by Dxc712 »

Can somebody please explain to me in non-technical terms what the problem is here and what needs to be changed?

For example, what needs to be taken out and what should replace it?

Is there and issue with the cable going into the side of the consumer unit or has the wrong fuse been put in? Or is it both?

I'm sorry but I'm struggling to follow the jargon.
Neelix
Senior Member
Posts: 1310
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 117 times
Been thanked: 213 times

Compliance certificates

Post by Neelix »

Just copy and paste my post into an email to the muppet you paid to install this and see what they say
Dxc712
Senior Member
Posts: 351
Joined: Sun Aug 19, 2018 3:42 pm
Has thanked: 165 times
Been thanked: 3 times

Compliance certificates

Post by Dxc712 »

Neelix wrote: Sun Aug 11, 2024 8:45 pm Just copy and paste my post into an email to the muppet you paid to install this and see what they say
Thanks but first I want to have some understanding of what the issue is otherwise I won't be able to discuss it.

For example, I won't know if the correct part has been fitted if I don't know what the correct part is.

From what I can gather from the above posts, the wrong circuit breaker has been put into the consumer unit.

A British General circuit breaker has been fitted. Just so I understand, why is that the wrong to have done?

Type A and type AC have also been mentioned in this thread.

Which type should have been fitted instead? Is it type A?

Is there a specific name for the correct circuit breaker that should have been fitted?

Is there any problem with the cable that has gone into the side of the consumer unit?

Thanks
Dxc712
Senior Member
Posts: 351
Joined: Sun Aug 19, 2018 3:42 pm
Has thanked: 165 times
Been thanked: 3 times

Compliance certificates

Post by Dxc712 »

OnlyMe wrote: Sun Aug 11, 2024 3:26 pm That will be a type A RCBO. It's the CUCRB40A (from the Fortress range) not the AC type that would have been labelled CUCR40A.

However it should not be a BG RCBO. The circuit should also be labelled up.

As it's a new circuit you need an electrical installation certificate.
Thanks. If it should not be a BG RCBO could you explain why that is and what should be there instead?

Am I correct in assuming that there isn't an issue with a cable going into the side of the consumer unit?
Neelix
Senior Member
Posts: 1310
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 117 times
Been thanked: 213 times

Compliance certificates

Post by Neelix »

Dxc712 wrote: Sun Aug 11, 2024 8:53 pm
Neelix wrote: Sun Aug 11, 2024 8:45 pm Just copy and paste my post into an email to the muppet you paid to install this and see what they say
Thanks but first I want to have some understanding of what the issue is otherwise I won't be able to discuss it.

For example, I won't know if the correct part has been fitted if I don't know what the correct part is.

From what I can gather from the above posts, the wrong <a href="http://shop.ebay.co.uk/?_nkw=circuit+breaker" class="skimwords-link" target="_blank" data-skimwords-id="877256" data-skimwords-word="circuit%20breaker" data-group-id="0" data-skim-creative="300003" title="Shopping Link Added by SkimWords" occurrence="1" data-skim-node-id="107:FromwhatIcangatherfr_1" style="">circuit breaker</a><span style="position: absolute;"></span><span style="position: absolute;"></span> has been put into the consumer unit.

A British General <span class="skimwords-potential">circuit breaker</span><span style="position: absolute;"></span><span style="position: absolute;"></span> has been fitted. Just so I understand, why is that the wrong to have done?

Type A and type AC have also been mentioned in this thread.

Which type should have been fitted instead? Is it type A?

Is there a specific name for the correct <span class="skimwords-potential">circuit breaker</span><span style="position: absolute;"></span><span style="position: absolute;"></span> that should have been fitted?

Is there any problem with the cable that has gone into the side of the consumer unit?

Thanks
All competent installers KNOW that mix and match isn't permitted in BS 7671

So the muppet you paid needs to return , remove the BG part and fit the appropriate breaker made by the manufacturer of the comsumer unit.

Have you got the paperwork yet?
These users thanked the author Neelix for the post:
Dxc712 (Mon Aug 12, 2024 7:14 am)
Rating: 7.14%
Dxc712
Senior Member
Posts: 351
Joined: Sun Aug 19, 2018 3:42 pm
Has thanked: 165 times
Been thanked: 3 times

Compliance certificates

Post by Dxc712 »

Neelix wrote: Mon Aug 12, 2024 6:54 am All competent installers KNOW that mix and match isn't permitted in BS 7671

So the muppet you paid needs to return , remove the BG part and fit the appropriate breaker made by the manufacturer of the comsumer unit.
Thanks. What's the right circuit breaker for the consumer unit?

Do you need me to attach more photos for you to tell?

Is there a problem having a new cable go into the side of the consumer unit?
Neelix wrote: Mon Aug 12, 2024 6:54 am Have you got the paperwork yet?
Only the invoice. He contacted me afterwards to say that he would send notice of the works over to a colleague and any compliance certificate will be with me in 7 days.