Replaced 3 port valve, now no power

Post by Alan Dale »

Hi everybody, I have just replaced a 3 port motorised valve, I replaced the wires one at a time as I took the old ones out but I have no power going to the pump or boiler. I have valves to isolate the water going to the motorised valve and wondered if I could still have an airlock or is it something else. there is resistance on the motorised valve, any help would be appreciated, thanks.
User avatar
moderator2
UHM Super Moderator
Posts: 4577
Joined: Fri Jan 27, 2006 10:54 pm
Has thanked: 155 times
Been thanked: 569 times

Replaced 3 port valve, now no power

Post by moderator2 »

Alan Dale, I have started you a new thread and changed the title.
Alan Dale
Newly registered Member
Posts: 5
Joined: Sun Aug 28, 2022 3:39 pm
Has thanked: 2 times
Been thanked: 0

Replaced 3 port valve, now no power

Post by Alan Dale »

Thanks
User avatar
Someone-Else
Senior Member
Posts: 14710
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 47 times
Been thanked: 2590 times

Replaced 3 port valve, now no power

Post by Someone-Else »

Have you actually checked for voltage at the valve? (If so, what with?)
These users thanked the author Someone-Else for the post:
Alan Dale (Fri Oct 25, 2024 11:42 am)
Rating: 7.14%
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
Neelix
Senior Member
Posts: 1333
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 118 times
Been thanked: 215 times

Replaced 3 port valve, now no power

Post by Neelix »

Have you tripped a circuit ? Blown a fuse ?
These users thanked the author Neelix for the post:
Alan Dale (Fri Oct 25, 2024 11:42 am)
Rating: 7.14%
Alan Dale
Newly registered Member
Posts: 5
Joined: Sun Aug 28, 2022 3:39 pm
Has thanked: 2 times
Been thanked: 0

Replaced 3 port valve, now no power

Post by Alan Dale »

Thanks for responding. On the multimeter I have 240v on terminal 8 (orange). 75 v ??? on terminal 7 (grey) 240v on terminal 5 (white). Blue terminal 2, earth terminal 3. I can hear the valve working when I turn the power on. I reset the boiler and have power to it now. Thanks
Alan Dale
Newly registered Member
Posts: 5
Joined: Sun Aug 28, 2022 3:39 pm
Has thanked: 2 times
Been thanked: 0

Replaced 3 port valve, now no power

Post by Alan Dale »

I found the culprit, the plug on the pump had slightly come out, I pushed it back and it all "seems" alright now.