Fan / Ceiling Light Removal / New Ceiling Pendant Install 2g 2w switch
Post by stefree0605 »
Hi,
I have removed a ceiling light fan and wired in a new pendant.
The wiring to the pendant are images attached.
Light Switch configuration is also attached.
The second switch turns light on and off but the operation of the 1st switch knocks out the mcb when switched on.
I have removed a ceiling light fan and wired in a new pendant.
The wiring to the pendant are images attached.
Light Switch configuration is also attached.
The second switch turns light on and off but the operation of the 1st switch knocks out the mcb when switched on.
- Attachments
-
- 20250323_094304.jpg (76.37 KiB) Viewed 268 times
-
- 20250323_094054.jpg (83.25 KiB) Viewed 268 times
stefree0605
- Someone-Else
- Senior Member
- Posts: 14827
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 48 times
- Been thanked: 2604 times
Fan / Ceiling Light Removal / New Ceiling Pendant Install 2g 2w switch
Post by Someone-Else »
You have connected the switch across Live and Neutral. It is only supposed to "break" the live.
Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section

Someone-Else
-
- Newly registered Member
- Posts: 8
- Joined: Tue Mar 05, 2024 6:50 pm
- Has thanked: 0
- Been thanked: 0
Fan / Ceiling Light Removal / New Ceiling Pendant Install 2g 2w switch
Post by stefree0605 »
Thank you,
What would be the best way to rectify this?
Link the red 1 way switch at the 1st switch across to the com output red conductor at the second switch?
What would be the best way to rectify this?
Link the red 1 way switch at the 1st switch across to the com output red conductor at the second switch?
stefree0605
- Someone-Else
- Senior Member
- Posts: 14827
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 48 times
- Been thanked: 2604 times
Fan / Ceiling Light Removal / New Ceiling Pendant Install 2g 2w switch
Post by Someone-Else »
To wire it correctly.
You need to test/identify what each wire does, it is not clear in your pictures what each wire is doing. I presume you have no means of testing? if so read my signature.
Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section

Someone-Else
-
- Newly registered Member
- Posts: 8
- Joined: Tue Mar 05, 2024 6:50 pm
- Has thanked: 0
- Been thanked: 0
Fan / Ceiling Light Removal / New Ceiling Pendant Install 2g 2w switch
Post by stefree0605 »
Yes I have a multimeter Duratool D0347.
stefree0605
-
- Newly registered Member
- Posts: 8
- Joined: Tue Mar 05, 2024 6:50 pm
- Has thanked: 0
- Been thanked: 0
Fan / Ceiling Light Removal / New Ceiling Pendant Install 2g 2w switch
Post by stefree0605 »
This was how the ceiling fan light was wired originally.
- 20250322_112940.jpg (99.73 KiB) Viewed 241 times
- 20250322_112950.jpg (97.99 KiB) Viewed 241 times
- 20250322_112946.jpg (106.36 KiB) Viewed 241 times
stefree0605
-
- Newly registered Member
- Posts: 8
- Joined: Tue Mar 05, 2024 6:50 pm
- Has thanked: 0
- Been thanked: 0
Fan / Ceiling Light Removal / New Ceiling Pendant Install 2g 2w switch
Post by stefree0605 »
Just to clarify, the wiring at the 2g 2w switch has stayed the same and I haven't altered this. I have however put a new pendant in place of ceiling fan/light.
stefree0605
-
- Approved Electrician
- Posts: 3132
- Joined: Sun Apr 24, 2011 6:01 pm
- Location: South Yorkshire
- Has thanked: 225 times
- Been thanked: 664 times
Fan / Ceiling Light Removal / New Ceiling Pendant Install 2g 2w switch
So the 2 gang switch had one gang operate the light and the other gang operate the fan and all you need now is a 1g switch?stefree0605 wrote: ↑Sun Mar 23, 2025 3:08 pm Just to clarify, the wiring at the 2g 2w switch has stayed the same and I haven't altered this. I have however put a new pendant in place of ceiling fan/light.
OnlyMe
-
- Newly registered Member
- Posts: 8
- Joined: Tue Mar 05, 2024 6:50 pm
- Has thanked: 0
- Been thanked: 0
Fan / Ceiling Light Removal / New Ceiling Pendant Install 2g 2w switch
Post by stefree0605 »
Yes.
The fan was operated by the 1st switch with the red conductor in the 1 way switch terminal and the black wire in the com terminal. One of the cables in the ceiling was marked up fan power in the ceiling.
The 2nd switch was wired in 3 core and earth (old colours) and has a red conductor in the com output with the blue and yellow conductors in the L1 L2 terminal respectively.
