Miswired 2-way switches?

Post by OnlyMe »

Neelix wrote: Sat Jan 06, 2024 11:24 am If you just swap the strappers the two way will not function properly as a 2 way switch
It will work. It will have the effect of turning the lightswitch upside down.
User avatar
wine~o
Senior Member
Posts: 26269
Joined: Sat Jan 10, 2009 3:49 pm
Location: hants/dorset border
Has thanked: 1414 times
Been thanked: 4017 times

Miswired 2-way switches?

Post by wine~o »

OnlyMe, Do you just swap the permanent and switched live or ???
Verwood Handyman

_____________________________________________________________________________

If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :

http://www.donnasdreamhouse.co.uk
Neelix
Senior Member
Posts: 1309
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 117 times
Been thanked: 213 times

Miswired 2-way switches?

Post by Neelix »

OnlyMe wrote: Sun Jan 07, 2024 11:32 am
Neelix wrote: Sat Jan 06, 2024 11:24 am If you just swap the strappers the two way will not function properly as a 2 way switch
It will work. It will have the effect of turning the lightswitch upside down.
It won’t . There is no on or off on 2 way switching
OnlyMe
Approved Electrician
Posts: 3116
Joined: Sun Apr 24, 2011 6:01 pm
Location: South Yorkshire
Has thanked: 225 times
Been thanked: 662 times

Miswired 2-way switches?

Post by OnlyMe »

wine~o wrote: Sun Jan 07, 2024 3:04 pm OnlyMe, Do you just swap the permanent and switched live or ???
That would work. Or you can just swap the strappers over in L1 and L2 (assuming Com is labelled as Com)
Neelix
Senior Member
Posts: 1309
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 117 times
Been thanked: 213 times

Miswired 2-way switches?

Post by Neelix »

OnlyMe wrote: Sun Jan 07, 2024 5:14 pm
wine~o wrote: Sun Jan 07, 2024 3:04 pm OnlyMe, Do you just swap the permanent and switched live or ???
That would work. Or you can just swap the strappers over in L1 and L2 (assuming Com is labelled as Com)
I can assure you it won't.

Have tried this on our 2 way switching for our utility
These users thanked the author Neelix for the post:
cjc (Mon Jan 08, 2024 7:13 pm)
Rating: 7.14%
cjc
Newly registered Member
Posts: 11
Joined: Fri Jan 05, 2024 7:50 am
Has thanked: 4 times
Been thanked: 0

Miswired 2-way switches?

Post by cjc »

So, when you swapped, assuming you started from the LH table in my original post, can you tell us what you got? Evidently it was not the RH table. Did you get a light which was only on when both switches were down? Or a light which was always on?
User avatar
ericmark
Senior Member
Posts: 4261
Joined: Tue May 10, 2011 2:43 am
Location: Mid Wales
Has thanked: 116 times
Been thanked: 783 times

Miswired 2-way switches?

Post by ericmark »

There are three standard ways to wire a two way switch.
1) Power in to com and then connect both n/o (L1) and n/c (L2) to the n/o (L1) and n/c (L2) contacts of other switch and power comes out of the com on the second switch, in practice this means a connector block inside the switch so non preferred method.
2) Power to L1 and power from L2 and connect three wires to L1 on one to L1 on other switch and L2 to L2 and Com to Com, this method is the preferred one as no connector block required.
3) Power in to power in terminal power out from power out terminal on master switch and connect power in to second (slave) switch and also link the S or 1 terminals between the switches, the switches are normally sold as pairs, and only twin and earth required between the two switches.

The other method is to use wireless switching, using either batteries or the power used to switch the switch (Kinetic) I used the former when temporary using the dinning room as a bedroom, the button switch simply stuck to the steel bed, once my wife returned upstairs it was used as a door bell push instead.

Smart switches have a power problem, either energy generated by moving the switch, use of a neutral, or batteries are required, so to get a switch working as two way, can be a problem, we have seen many attempts to get two way to work with less wires, the use of the S or 1 sensing wire I know was used, the only one make I have come across is now discontinued, the other make to use the S or 1 still wants a switched live wire connected. And even the main switch when used without a neutral needs at least a 5 watt load, and has been know to cause a shimmer when switched on, and not switch off fully, and still have a glow, so either you need a neutral at the switch or batteries.

I have used a smart relay for my stairs and landing, as the switch down stairs was the wrong end of the hall, and I now use voice commands. Switches still work, but don't use them.
OnlyMe
Approved Electrician
Posts: 3116
Joined: Sun Apr 24, 2011 6:01 pm
Location: South Yorkshire
Has thanked: 225 times
Been thanked: 662 times

Miswired 2-way switches?

Post by OnlyMe »

simplestrapper1.png
simplestrapper1.png (27.76 KiB) Viewed 12642 times
LHLS ON RHLS ON = Light OFF
LHLS OFF RHLS ON = Light ON
LHSW ON RHLS OFF = Light ON
LHLS OFF RHLS ON = Light OFF
simplestrapper2.png
simplestrapper2.png (27.77 KiB) Viewed 12642 times
LHLS ON RHLS ON = Light ON
LHLS OFF RHLS ON = Light OFF
LHSW ON RHLS OFF = Light OFF
LHLS OFF RHLS ON = Light ON
OnlyMe
Approved Electrician
Posts: 3116
Joined: Sun Apr 24, 2011 6:01 pm
Location: South Yorkshire
Has thanked: 225 times
Been thanked: 662 times

Miswired 2-way switches?

Post by OnlyMe »

An error on the state of the switches
Strapper 1 is
LHLS ON RHLS ON = Light OFF
LHLS OFF RHLS ON = Light ON
LHSW ON RHLS OFF = Light ON
LHLS OFF RHLS OFF = Light OFF

and strapper 2 is

LHLS ON RHLS ON = Light ON
LHLS OFF RHLS ON = Light OFF
LHSW ON RHLS OFF = Light OFF
LHLS ON RHLS ON = Light ON
OnlyMe
Approved Electrician
Posts: 3116
Joined: Sun Apr 24, 2011 6:01 pm
Location: South Yorkshire
Has thanked: 225 times
Been thanked: 662 times

Miswired 2-way switches?

Post by OnlyMe »

OnlyMe wrote: Wed Jan 10, 2024 7:35 pm An error on the state of the switches
Strapper 1 is
LHLS ON RHLS ON = Light OFF
LHLS OFF RHLS ON = Light ON
LHSW ON RHLS OFF = Light ON
LHLS OFF RHLS OFF = Light OFF

and strapper 2 is

LHLS ON RHLS ON = Light ON
LHLS OFF RHLS ON = Light OFF
LHSW ON RHLS OFF = Light OFF
LHLS OFF RHLS OFF = Light ON
These users thanked the author OnlyMe for the post:
cjc (Wed Jan 10, 2024 10:07 pm)
Rating: 7.14%