Downstairs hot water problem.
Moderator: Moderators
-
- Newly registered Member
- Posts: 10
- Joined: Fri Oct 12, 2018 8:29 pm
- Has thanked: 3 times
- Been thanked: 0
Downstairs hot water problem.
Got a bit of a problem, we are getting no hot water to tap in kitchen, but upstairs is ok, and radiators downstairs and upstairs are fine. Could someone please help me? Thanks in advance.
-
- Senior Member
- Posts: 17265
- Joined: Fri Jan 20, 2006 5:51 pm
- Location: Essex
- Has thanked: 823 times
- Been thanked: 3560 times
Downstairs hot water problem.
We need to know what the hot water source is. Do you have a combi boiler or is the water heated by a different method? A bit more info would help
DWD
DWD
-
- Newly registered Member
- Posts: 10
- Joined: Fri Oct 12, 2018 8:29 pm
- Has thanked: 3 times
- Been thanked: 0
Downstairs hot water problem.
Sorry, it a coventional boiler system, 2 tanks in loft and a copper boiler and boiler in kitchen... Just to clarify, we can get cold water out of the hot water tap, but its not getting hot.dewaltdisney wrote: ↑Mon Mar 13, 2023 10:31 am We need to know what the hot water source is. Do you have a combi boiler or is the water heated by a different method? A bit more info would help
DWD
-
- Senior Member
- Posts: 17265
- Joined: Fri Jan 20, 2006 5:51 pm
- Location: Essex
- Has thanked: 823 times
- Been thanked: 3560 times
Downstairs hot water problem.
Well, this is out of my experience loop. The two tanks in the loft I assume are the cold water tank and the header tank for the boiler. I think I would firstly check that the ballcocks on the two tanks are working properly as this could cause a pressure imbalance and impaired flows. Not sure what the copper boiler is do you mean a hot water tank?
DWD
DWD
-
- Newly registered Member
- Posts: 10
- Joined: Fri Oct 12, 2018 8:29 pm
- Has thanked: 3 times
- Been thanked: 0
Downstairs hot water problem.
Sorry, yes I mean the hot water tank,and yes the 2 tanks in the loft are exactly that.dewaltdisney wrote: ↑Mon Mar 13, 2023 11:37 am Well, this is out of my experience loop. The two tanks in the loft I assume are the cold water tank and the header tank for the boiler. I think I would firstly check that the ballcocks on the two tanks are working properly as this could cause a pressure imbalance and impaired flows. Not sure what the copper boiler is do you mean a hot water tank?
DWD
-
- Newly registered Member
- Posts: 10
- Joined: Fri Oct 12, 2018 8:29 pm
- Has thanked: 3 times
- Been thanked: 0
Downstairs hot water problem.
Actually, I have been given the wrong info off the mrs lol..... There is actually no hot water upstairs either!!
Checked pipes on hot water tank... (pic included) I have marked the pipes up, the ones that are cold and the other pipes are really hot
Checked pipes on hot water tank... (pic included) I have marked the pipes up, the ones that are cold and the other pipes are really hot
- Attachments
-
- water pipes.jpg (139.9 KiB) Viewed 1026 times
-
- Senior Member
- Posts: 17265
- Joined: Fri Jan 20, 2006 5:51 pm
- Location: Essex
- Has thanked: 823 times
- Been thanked: 3560 times
Downstairs hot water problem.
I suspect the motorised valve may be stuck shut (the silver box with QC 02 on). I am not sure but I think that the hot water for the rads is diverted through the hot water coil in the tank by the motorised valve activated by the temperature in the tank. A fairly simple job to replace but I would hang on until other more experienced members chip in to help.
DWD
DWD
-
- Newly registered Member
- Posts: 10
- Joined: Fri Oct 12, 2018 8:29 pm
- Has thanked: 3 times
- Been thanked: 0
Downstairs hot water problem.
Thank you very much for you help, it`s really appreciated. What I have just done is tap the pipe what is cold, and that pipe seemed to get hot pretty quickly, so I am hoping it was a blockage, I will give it a hour to see if I get any hot water.dewaltdisney wrote: ↑Mon Mar 13, 2023 12:41 pm I suspect the motorised valve may be stuck shut (the silver box with QC 02 on). I am not sure but I think that the hot water for the rads is diverted through the hot water coil in the tank by the motorised valve activated by the temperature in the tank. A fairly simple job to replace but I would hang on until other more experienced members chip in to help.
DWD
- Someone-Else
- Senior Member
- Posts: 14709
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 47 times
- Been thanked: 2590 times
Downstairs hot water problem.
I am NOT a heating engineer or plumber. I would suggest that we wait till you get home. Then you can tell us what is really happening. Does any water come out of either of the hot taps?
