Bathroom latch
Post by AidanOrton »
Hi
Newbie here, so please be gentle.
I'm in the middle of a bathroom refit and I dislike having pull cords, but the problem with light switches outside the room is someone can switch the light off when you're in the shower with the door locked.
I have an idea that if I have a normal external light switch and a micro switch on the door I could latch the light on until the door is open.
In an ideal world, with the door open the external switch would behave as normal and with the door closed its state would be latched until the door is open.
A latching relay feels the way to go, but if anyone could offer advice or knowledge of any regulations preventing this, it'd be appreciated.
Thanks,
Aidan
Newbie here, so please be gentle.
I'm in the middle of a bathroom refit and I dislike having pull cords, but the problem with light switches outside the room is someone can switch the light off when you're in the shower with the door locked.
I have an idea that if I have a normal external light switch and a micro switch on the door I could latch the light on until the door is open.
In an ideal world, with the door open the external switch would behave as normal and with the door closed its state would be latched until the door is open.
A latching relay feels the way to go, but if anyone could offer advice or knowledge of any regulations preventing this, it'd be appreciated.
Thanks,
Aidan
AidanOrton
-
- Senior Member
- Posts: 17556
- Joined: Fri Jan 20, 2006 5:51 pm
- Location: Essex
- Has thanked: 831 times
- Been thanked: 3628 times
dewaltdisney
- Someone-Else
- Senior Member
- Posts: 14827
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 48 times
- Been thanked: 2604 times
Bathroom latch
Post by Someone-Else »
Seems an odd thing to do, but if you want to, that would be up to you, providing everything is suitably protected. You could of course have a normal switch, provided it is more than 60cm from the edge of the bath, and the circuit is RCD protected.
Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section

Someone-Else
-
- Approved Electrician
- Posts: 3132
- Joined: Sun Apr 24, 2011 6:01 pm
- Location: South Yorkshire
- Has thanked: 225 times
- Been thanked: 664 times
Bathroom latch
So? Either break their fingers or put the lightswitch on the inside.AidanOrton wrote: ↑Tue Apr 02, 2024 6:51 pm Hi
Newbie here, so please be gentle.
I'm in the middle of a bathroom refit and I dislike having pull cords, but the problem with light switches outside the room is someone can switch the light off when you're in the shower with the door locked.
OnlyMe
-
- Newly registered Member
- Posts: 4
- Joined: Tue Apr 02, 2024 6:41 pm
- Has thanked: 0
- Been thanked: 0
Bathroom latch
Post by AidanOrton »
Hmm, shame not to have a solution to the idea raised, but some interesting feedback.
Despite being a decent sized bathroom, there's not zone 3 space around the door for a normal light switch and I don't fancy flapping my arms around from the bath\shower to get the lights back on, but passive \ low voltage switches in zone 2 seem to be an option, so I'll investigate those.
Thanks.
Despite being a decent sized bathroom, there's not zone 3 space around the door for a normal light switch and I don't fancy flapping my arms around from the bath\shower to get the lights back on, but passive \ low voltage switches in zone 2 seem to be an option, so I'll investigate those.
Thanks.
AidanOrton
-
- Senior Member
- Posts: 17556
- Joined: Fri Jan 20, 2006 5:51 pm
- Location: Essex
- Has thanked: 831 times
- Been thanked: 3628 times
Bathroom latch
Post by dewaltdisney »
Well for a fiver it is worth a go, my porch light is very sensitive to any movement and in a bathroom, there is detectable movement, unless you have a shower curtain. You could maybe go a step further and look at a smart LED bulb that you can control with your phone or Alexa. Have a look at this one from Argos https://www.argos.co.uk/product/1931738 ... R=plp:9:36
DWD
DWD
dewaltdisney
- Someone-Else
- Senior Member
- Posts: 14827
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 48 times
- Been thanked: 2604 times
Bathroom latch
Post by Someone-Else »
There is no zone 3, that is why I said as I did. Zone 3 went with the 17th editionAidanOrton wrote: ↑Wed Apr 03, 2024 7:21 amthere's not zone 3 space around the door for a normal light switch
Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section

Someone-Else
-
- Newly registered Member
- Posts: 4
- Joined: Tue Apr 02, 2024 6:41 pm
- Has thanked: 0
- Been thanked: 0
Bathroom latch
Post by AidanOrton »
Sigh, pedant award goes to.. Anything outside zone 2, not in a zone, safety zone, non-wet area, call it what you will.Someone-Else wrote: ↑Wed Apr 03, 2024 9:07 amThere is no zone 3, that is why I said as I did. Zone 3 went with the 17th editionAidanOrton wrote: ↑Wed Apr 03, 2024 7:21 amthere's not zone 3 space around the door for a normal light switch
AidanOrton
-
- Approved Electrician
- Posts: 3132
- Joined: Sun Apr 24, 2011 6:01 pm
- Location: South Yorkshire
- Has thanked: 225 times
- Been thanked: 664 times
Bathroom latch
So you mean it's a tiny bathroom then?AidanOrton wrote: ↑Wed Apr 03, 2024 6:15 pm Sigh, pedant award goes to.. Anything outside zone 2, not in a zone, safety zone, non-wet area, call it what you will.
