Earthing enquiry
HarlemSparton
Has thanked: 11 times
Earthing enquiry
Post by HarlemSparton »
Ze came at 97 ohms. Rainy day. Would reach 100's at a hot day... :bs:
This TT would not achieve anything. :roll:
ericmark
Has thanked: 118 times
Been thanked: 785 times
Earthing enquiry
Post by ericmark »
How did we manage all those years ago? My RCD did not even say it was a type AC, but not an ELCB-v at least, I do think it's a problem when your boss tells you to do something you know is wrong, after all you want the job, can't afford a boss to say your a cantankerous so and so, so letting you go.
Your I am sure your reasonably sure it is wrong, so the question is how to tell your boss, "The ELI is too high, only getting X ohms, think this is a TT setup." seems to be easy way, followed by "What should I do about it?" and as a text message not voice, so you can show anyone you did tell him. All health and safety matters should be in writing.
These users thanked the author ericmark for the post:
HarlemSparton (Thu Jun 29, 2023 6:13 pm)
HarlemSparton
Earthing enquiry
Its all resolved.
The installation has a upfront 100ma rcd with a 30ma rcd protecting for faults. Didnt notice that for some reason.
It does meet disconnection times
Neelix
Been thanked: 219 times
Earthing enquiry
Post by Neelix »
aeromech3 wrote: Thu Jun 29, 2023 10:20 am Ramble: My overseas property was TT, the only earth rod being for the shower heater which incorporated an ELCD; when I had an air conditioner fitted, they also put in an earth rod for that; not happy with the situation, I fitted this RCD on the incoming tails to the existing MCB and DP master switch box; would not pass muster in UK though.
On my newer separate extension, I insisted on an RCD type consumer unit; the air con and shower heater still needed separate earth rods.
Upfront RCD's don't comply with the regs and that enclosure isn't metal
HarlemSparton
Earthing enquiry
Neelix wrote: Fri Jun 30, 2023 10:21 am
I dont see why upfront RCD's dont comply with the regs. You can use them with double pole rcbos on a TT.
Neelix
Earthing enquiry
Post by Neelix »
HarlemSparton wrote: Fri Jun 30, 2023 12:30 pm
314.2 iirc
Return to “Electric Forum UK”