I have a 2-gang socket that is close to the corner of the room. I need an extra socket, so wondered if a 2 to 3-gang converter might work. Trouble is, I assume the converter socket will be symmetrical, in chich case, it will not fit. Do such things and Left-handed or Right-handed converters exist?
Attachments
RouterSockets.jpg
RouterSockets.jpg (76.92 KiB) Viewed 1005 times
User avatar
Someone-Else
Senior Member
Posts: 14827
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 48 times
Been thanked: 2604 times

3-gang converter socket

Post by Someone-Else »

What does google show?
All the ones I have seen have the connections in the middle, so would not fit where you want.
Why not put another twin socket above or below the existing one?
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
Rorschach
Senior Member
Posts: 5431
Joined: Wed Feb 26, 2014 9:35 pm
Has thanked: 120 times
Been thanked: 1043 times

3-gang converter socket

Post by Rorschach »

I have seen some that can be placed centrally or off to the left or the right.

The only problem with 3 gang sockets is they are usually fused to 13amp which is annoying given a standard 2 gang will be 26amp.
Neelix
Senior Member
Posts: 1366
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 118 times
Been thanked: 219 times

3-gang converter socket

Post by Neelix »

Can’t you use a 4 way adapter fixed to the wall ?
User avatar
big-all
Pro Carpenter
Posts: 23655
Joined: Sat Dec 16, 2006 10:11 pm
Location: redhill surrey an auld reekie laddie
Has thanked: 740 times
Been thanked: 2355 times

3-gang converter socket

Post by big-all »

i use these quite a lot plug in sockets switched and unswitched random link
https://www.ebay.co.uk/sch/i.html?_nkw= ... &_osacat=0

your router could still be plugged in where it is as no hard cable out the bottom
we are all ------------------still learning
OnlineOnline
User avatar
Someone-Else
Senior Member
Posts: 14827
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 48 times
Been thanked: 2604 times

3-gang converter socket

Post by Someone-Else »

Rorschach wrote: Fri Feb 28, 2025 4:07 pmThe only problem with 3 gang sockets is they are usually fused to 13amp which is annoying given a standard 2 gang will be 26amp
The majority of twin sockets are only rated for 13A
s3.jpg
s3.jpg (65.42 KiB) Viewed 990 times
s2.jpg
s2.jpg (57.96 KiB) Viewed 990 times
s1.jpg
s1.jpg (64.89 KiB) Viewed 990 times

They are only tested to 20A
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
User avatar
big-all
Pro Carpenter
Posts: 23655
Joined: Sat Dec 16, 2006 10:11 pm
Location: redhill surrey an auld reekie laddie
Has thanked: 740 times
Been thanked: 2355 times

3-gang converter socket

Post by big-all »

asda do doubles with usb outputs £9
These users thanked the author big-all for the post:
headey (Fri Feb 28, 2025 11:53 pm)
Rating: 7.14%
we are all ------------------still learning
OnlineOnline
Rorschach
Senior Member
Posts: 5431
Joined: Wed Feb 26, 2014 9:35 pm
Has thanked: 120 times
Been thanked: 1043 times

3-gang converter socket

Post by Rorschach »

Someone-Else wrote: Fri Feb 28, 2025 5:06 pm
Rorschach wrote: Fri Feb 28, 2025 4:07 pmThe only problem with 3 gang sockets is they are usually fused to 13amp which is annoying given a standard 2 gang will be 26amp
The majority of twin sockets are only rated for 13A



They are only tested to 20A
Plenty of people plug a kettle and toaster into a double socket and run it with no issues. There is no fuse so they are expecting you to pull up to 26amps. A 3 gang socket would not be able to handle kettle and toaster without blowing the fuse.
User avatar
Someone-Else
Senior Member
Posts: 14827
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 48 times
Been thanked: 2604 times

3-gang converter socket

Post by Someone-Else »

Rorschach wrote: Fri Feb 28, 2025 6:06 pmThere is no fuse so they are expecting you to pull up to 26amps.
If what you say is true, (and it isn't) why are they all clearly labelled as 13A?
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
headey
Senior Member
Posts: 307
Joined: Thu Jan 22, 2009 9:53 am
Has thanked: 71 times
Been thanked: 2 times

3-gang converter socket

Post by headey »