OnlyMe
-
- Newly registered Member
- Posts: 4
- Joined: Tue Apr 02, 2024 6:41 pm
- Has thanked: 0
- Been thanked: 0
Bathroom latch
Post by AidanOrton »
2.25m x 3m, tiny?OnlyMe wrote: ↑Wed Apr 03, 2024 6:43 pmSo you mean it's a tiny bathroom then?AidanOrton wrote: ↑Wed Apr 03, 2024 6:15 pm Sigh, pedant award goes to.. Anything outside zone 2, not in a zone, safety zone, non-wet area, call it what you will.
AidanOrton
Jump to
- Ultimate Handyman DIY forum
- ↳ Welcome to the Ultimate Handyman DIY Forum
- WELCOME
- ↳ WELCOME
- ↳ About the forums
- UltimateHandyman Discounts
- ↳ Ultimatehandyman Discounts
- ULTIMATE HANDYMAN COMPETITIONS
- ↳ UHM Forum competitions
- SHOW CASE- A place to show us your work
- ↳ Show Case Gallery
- ↳ Rogues Gallery
- TOOL FORUM
- ↳ Power Tool Reviews
- ↳ Bosch
- ↳ budget power tools
- ↳ Dewalt
- ↳ Festool
- ↳ Hikoki/Hitachi
- ↳ Makita
- ↳ Metabo
- ↳ Milwaukee
- ↳ Ryobi
- ↳ Tool Talk
- ↳ Bargain Tools
- ↳ Hand tool reviews
- ↳ Power Tool Manuals
- ↳ Bosch
- ↳ Dolmar
- ↳ ELEKTRA BECKUM
- ↳ Hitachi
- ↳ Husqvarna
- ↳ Jonsered
- ↳ Makita
- ↳ Stihl
- Other DIY
- ↳ Computers
- ↳ communications and broadband
- ↳ Gardeners World
- ↳ Money Saving
- ↳ Vehicle maintenance & Repair
- ↳ Energy Saving
- DIY Forum/Home improvement
- ↳ General DIY forum
- ↳ Acrylic Forum
- ↳ DIY Disasters
- ↳ Stoves
- ↳ Building Forum
- ↳ Carpentry/Joinery Forum
- ↳ Kitchen Fitting
- ↳ Damp Proofing and Remedial problems
- ↳ Electric Forum UK
- ↳ Lighting
- ↳ Alarm Manuals
- ↳ Painting & Decorating Forum
- ↳ Plastering Forum
- ↳ Plumbing Forum
- ↳ Central Heating & Boilers
- ↳ Boiler Manuals
- ↳ Alpha
- ↳ Ariston
- ↳ ATAG
- ↳ Atmos
- ↳ Baxi
- ↳ Biasi
- ↳ Broag
- ↳ Chaffoteux
- ↳ Ferroli
- ↳ Glow-worm
- ↳ Halstead
- ↳ Ideal
- ↳ Intergas
- ↳ Keston
- ↳ Myson
- ↳ Potterton
- ↳ Protherm
- ↳ Ravenheat
- ↳ Saunier Duval
- ↳ Sime
- ↳ Thorn
- ↳ Vaillant
- ↳ Viessmann
- ↳ Vokera
- ↳ warmflow
- ↳ Worcester Bosch
- ↳ Shower Manuals
- ↳ Tiling Forum
- ↳ Metalworking Forum
- General
- ↳ The Lounge
- ↳ The games corner
- ↳ The Grumpy corner
- ↳ The Sport corner
- ↳ The Cookery corner
- ↳ The Music Corner
- ↳ BUY - SELL - FREE