Omi and Bi directional RCD/RCBO why does it matter etc.
Posted: Mon May 13, 2024 8:56 am
I know an amendment is about to be issued with BS 7671 on the use of omi directional RCD's where one can have power both sides.
however if the RCD does not cause the supply to fail, what is the point? I can see if fitted the wrong way around then after it trips it can still energise the tripping mechanism so cause over heating under fault conditions, but I looked at my own solar and battery install and the solar inverter is designed not to island, so if the supply is removed it shuts down, so even if the inverter did have a RCD between the inverter and grid, it would never trip and have power both sides.
Yes power can transfer in both directions when all is running correctly, but how would the direct of power flow affect a RCD? Current always flows in both directions as it is AC.
however if the RCD does not cause the supply to fail, what is the point? I can see if fitted the wrong way around then after it trips it can still energise the tripping mechanism so cause over heating under fault conditions, but I looked at my own solar and battery install and the solar inverter is designed not to island, so if the supply is removed it shuts down, so even if the inverter did have a RCD between the inverter and grid, it would never trip and have power both sides.
Yes power can transfer in both directions when all is running correctly, but how would the direct of power flow affect a RCD? Current always flows in both directions as it is AC.