Thanks for all the advice. The hanging adaptor suggested by Big-All would be too big, but a 2 or 3-way might fit. As the new item is a Hive box, which uses a USB charger, the socket with a USB output might be an ideal option. Thanks for the tip.
User avatar
big-all
Pro Carpenter
Posts: 23655
Joined: Sat Dec 16, 2006 10:11 pm
Location: redhill surrey an auld reekie laddie
Has thanked: 740 times
Been thanked: 2355 times

3-gang converter socket

Post by big-all »

incase its relevant
i have measured 3 plug in sockets and they are all between 100-110mm from the top surface off the earth pin to the bottom surface off the adaptor so finished about 2"/55mm below the actual socket level that would off course need a further say 25mm for moulded cord protector on thicker cables but not on wall plug in power sources

would something like this work ???
https://www.ebay.co.uk/itm/125006736000 ... K9SG4B7NG4

or this
https://www.ebay.co.uk/itm/286283309489 ... D9CNP0PBN7
we are all ------------------still learning
OnlineOnline
Rorschach
Senior Member
Posts: 5431
Joined: Wed Feb 26, 2014 9:35 pm
Has thanked: 120 times
Been thanked: 1043 times

3-gang converter socket

Post by Rorschach »

Someone-Else wrote: Fri Feb 28, 2025 6:54 pm
Rorschach wrote: Fri Feb 28, 2025 6:06 pmThere is no fuse so they are expecting you to pull up to 26amps.
If what you say is true, (and it isn't) why are they all clearly labelled as 13A?
Arse covering. If they put anything other than 13amp on there people would start putting devices rated higher than 13amp in there.

BTW, the 13amp is on the back, the bit you can't see when you are using it. If you really could only put 13amp through, they would write it on the front very clearly.
OnlyMe
Approved Electrician
Posts: 3132
Joined: Sun Apr 24, 2011 6:01 pm
Location: South Yorkshire
Has thanked: 225 times
Been thanked: 664 times

3-gang converter socket

Post by OnlyMe »

Rorschach wrote: Fri Feb 28, 2025 6:06 pm
Someone-Else wrote: Fri Feb 28, 2025 5:06 pm
Rorschach wrote: Fri Feb 28, 2025 4:07 pmThe only problem with 3 gang sockets is they are usually fused to 13amp which is annoying given a standard 2 gang will be 26amp
The majority of twin sockets are only rated for 13A



They are only tested to 20A
Plenty of people plug a kettle and toaster into a double socket and run it with no issues. There is no fuse so they are expecting you to pull up to 26amps. A 3 gang socket would not be able to handle kettle and toaster without blowing the fuse.
A 13A BS 1362 fuse will happily sit there and allow a kettle and toaster to run for hours. It will not even blow whilst the socket melts.
OnlyMe
Approved Electrician
Posts: 3132
Joined: Sun Apr 24, 2011 6:01 pm
Location: South Yorkshire
Has thanked: 225 times
Been thanked: 664 times

3-gang converter socket

Post by OnlyMe »

Someone-Else wrote: Fri Feb 28, 2025 5:06 pm
Rorschach wrote: Fri Feb 28, 2025 4:07 pmThe only problem with 3 gang sockets is they are usually fused to 13amp which is annoying given a standard 2 gang will be 26amp
The majority of twin sockets are only rated for 13A
s3.jpgs2.jpgs1.jpg


They are only tested to 20A
And in the real world is the OP trying to draw more than 1 amp?
Rorschach
Senior Member
Posts: 5431
Joined: Wed Feb 26, 2014 9:35 pm
Has thanked: 120 times
Been thanked: 1043 times

3-gang converter socket

Post by Rorschach »

OnlyMe wrote: Sun Mar 02, 2025 8:11 pm
Rorschach wrote: Fri Feb 28, 2025 6:06 pm
Someone-Else wrote: Fri Feb 28, 2025 5:06 pm
Rorschach wrote: Fri Feb 28, 2025 4:07 pmThe only problem with 3 gang sockets is they are usually fused to 13amp which is annoying given a standard 2 gang will be 26amp
The majority of twin sockets are only rated for 13A



They are only tested to 20A
Plenty of people plug a kettle and toaster into a double socket and run it with no issues. There is no fuse so they are expecting you to pull up to 26amps. A 3 gang socket would not be able to handle kettle and toaster without blowing the fuse.
A 13A BS 1362 fuse will happily sit there and allow a kettle and toaster to run for hours. It will not even blow whilst the socket melts.
I'll have to test this, I'd really like a 3 gang socket in my kitchen but have not done it because I will often need to pull more than 13amps from it.