I have a Worcester Bosch Greenstar 18Ri regular boiler within my garage
which has a separate, Honeywell T4360 Frost Thermostat on the wall.
Also installed to the boiler Return pipe is a Honeywell Low Limit PipeStat_L641B1004.
Stats are set as below:
Frost Stat is set at: 5°C
Low Limit Pipe Stat is set at: 15°C
I have also looked at my boiler information and its states;
Which ties in with my current settings above.We recommend that the Frost
Thermostat is installed at the
coldest location. Frost
Thermostat to be set on at 5°C
and the Pipe Thermostat to be off
at 15°C.
Now the weather has turned cold, the frost protection has been activating, as the
temperature in the garage is below 5°C, and the boiler and Central Heating pump have
been coming on. Then when the temperature on the Return pipe reaches 15°C,
it turns the boiler back off. Which I have observed while in the garage and seems
to be happening quite frequently. Which I guess is ramping up my Gas usage
(Not sure how much this will be costing having this happen so often, especially with
the way current energy prices are).
So, onto my actual question: While the Frost protection is activating
should my radiators be heating up? As they seem to be constantly warm/hot,
which is most of the day and night while the temperature is low.
NOTE.
Even if I turn my 'house thermostat' to say 12°C (so I know there is it is
not calling to fire the boiler up), the radiators still heat up from when
the frost stat protection kicks in and fires up the boiler. hence my query above.
With the above in mind, is the following a correct assumption?
When the frost stat kicks in and fires up the boiler, this then heat the water and will
then send that heated water around all the whole central heating system / radiators,
to finally come back to the boiler via the Return Pipe, which the temperature of is then
sensed by the Low Limit Pipe Stat, which then when it reaches 15°C, will then turn the boiler off.
Which I guess would be why the radiators are heating up?
Also, to prevent the frost protection constantly kicking in, could I lower
the temperature at which the Low limit pipe stat turns the boiler off,
from the current 15°C, to a lower value to stop the radiators heating up as much
or would this be detrimental to the whole frost protection system.
Thanks in advance.