Adding downlights to a ceiling
All electrical lighting questions in here please. Including outside lighting and light switch / dimmer questions.
Moderator: Moderators
-
- Newly registered Member
- Posts: 2
- Joined: Sat Dec 30, 2006 9:06 pm
- Has thanked: 0
- Been thanked: 0
Adding downlights to a ceiling
Hi
I would like to add downlights to my ceiling. I have no idea what is involved, but as a guess I would have to create a new ceiling from sheets of plasterboard attached to the existing ceiling and make holes for the downlights. Insert the downlights and and then connect them up before I secure the plasterboard. There are existing lights in the ceiling.
Is it something that requires a professional or could I do it myself? I am reasonably good at DIY although haven't worked with plasterboard.
Any suggestions would be much appreciated.
Thanks
I would like to add downlights to my ceiling. I have no idea what is involved, but as a guess I would have to create a new ceiling from sheets of plasterboard attached to the existing ceiling and make holes for the downlights. Insert the downlights and and then connect them up before I secure the plasterboard. There are existing lights in the ceiling.
Is it something that requires a professional or could I do it myself? I am reasonably good at DIY although haven't worked with plasterboard.
Any suggestions would be much appreciated.
Thanks
adugga
- ultimatehandyman
- Site Admin
- Posts: 24425
- Joined: Sat Jul 16, 2005 7:06 pm
- Location: Darwen, Lancashire
- Has thanked: 1012 times
- Been thanked: 918 times
Post by ultimatehandyman »
Hi, I have moved this to the sparks forum as they will be the ones to answer this.
As long as your existing ceiling is ok then I can't see why you can't just use an holesaw and cut out the required holes for the downlights?
Can you get access to the ceiling from above, by lifting a few floorboards in the room above?
Is the ceiling in good condition?
As long as your existing ceiling is ok then I can't see why you can't just use an holesaw and cut out the required holes for the downlights?
Can you get access to the ceiling from above, by lifting a few floorboards in the room above?
Is the ceiling in good condition?
ultimatehandyman
- Jaeger_S2k
- Pro Handyman
- Posts: 3423
- Joined: Sun Nov 19, 2006 4:31 pm
- Location: North West, England, United Kingdom
- Has thanked: 20 times
- Been thanked: 27 times
Post by Jaeger_S2k »
Just to confuse matters, if there are rooms above and you cut into the ceiling (i.e. make holes) for the down lights you need to install Fire Capped ones or fit Fire Caps to the lights. These provide a 1 hour fire protection.
See here viewtopic.php?t=1101
Just bought some for under stairs fitting https://www.screwfix.com/app/sfd/cat/pr ... 6&id=25727
Or hoods for smaller lights http://www.screwfix.com/app/sfd/cat/pro ... 4&ts=26266
See here viewtopic.php?t=1101
Just bought some for under stairs fitting https://www.screwfix.com/app/sfd/cat/pr ... 6&id=25727
Or hoods for smaller lights http://www.screwfix.com/app/sfd/cat/pro ... 4&ts=26266
Jaeger.
Senior Member doesn't mean I'm OLD!
Senior Member doesn't mean I'm OLD!
Jaeger_S2k
Stoday
- Jaeger_S2k
- Pro Handyman
- Posts: 3423
- Joined: Sun Nov 19, 2006 4:31 pm
- Location: North West, England, United Kingdom
- Has thanked: 20 times
- Been thanked: 27 times
Post by Jaeger_S2k »
Cause them’s the rules .Stoday wrote:Why bother fitting a fire hood to a little hole like that when you have a somewhat bigger hole that the staircase passes through nearby?Jaeger_S2k wrote: Just bought some for under stairs fitting
It's a staircase that comes from the hallway and I've removed the under stairs cupboard and plaster boarded between the strings.
Jaeger.
Senior Member doesn't mean I'm OLD!
Senior Member doesn't mean I'm OLD!
Jaeger_S2k
-
- BANNED
- Posts: 418
- Joined: Fri Oct 27, 2006 5:40 pm
- Has thanked: 0
- Been thanked: 2 times
Post by ban-all-sheds »
Sorry, Allan, but I'm afraid that you are confusing matters where no confusion needs to be introduced - fire hoods etc are NOT required...Jaeger_S2k wrote:Just to confuse matters, if there are rooms above and you cut into the ceiling (i.e. make holes) for the down lights you need to install Fire Capped ones or fit Fire Caps to the lights. These provide a 1 hour fire protection.
