Hi all,
I currently have a dedicated 20a mcb on my consumer unit in the house that goes to a switch on the inside of my house which then supplies what looks like SWA 2.5mm t & e and that goes to my garage underground and then terminates in the garage at a fused switch. I've checked the fused switch as this is fused only for a light in the garage and there is also another 2.5mm t & e cable which is connected on the live and neutral side which goes to a double socket. My question is can a small garage consumer unit be installed instead of having the metal fused switch and if so which one would be suitable seeing as I already have a 20a mcb with RCD protection from the domestic c/u. I was thinking of just a mains switch with a 6a mcb for lighting in garage and a 16a mcb for the socket. I would like to install another socket from the existing one if possible.
I currently have a dedicated 20a mcb on my consumer unit in the house that goes to a switch on the inside of my house which then supplies what looks like SWA 2.5mm t & e and that goes to my garage underground and then terminates in the garage at a fused switch. I've checked the fused switch as this is fused only for a light in the garage and there is also another 2.5mm t & e cable which is connected on the live and neutral side which goes to a double socket. My question is can a small garage consumer unit be installed instead of having the metal fused switch and if so which one would be suitable seeing as I already have a 20a mcb with RCD protection from the domestic c/u. I was thinking of just a mains switch with a 6a mcb for lighting in garage and a 16a mcb for the socket. I would like to install another socket from the existing one if possible.
- Someone-Else
- Senior Member
- Posts: 14628
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 47 times
- Been thanked: 2575 times
Garage c/u question
Yes you can do as you suggest, the consumers unit would be your choice, but you want one without an RCD
- These users thanked the author Someone-Else for the post:
- Sparky70 (Sat Jan 08, 2022 7:34 pm)
- Rating: 7.14%
Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
-
- Senior Member
- Posts: 456
- Joined: Thu Jan 03, 2013 6:15 pm
- Has thanked: 157 times
- Been thanked: 1 time
Garage c/u question
Because I already have a 2.5mm and two 1.5mm t & e in the metal fcu and I need another light switch at the other end of the garage so thought it would be best to upgrade due to the amount of cabling.
-
- Senior Member
- Posts: 456
- Joined: Thu Jan 03, 2013 6:15 pm
- Has thanked: 157 times
- Been thanked: 1 time
-
- Senior Member
- Posts: 1311
- Joined: Mon May 03, 2021 1:36 pm
- Has thanked: 117 times
- Been thanked: 214 times
-
- Senior Member
- Posts: 456
- Joined: Thu Jan 03, 2013 6:15 pm
- Has thanked: 157 times
- Been thanked: 1 time
Garage c/u question
I have a 2.5mm swa cable going into the garage and it terminates into a metal switch fcu, the light in the garage is connected to the the fused switch and the sockets are connected directly to the incoming side along with a 1.0mm cable on the incoming side to a fused switch 1amp for 2 led floodlights. so there's currently 3 x cables in this fused switch. What i'm trying to achieve is to have another light switch ( 2 way ) at the other end of the garage and another (2 way ) near the existing fused switch, I'll be installing to new led light battens and I want to have control at either end of the garage, I will also add another socket from the existing socket, do you have any recomendations to achieve this ? regards.
-
- Senior Member
- Posts: 1311
- Joined: Mon May 03, 2021 1:36 pm
- Has thanked: 117 times
- Been thanked: 214 times
Garage c/u question
You’ve moved the goal posts a lot now …Sparky70 wrote: ↑Sun Jan 09, 2022 4:58 pm
I have a 2.5mm swa cable going into the garage and it terminates into a metal switch fcu, the light in the garage is connected to the the fused switch and the sockets are connected directly to the incoming side along with a 1.0mm cable on the incoming side to a fused switch 1amp for 2 led floodlights. so there's currently 3 x cables in this fused switch. What i'm trying to achieve is to have another light switch ( 2 way ) at the other end of the garage and another (2 way ) near the existing fused switch, I'll be installing to new led light battens and I want to have control at either end of the garage, I will also add another socket from the existing socket, do you have any recomendations to achieve this ? regards.
-
- Senior Member
- Posts: 456
- Joined: Thu Jan 03, 2013 6:15 pm
- Has thanked: 157 times
- Been thanked: 1 time
Garage c/u question
ThanksNeelix wrote: ↑Sun Jan 09, 2022 8:07 pmYou’ve moved the goal posts a lot now …Sparky70 wrote: ↑Sun Jan 09, 2022 4:58 pm
I have a 2.5mm swa cable going into the garage and it terminates into a metal switch fcu, the light in the garage is connected to the the fused switch and the sockets are connected directly to the incoming side along with a 1.0mm cable on the incoming side to a fused switch 1amp for 2 led floodlights. so there's currently 3 x cables in this fused switch. What i'm trying to achieve is to have another light switch ( 2 way ) at the other end of the garage and another (2 way ) near the existing fused switch, I'll be installing to new led light battens and I want to have control at either end of the garage, I will also add another socket from the existing socket, do you have any recomendations to achieve this ? regards.
- ericmark
- Senior Member
- Posts: 4265
- Joined: Tue May 10, 2011 2:43 am
- Location: Mid Wales
- Has thanked: 117 times
- Been thanked: 783 times
Garage c/u question
I would change the FCU to a double back box and LAP grid fuse and switch from Screwfix so I can fit a two way switch and also 2 fuses if I want with a little more room to work in.
Similar to as done here to fuse and extend a spur.
Similar to as done here to fuse and extend a spur.
-