Weird instruction.
Moderator: Moderators
- ericmark
- Senior Member
- Posts: 4260
- Joined: Tue May 10, 2011 2:43 am
- Location: Mid Wales
- Has thanked: 116 times
- Been thanked: 782 times
Weird instruction.
As far as I am aware, the 3 meters from the bath or shower has been reduced, not got the current edition of BS 7671 so if 3 meter or more from bath or shower would be permitted. My top bathroom must be on the edge of being able to comply with 3 meter rule, the other 2 are too small.
Be it a FCU or socket, being slightly to the side of the heater would normally not be a problem, and it is the same as the hob isolator, may be no regulation to say don't mount so you have to reach over hob to reach it or above heater to switch it off, but common sense says if some thing goes wrong you need to access the isolator.
Oh and BS 7671 is not law, although can be used in a court of law, and only with rented homes is there any law saying must comply with BS 7671. Although scheme member electricians have a contract with the scheme provider to say they must follow BS 7671.
Be it a FCU or socket, being slightly to the side of the heater would normally not be a problem, and it is the same as the hob isolator, may be no regulation to say don't mount so you have to reach over hob to reach it or above heater to switch it off, but common sense says if some thing goes wrong you need to access the isolator.
Oh and BS 7671 is not law, although can be used in a court of law, and only with rented homes is there any law saying must comply with BS 7671. Although scheme member electricians have a contract with the scheme provider to say they must follow BS 7671.
-
- Senior Member
- Posts: 5375
- Joined: Wed Feb 26, 2014 9:35 pm
- Has thanked: 108 times
- Been thanked: 1038 times
Weird instruction.
My bathroom at only just over 1.5m square is definitely too small to legally fit a socket. Still always thought the rules were weird though, you can put loads of sockets and appliances in a kitchen, and you can have a 240v shaver socket next to a sink, but then loads of rules around fitting things like heaters which always have controls that are safe to use with wet hands.ericmark wrote: ↑Mon Sep 16, 2024 11:35 am As far as I am aware, the 3 meters from the bath or shower has been reduced, not got the current edition of BS 7671 so if 3 meter or more from bath or shower would be permitted. My top bathroom must be on the edge of being able to comply with 3 meter rule, the other 2 are too small.
Be it a FCU or socket, being slightly to the side of the heater would normally not be a problem, and it is the same as the hob isolator, may be no regulation to say don't mount so you have to reach over hob to reach it or above heater to switch it off, but common sense says if some thing goes wrong you need to access the isolator.
Oh and BS 7671 is not law, although can be used in a court of law, and only with rented homes is there any law saying must comply with BS 7671. Although scheme member electricians have a contract with the scheme provider to say they must follow BS 7671.
Anyway I didn't need to fit mine directly below the socket, it's off to one side, just thought it was a very weird instruction.
- Someone-Else
- Senior Member
- Posts: 14576
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 47 times
- Been thanked: 2559 times
Weird instruction.
Sorry about this but..............
Yes you can, but a shaver socket has an isolation transformer in it (That's why they are heavy and cost a lot) so they are "Safe" (You can't draw a lot of current from one) so a shaver socket does not count in your example
Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
- ericmark
- Senior Member
- Posts: 4260
- Joined: Tue May 10, 2011 2:43 am
- Location: Mid Wales
- Has thanked: 116 times
- Been thanked: 782 times
Weird instruction.
Just measured mine and 2 meters from bath so I can't fit a socket. In the main the old 3 meter rules replaced the rules for fitting a shower in a bedroom.
I agree that even 2 meters seems far enough from the bath or shower to not need the regulations not to permit sockets, in the main the idea was to stop some one plugging in a hair drier and using it in the bath, but who knows what went through the minds of the writers when they wrote the regulations.
But all we can do is follow the regulations, yes when I was a member of the IET I could have lobbied them to change it. But as a lowly level 5 member (foundation degree) I don't think my opinion would have had much weight.
I agree that even 2 meters seems far enough from the bath or shower to not need the regulations not to permit sockets, in the main the idea was to stop some one plugging in a hair drier and using it in the bath, but who knows what went through the minds of the writers when they wrote the regulations.
But all we can do is follow the regulations, yes when I was a member of the IET I could have lobbied them to change it. But as a lowly level 5 member (foundation degree) I don't think my opinion would have had much weight.
-
- Approved Electrician
- Posts: 3114
- Joined: Sun Apr 24, 2011 6:01 pm
- Location: South Yorkshire
- Has thanked: 225 times
- Been thanked: 662 times
Weird instruction.
Rorschach wrote: ↑Mon Sep 16, 2024 12:24 pmMy bathroom at only just over 1.5m square is definitely too small to legally fit a socket.ericmark wrote: ↑Mon Sep 16, 2024 11:35 am As far as I am aware, the 3 meters from the bath or shower has been reduced, not got the current edition of BS 7671 so if 3 meter or more from bath or shower would be permitted. My top bathroom must be on the edge of being able to comply with 3 meter rule, the other 2 are too small.
Be it a FCU or socket, being slightly to the side of the heater would normally not be a problem, and it is the same as the hob isolator, may be no regulation to say don't mount so you have to reach over hob to reach it or above heater to switch it off, but common sense says if some thing goes wrong you need to access the isolator.
Oh and BS 7671 is not law, although can be used in a court of law, and only with rented homes is there any law saying must comply with BS 7671. Although scheme member electricians have a contract with the scheme provider to say they must follow BS 7671.