Cold water is heated in the copper cylinder via a coil inside said cylinder, the water in the coil is heated by your boiler. (It can also be heated by an immersion heater if you have one) The radiators are heated by water that runs through the boiler, the rads and tap water never meet. (If they do, you have a problem but that is for another time.)
When you turn on a hot tap, water (heated) comes out from the top of the copper cylinder (Through the pipes to the now open tap) you have to let the tap "run" to get hot water as you have to let the standing cold water out of the pipes from the cylinder to the tap. Water can not come out of the cylinder unless it is forced out, that is where one of the tanks in the loft come in. When you turn on a hot tap, as said water comes from the top of the cylinder, this water is forced out by cold water coming in (close to) the bottom of the cylinder from one of the loft tanks, if the loft tanks ball valve is stuck (Or the tank is empty) there is no water going into the tank to force the hot water out, so I would also have a look in the loft tanks, to see are they both full of water.
Cold water is heated in the copper cylinder via a coil inside said cylinder, the water in the coil is heated by your boiler. (It can also be heated by an immersion heater if you have one) The radiators are heated by water that runs through the boiler, the rads and tap water never meet. (If they do, you have a problem but that is for another time.)
When you turn on a hot tap, water (heated) comes out from the top of the copper cylinder (Through the pipes to the now open tap) you have to let the tap "run" to get hot water as you have to let the standing cold water out of the pipes from the cylinder to the tap. Water can not come out of the cylinder unless it is forced out, that is where one of the tanks in the loft come in. When you turn on a hot tap, as said water comes from the top of the cylinder, this water is forced out by cold water coming in (close to) the bottom of the cylinder from one of the loft tanks, if the loft tanks ball valve is stuck (Or the tank is empty) there is no water going into the tank to force the hot water out, so I would also have a look in the loft tanks, to see are they both full of water.
- These users thanked the author Someone-Else for the post:
- dawson456 (Mon Mar 13, 2023 3:08 pm)
- Rating: 7.14%
Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
-
- Newly registered Member
- Posts: 10
- Joined: Fri Oct 12, 2018 8:29 pm
- Has thanked: 3 times
- Been thanked: 0
Downstairs hot water problem.
I would like to thank everyone who as commented on this thread..... It must have been a blockage, because when I tapped the pipe, that piped got hot immediately, and I now have hot water back. Thanks again guys.
-
- Senior Member
- Posts: 17265
- Joined: Fri Jan 20, 2006 5:51 pm
- Location: Essex
- Has thanked: 823 times
- Been thanked: 3560 times
Downstairs hot water problem.
You may have released the motorised valve by tapping, keep an eye on it
DWD
DWD
- These users thanked the author dewaltdisney for the post:
- dawson456 (Mon Mar 13, 2023 3:08 pm)
- Rating: 7.14%
- wine~o
- Senior Member
- Posts: 26293
- Joined: Sat Jan 10, 2009 3:49 pm
- Location: hants/dorset border
- Has thanked: 1415 times
- Been thanked: 4024 times
Downstairs hot water problem.
DWD is spot on, could be a blockage, could be 3 port valve. Please keep us updated if you have any further issues.
- Rating: 7.14%
Verwood Handyman
_____________________________________________________________________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :
http://www.donnasdreamhouse.co.uk
_____________________________________________________________________________
If you feel you have benefited from the Free advice given on the Forum, Please consider making a donation to UHM's Nominated charity, read all about it and donate here :
http://www.donnasdreamhouse.co.uk
- Razor
- Senior Member
- Posts: 8760
- Joined: Wed Nov 14, 2007 10:21 pm
- Location: Northampton
- Has thanked: 483 times
- Been thanked: 1251 times
Downstairs hot water problem.
Much more likely it was airlocked and the tap dislodged it if the pump was running. The vertical pipe in your picture that goes out of sight probably has an air bleed at the top of it.
The isolation valve shouldn't be there in the flow to the cylinder either. It will have a small orifice that could also block
The isolation valve shouldn't be there in the flow to the cylinder either. It will have a small orifice that could also block
I think I'll take two chickens...
-
- Newly registered Member
- Posts: 10
- Joined: Fri Oct 12, 2018 8:29 pm
- Has thanked: 3 times
- Been thanked: 0
Downstairs hot water problem.
Yes I actually did bleed that before I tapped it.Razor wrote: ↑Mon Mar 13, 2023 7:04 pm Much more likely it was airlocked and the tap dislodged it if the pump was running. The vertical pipe in your picture that goes out of sight probably has an air bleed at the top of it.
The isolation valve shouldn't be there in the flow to the cylinder either. It will have a small orifice that could also block