armoured cable

Post by paul777 »

hello
would I need to earth both ends of armoured cable SWA glands at both ends
or just one end
thanks paul
Neelix
Senior Member
Posts: 1304
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 117 times
Been thanked: 212 times

armoured cable

Post by Neelix »

Depends on the earthing system you have and what the swa cable is being used to connect
User avatar
ericmark
Senior Member
Posts: 4259
Joined: Tue May 10, 2011 2:43 am
Location: Mid Wales
Has thanked: 116 times
Been thanked: 782 times

armoured cable

Post by ericmark »

The SWA can be used as an earth wire, it can also be an earthed shroud only protecting the cable. We have three earth systems TN, TT, IT the latter is not earthed, these can be further split into TN-S and TN-C-S the latter is banned for caravans, boats, and similar metal clad structures, so some times we do not take the earth to the destination. But use a TT earth system instead (earth rod).

The process is complex as services can end up joining premises which it was the intension to keep isolated, some times directly with say an air line, and some times due to how close an earth rod is to it, like a water pipe.

John Ward does a good youtube video to explain.