No, those are not the rules.Jaeger_S2k wrote: Cause them’s the rules .
In a single dwelling there are no fire compartment boundaries other than above an integral garage. The presence of a habitable room above the ceiling is immaterial.
You should read all the relevant bits of Building Regulation Part B.
I'm sorry - I can't come in to work today, the voices are telling me to stay at home and clean the guns.
[size=9][color=white].[/color] [/size]
ban-all-sheds
- Jaeger_S2k
- Pro Handyman
- Posts: 3423
- Joined: Sun Nov 19, 2006 4:31 pm
- Location: North West, England, United Kingdom
- Has thanked: 20 times
- Been thanked: 27 times
Post by Jaeger_S2k »
Hi B A S,ban-all-sheds wrote:Sorry, Allan, but I'm afraid that you are confusing matters where no confusion needs to be introduced - fire hoods etc are NOT required...Jaeger_S2k wrote:Just to confuse matters, if there are rooms above and you cut into the ceiling (i.e. make holes) for the down lights you need to install Fire Capped ones or fit Fire Caps to the lights. These provide a 1 hour fire protection.
No, those are not the rules.Jaeger_S2k wrote: Cause them’s the rules .
In a single dwelling there are no fire compartment boundaries other than above an integral garage. The presence of a habitable room above the ceiling is immaterial.
You should read all the relevant bits of Building Regulation Part B.
Thanks for that and for the informative stuff on my Part P enquiry, I’ll have a good read.
Far from being an expert and I’ve proved that a couple of times recently , I'm learning all the time and I'm grateful for all the experience you and others are willing to share.
I’ve read Part B AGAIN! And you’re right I’m wrong and I take the correction on board. I don’t mind being wrong as long as I’m wrong in a good way, if you know what I mean?
I do hate the way Part B, or for that matter many parts of Building Regs are open to interpretation depending on who you are when reading it/complying to it, as in are you the occupant of the dwelling in question or are you the person responsible to only fulfil the requirements of the said Building Regs.
Don’t get me wrong, if I was developing this house and not living in it I would probably do as you rightly say, but not before you rightly said it
What are your thoughts on Part E, E2?
As the person occupying the dwelling, I am more concerned about my means of escape than say the Secretary of State or the local Building Control Officer.
In that, yes I do have first floor windows that are of the recommended size to be fit for throwing ones person out of, to land in what ever soil, paving, motor vehicles, bins, passing dogs or for that matter passsing dog’s visiting card. But I would much rather have a less damaging and more civilised route of escape.
The fact that there are a perfectly serviceable set of stairs attached to the first floor which lead conveniently to the front door and have 30 min fire doors from each connecting room their only failing in the event of a fire is that they are constructed in wood, not the best fabric in the event.
I've cut 3 x 85mm holes in the underside of the already flammable stairs and would rather reduce the egress of fire and smoke through those holes as best I can so I've installed 30min to 1 hour fire rated light with an integrated intumescent material.
Accepted that the first floor is not greater than 4.5mtrs above ground (apparently the accepted height below which it is deemed reasonable to throw ones self from a first floor window) I note with a smile they also say "should enable the person escaping to reach a place free from fire."
As I'm not keen on the window option I have opted for the provision of point 2.4 b direct access to a protected stairway.
My point is not that I am right but that I’m reading the Regs. from the perspective of the occupant and perhaps rather than say “Cause them’s the rules” I should have said, if you want to be as safe as you can be and in my case protect the means of escape available to you, or you want to limit the spread of fire through the holes you’ve drilled in your ceiling below your child’s bedroom then install the fire capped lights?
Jaeger.
Senior Member doesn't mean I'm OLD!
Senior Member doesn't mean I'm OLD!
Jaeger_S2k
-
- BANNED
- Posts: 418
- Joined: Fri Oct 27, 2006 5:40 pm
- Has thanked: 0
- Been thanked: 2 times
Post by ban-all-sheds »
1) Fire hoods don't stop smoke, they only react and close up when there is fire-level heat.
2) The presence of downlighters does not adversely affect the 30-minute fire rating of a normal ceiling. So if you say " if you want to limit the spread of fire through the holes you’ve drilled in your ceiling below your child’s bedroom" as a reason for installing firehoods or fire rated downlights, what you are saying is "would you like to install firehoods or fire rated downlights in order to give a few parts of the ceiling a 1- or 2-hour rating despite the fact that the rest of it will collapse after 30 minutes?"
