Vaillant Turboxmax boiler gaining pressure
Moderator: Moderators
-
- Newly registered Member
- Posts: 4
- Joined: Wed Oct 30, 2024 9:47 am
- Has thanked: 0
- Been thanked: 0
Vaillant Turboxmax boiler gaining pressure
My hot water stopped working and I noticed the pressure on my Vaillant Turbomax boiler had dropped to zero. I increased the pressure to 1.5 by opening the Filling Loop valve, but after I closed the valve, the pressure kept on rising getting very close to the red area.
I bled a radiator and it decreased a little, but then start rising again. I then released pressure using the Pressure Relief Valve and it quickly dropped down, but then immediately went up again when I released the valve, and is continuing to creep up. Is this something to worry about? Hopefully an easy fix?
I bled a radiator and it decreased a little, but then start rising again. I then released pressure using the Pressure Relief Valve and it quickly dropped down, but then immediately went up again when I released the valve, and is continuing to creep up. Is this something to worry about? Hopefully an easy fix?
- wine~o
- Senior Member
- Posts: 26279
- Joined: Sat Jan 10, 2009 3:49 pm
- Location: hants/dorset border
- Has thanked: 1414 times
- Been thanked: 4019 times
Vaillant Turboxmax boiler gaining pressure
sounds like the isolating valve isn't closed correctly, there should be 2 valves (one at each end of the filling loop )
Verwood Handyman
_____________________________________________________________________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :
http://www.donnasdreamhouse.co.uk
_____________________________________________________________________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :
http://www.donnasdreamhouse.co.uk
-
- Newly registered Member
- Posts: 4
- Joined: Wed Oct 30, 2024 9:47 am
- Has thanked: 0
- Been thanked: 0
Vaillant Turboxmax boiler gaining pressure
Thanks for getting back to me.
This boiler doesn’t have the usual taps to open and close the valves.
I've atacched a pic of the filling loop.
I increased the pressure by turning the screw in the brass cubed shaped end.
By Isolating Valve, do you mean the large black cross head at the other end of the hose? I didn’t touch this and have just had a look at it seems firmly closed, in fact I’m not sure I can loosen it with a screwdriver.
The gauge has been fluctuating over the last 24hrs, but remains high and is currently approaching maximum now. Is this dangerous?
This boiler doesn’t have the usual taps to open and close the valves.
I've atacched a pic of the filling loop.
I increased the pressure by turning the screw in the brass cubed shaped end.
By Isolating Valve, do you mean the large black cross head at the other end of the hose? I didn’t touch this and have just had a look at it seems firmly closed, in fact I’m not sure I can loosen it with a screwdriver.
The gauge has been fluctuating over the last 24hrs, but remains high and is currently approaching maximum now. Is this dangerous?
- Attachments
-
- Turbomax filling loop.s-l1600.jpg (60.59 KiB) Viewed 235 times
-
- Senior Member
- Posts: 17029
- Joined: Fri Jan 20, 2006 5:51 pm
- Location: Essex
- Has thanked: 818 times
- Been thanked: 3514 times
Vaillant Turboxmax boiler gaining pressure
A filling loop invariably has a valve on the incoming water pipe and a valve on the boiler water inlet. You turn on the water inlet and then control the boiler fill with the other to stop contamination of the mains by possible back flow. From what you describe the boiler inlet might be letting in increasing the pressure or it might be a defective gauge giving false readings. There will be a pressure release valve that will automatically discharge if the pressure gets too high. Check if there are any apparent drips on the end of the PRV drain pipe which is normally outside.
DWD
DWD
-
- Newly registered Member
- Posts: 4
- Joined: Wed Oct 30, 2024 9:47 am
- Has thanked: 0
- Been thanked: 0
Vaillant Turboxmax boiler gaining pressure
Sorryu, forgot to mention, I did try the Pressure Release Valve and the gauge quickly dropped down, but then immediately went up again when I released the valve, and continued to creep up. Before that, I also bled a radiator (the only one inn the hous3e I can do with a key).
- Someone-Else
- Senior Member
- Posts: 14624
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 47 times
- Been thanked: 2575 times
Vaillant Turboxmax boiler gaining pressure
I am NOT a plumber or heating engineer.
You started by saying the pressure was Zero, this usually happens if you have a leak or the PRV operates.
You then on purpose opened the filling loop. Since then the pressure keeps rising (slowly)
My guess is the filling loop is and has been letting water past for some time, just that you did not know. I would suggest either remove the filling loop or change it.
You started by saying the pressure was Zero, this usually happens if you have a leak or the PRV operates.
You then on purpose opened the filling loop. Since then the pressure keeps rising (slowly)
My guess is the filling loop is and has been letting water past for some time, just that you did not know. I would suggest either remove the filling loop or change it.
Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
- wine~o
- Senior Member
- Posts: 26279
- Joined: Sat Jan 10, 2009 3:49 pm
- Location: hants/dorset border
- Has thanked: 1414 times
- Been thanked: 4019 times
Vaillant Turboxmax boiler gaining pressure
IF that is your own filling loop AND it has been removed from your boiler then you have a big issue internally on your boiler, get a gas safe registered engineer in to advise. IT IS NOT a Diy-able job.
Verwood Handyman
_____________________________________________________________________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :
http://www.donnasdreamhouse.co.uk
_____________________________________________________________________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :
http://www.donnasdreamhouse.co.uk
-
- Newly registered Member
- Posts: 4
- Joined: Wed Oct 30, 2024 9:47 am
- Has thanked: 0
- Been thanked: 0
Vaillant Turboxmax boiler gaining pressure
Thanks both. To clarify, it's not my own filling loop and it has not been removed.
I tried to take a picture to show the valve I adjusted, but it was too difficult, so the pic was taken from an ebay listing for the part, the one on the boiler looks exactly the same. This forum doesn't seem to let me post links, so I had to download the picture and attach it. I also wanted to post the youtube clip that explained how to fill the boiler, but couldn't get the yoube link to work. If you casn be bothered, the video number to put after the youtube URL is: vspiFvhSjxc
The event that triggered this was the hot water stopped running andf thhere was an F.22 error on thr boiler. Several videos and online sources suggested increasing the pressure to solve this.
I tried to take a picture to show the valve I adjusted, but it was too difficult, so the pic was taken from an ebay listing for the part, the one on the boiler looks exactly the same. This forum doesn't seem to let me post links, so I had to download the picture and attach it. I also wanted to post the youtube clip that explained how to fill the boiler, but couldn't get the yoube link to work. If you casn be bothered, the video number to put after the youtube URL is: vspiFvhSjxc
The event that triggered this was the hot water stopped running andf thhere was an F.22 error on thr boiler. Several videos and online sources suggested increasing the pressure to solve this.
- Someone-Else
- Senior Member
- Posts: 14624
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 47 times
- Been thanked: 2575 times
Vaillant Turboxmax boiler gaining pressure
As You are new, you can't insert links (Answers that question) But a picture and or video of your filling loop would make no difference. The answer is still the same, the pressure goes up when the filling loop is not 100% closed, you need to close it, change it, or remove it.
Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
-
- Senior Member
- Posts: 7203
- Joined: Mon Apr 13, 2009 7:03 pm
- Has thanked: 419 times
- Been thanked: 900 times
Vaillant Turboxmax boiler gaining pressure
The valves are the square brass block.
I would think the screw in the block hasn't been closed properly. They can be very stiff/awkward to use if you are not using the proper Vaillant key.
I would think the screw in the block hasn't been closed properly. They can be very stiff/awkward to use if you are not using the proper Vaillant key.
Dave