Use an extension lead from the landing socket then
The UK has always had a problem with 13A sockets in bathrooms. In Eastern Europe the bathroom has for many years been considered the place to locate a washing machine.
And as for UK bathroom safety in the past - who remembers those halogen heaters you could poke your fingers onto. I wonder why many people didn't try that twice - or even once.
-
- Senior Member
- Posts: 5375
- Joined: Wed Feb 26, 2014 9:35 pm
- Has thanked: 108 times
- Been thanked: 1038 times
Weird instruction.
Can't have a socket, but nothing to stop you running an extension in from the landing!ericmark wrote: ↑Mon Sep 16, 2024 1:47 pm Just measured mine and 2 meters from bath so I can't fit a socket. In the main the old 3 meter rules replaced the rules for fitting a shower in a bedroom.
I agree that even 2 meters seems far enough from the bath or shower to not need the regulations not to permit sockets, in the main the idea was to stop some one plugging in a hair drier and using it in the bath, but who knows what went through the minds of the writers when they wrote the regulations.
But all we can do is follow the regulations, yes when I was a member of the IET I could have lobbied them to change it. But as a lowly level 5 member (foundation degree) I don't think my opinion would have had much weight.
-
- Senior Member
- Posts: 5375
- Joined: Wed Feb 26, 2014 9:35 pm
- Has thanked: 108 times
- Been thanked: 1038 times
Weird instruction.
Those halogen wall heaters are still for sale in Argos!OnlyMe wrote: ↑Mon Sep 16, 2024 5:44 pmRorschach wrote: ↑Mon Sep 16, 2024 12:24 pmMy bathroom at only just over 1.5m square is definitely too small to legally fit a socket.ericmark wrote: ↑Mon Sep 16, 2024 11:35 am As far as I am aware, the 3 meters from the bath or shower has been reduced, not got the current edition of BS 7671 so if 3 meter or more from bath or shower would be permitted. My top bathroom must be on the edge of being able to comply with 3 meter rule, the other 2 are too small.
Be it a FCU or socket, being slightly to the side of the heater would normally not be a problem, and it is the same as the hob isolator, may be no regulation to say don't mount so you have to reach over hob to reach it or above heater to switch it off, but common sense says if some thing goes wrong you need to access the isolator.
Oh and BS 7671 is not law, although can be used in a court of law, and only with rented homes is there any law saying must comply with BS 7671. Although scheme member electricians have a contract with the scheme provider to say they must follow BS 7671.
Use an extension lead from the landing socket then
The UK has always had a problem with 13A sockets in bathrooms. In Eastern Europe the bathroom has for many years been considered the place to locate a washing machine.
And as for UK bathroom safety in the past - who remembers those halogen heaters you could poke your fingers onto. I wonder why many people didn't try that twice - or even once.
As for your extension idea, you aren't far off reality ;)
-
- Senior Member
- Posts: 16940
- Joined: Fri Jan 20, 2006 5:51 pm
- Location: Essex
- Has thanked: 807 times
- Been thanked: 3498 times
Weird instruction.
I am in Ibiza this week and they do not worry about this issue. We have a hairdryer over the sink in the hotel room that cuts out if you do not press the trigger. I wondered what would happen if I dropped it in water (not that I would use it with water in the sink) The Spanish do not worry it seems.
DWD
DWD
- These users thanked the author dewaltdisney for the post:
- Rorschach (Mon Sep 16, 2024 8:16 pm)
- Rating: 7.14%
-
- Approved Electrician
- Posts: 3114
- Joined: Sun Apr 24, 2011 6:01 pm
- Location: South Yorkshire
- Has thanked: 225 times
- Been thanked: 662 times
Weird instruction.
Correct. The Spanish do worry about British tourists.dewaltdisney wrote: ↑Mon Sep 16, 2024 7:36 pm I am in Ibiza this week and they do not worry about this issue. We have a <a href="http://shop.ebay.co.uk/?&_nkw=hairdryer" class="skimwords-link" target="_blank" data-skimwords-id="815084" data-skimwords-word="hairdryer" data-group-id="0" data-skim-creative="300003" title="Shopping Link Added by SkimWords" occurrence="1" data-skim-node-id="300:IaminIbizathisweekan_1" style="">hairdryer</a><span style="position: absolute;"></span><span style="position: absolute;"></span> over the sink in the hotel room that cuts out if you do not press the trigger. I wondered what would happen if I dropped it in water (not that I would use it with water in the sink) The Spanish do not worry it seems.
DWD
-
- Senior Member
- Posts: 5375
- Joined: Wed Feb 26, 2014 9:35 pm
- Has thanked: 108 times
- Been thanked: 1038 times
Weird instruction.
Same in the US, when I visited there were standard light switches inside the bathroom and there was a double socket on the wall right next to the sink.
-
- Senior Member
- Posts: 1257
- Joined: Fri Jun 09, 2017 11:55 am
- Has thanked: 144 times
- Been thanked: 124 times
Weird instruction.
Re fused spur in the bathroom is not allowed in the regs but a fan heater on bathroom wall is fine:
Q. Which is more dangerous, water splash on a bathroom fan heater or on fused spur?
Q. Which is more dangerous, water splash on a bathroom fan heater or on fused spur?
-
- Senior Member
- Posts: 5375
- Joined: Wed Feb 26, 2014 9:35 pm
- Has thanked: 108 times
- Been thanked: 1038 times