If you're still in an upstairs room 30 minutes after the flames downstairs have started licking at the ceiling, you are never going to be leaving under your own steam.
2) The presence of downlighters does not adversely affect the 30-minute fire rating of a normal ceiling. So if you say " if you want to limit the spread of fire through the holes you’ve drilled in your ceiling below your child’s bedroom" as a reason for installing firehoods or fire rated downlights, what you are saying is "would you like to install firehoods or fire rated downlights in order to give a few parts of the ceiling a 1- or 2-hour rating despite the fact that the rest of it will collapse after 30 minutes?"
If you're still in an upstairs room 30 minutes after the flames downstairs have started licking at the ceiling, you are never going to be leaving under your own steam.
I'm sorry - I can't come in to work today, the voices are telling me to stay at home and clean the guns.
[size=9][color=white].[/color] [/size]
ban-all-sheds
- Jaeger_S2k
- Pro Handyman
- Posts: 3423
- Joined: Sun Nov 19, 2006 4:31 pm
- Location: North West, England, United Kingdom
- Has thanked: 20 times
- Been thanked: 27 times
Post by Jaeger_S2k »
Lights being returned to SF as we speak. I'm going for a lie down! :|
Jaeger.
Senior Member doesn't mean I'm OLD!
Senior Member doesn't mean I'm OLD!
Jaeger_S2k
Jump to
- Ultimate Handyman DIY forum
- ↳ Welcome to the Ultimate Handyman DIY Forum
- WELCOME
- ↳ WELCOME
- ↳ About the forums
- UltimateHandyman Discounts
- ↳ Ultimatehandyman Discounts
- ULTIMATE HANDYMAN COMPETITIONS
- ↳ UHM Forum competitions
- SHOW CASE- A place to show us your work
- ↳ Show Case Gallery
- ↳ Rogues Gallery
- TOOL FORUM
- ↳ Power Tool Reviews
- ↳ Bosch
- ↳ budget power tools
- ↳ Dewalt
- ↳ Festool
- ↳ Hikoki/Hitachi
- ↳ Makita
- ↳ Metabo
- ↳ Milwaukee
- ↳ Ryobi
- ↳ Tool Talk
- ↳ Bargain Tools
- ↳ Hand tool reviews
- ↳ Power Tool Manuals
- ↳ Bosch
- ↳ Dolmar
- ↳ ELEKTRA BECKUM
- ↳ Hitachi
- ↳ Husqvarna
- ↳ Jonsered
- ↳ Makita
- ↳ Stihl
- Other DIY
- ↳ Computers
- ↳ communications and broadband
- ↳ Gardeners World
- ↳ Money Saving
- ↳ Vehicle maintenance & Repair
- ↳ Energy Saving
- DIY Forum/Home improvement
- ↳ General DIY forum
- ↳ Acrylic Forum
- ↳ DIY Disasters
- ↳ Stoves
- ↳ Building Forum
- ↳ Carpentry/Joinery Forum
- ↳ Kitchen Fitting
- ↳ Damp Proofing and Remedial problems
- ↳ Electric Forum UK
- ↳ Lighting
- ↳ Alarm Manuals
- ↳ Painting & Decorating Forum
- ↳ Plastering Forum
- ↳ Plumbing Forum
- ↳ Central Heating & Boilers
- ↳ Boiler Manuals
- ↳ Alpha
- ↳ Ariston
- ↳ ATAG
- ↳ Atmos
- ↳ Baxi
- ↳ Biasi
- ↳ Broag
- ↳ Chaffoteux
- ↳ Ferroli
- ↳ Glow-worm
- ↳ Halstead
- ↳ Ideal
- ↳ Intergas
- ↳ Keston
- ↳ Myson
- ↳ Potterton
- ↳ Protherm
- ↳ Ravenheat
- ↳ Saunier Duval
- ↳ Sime
- ↳ Thorn
- ↳ Vaillant
- ↳ Viessmann
- ↳ Vokera
- ↳ warmflow
- ↳ Worcester Bosch
- ↳ Shower Manuals
- ↳ Tiling Forum
- ↳ Metalworking Forum
- General
- ↳ The Lounge
- ↳ The games corner
- ↳ The Grumpy corner
- ↳ The Sport corner
- ↳ The Cookery corner
- ↳ The Music Corner
- ↳ BUY - SELL - FREE