Before I took the ceiling fan light down I switched the 1st switch on and off and the mcb didn't trip, but now that I have wired the pendant, it knocks out the mcb when I switch it back on, 2nd switch works fine with light on and off working as it should. Is it as simple as just changing the switch for a 1g 2w switch? If so where would the wiring go that used to operate the ceiling fan ie red conductor in 1w terminal and black conductor in com which is located in 1st switch?
The fan was operated by the 1st switch with the red conductor in the 1 way switch terminal and the black wire in the com terminal. One of the cables in the ceiling was marked up fan power in the ceiling.
The 2nd switch was wired in 3 core and earth (old colours) and has a red conductor in the com output with the blue and yellow conductors in the L1 L2 terminal respectively.
Before I took the ceiling fan light down I switched the 1st switch on and off and the mcb didn't trip, but now that I have wired the pendant, it knocks out the mcb when I switch it back on, 2nd switch works fine with light on and off working as it should. Is it as simple as just changing the switch for a 1g 2w switch? If so where would the wiring go that used to operate the ceiling fan ie red conductor in 1w terminal and black conductor in com which is located in 1st switch?
stefree0605
-
- Approved Electrician
- Posts: 3132
- Joined: Sun Apr 24, 2011 6:01 pm
- Location: South Yorkshire
- Has thanked: 225 times
- Been thanked: 664 times
Fan / Ceiling Light Removal / New Ceiling Pendant Install 2g 2w switch
So just take the black wire out of the switch and put it into a wago connector and use the other switch to operate the light.
OnlyMe
-
- Newly registered Member
- Posts: 8
- Joined: Tue Mar 05, 2024 6:50 pm
- Has thanked: 0
- Been thanked: 0
Fan / Ceiling Light Removal / New Ceiling Pendant Install 2g 2w switch
Post by stefree0605 »
Okay.
Thank you for your help, I thought I had wired up the pendant incorrectly and it was interfering with the 1st switch and hence taking out the mcb when I turned the 1st switch on.
I will do just that.
Thank you for your help, I thought I had wired up the pendant incorrectly and it was interfering with the 1st switch and hence taking out the mcb when I turned the 1st switch on.
I will do just that.
stefree0605
Jump to
- Ultimate Handyman DIY forum
- ↳ Welcome to the Ultimate Handyman DIY Forum
- WELCOME
- ↳ WELCOME
- ↳ About the forums
- UltimateHandyman Discounts
- ↳ Ultimatehandyman Discounts
- ULTIMATE HANDYMAN COMPETITIONS
- ↳ UHM Forum competitions
- SHOW CASE- A place to show us your work
- ↳ Show Case Gallery
- ↳ Rogues Gallery
- TOOL FORUM
- ↳ Power Tool Reviews
- ↳ Bosch
- ↳ budget power tools
- ↳ Dewalt
- ↳ Festool
- ↳ Hikoki/Hitachi
- ↳ Makita
- ↳ Metabo
- ↳ Milwaukee
- ↳ Ryobi
- ↳ Tool Talk
- ↳ Bargain Tools
- ↳ Hand tool reviews
- ↳ Power Tool Manuals
- ↳ Bosch
- ↳ Dolmar
- ↳ ELEKTRA BECKUM
- ↳ Hitachi
- ↳ Husqvarna
- ↳ Jonsered
- ↳ Makita
- ↳ Stihl
- Other DIY
- ↳ Computers
- ↳ communications and broadband
- ↳ Gardeners World
- ↳ Money Saving
- ↳ Vehicle maintenance & Repair
- ↳ Energy Saving
- DIY Forum/Home improvement
- ↳ General DIY forum
- ↳ Acrylic Forum
- ↳ DIY Disasters
- ↳ Stoves
- ↳ Building Forum
- ↳ Carpentry/Joinery Forum
- ↳ Kitchen Fitting
- ↳ Damp Proofing and Remedial problems
- ↳ Electric Forum UK
- ↳ Lighting
- ↳ Alarm Manuals
- ↳ Painting & Decorating Forum
- ↳ Plastering Forum
- ↳ Plumbing Forum
- ↳ Central Heating & Boilers
- ↳ Boiler Manuals
- ↳ Alpha
- ↳ Ariston
- ↳ ATAG
- ↳ Atmos
- ↳ Baxi
- ↳ Biasi
- ↳ Broag
- ↳ Chaffoteux
- ↳ Ferroli
- ↳ Glow-worm
- ↳ Halstead
- ↳ Ideal
- ↳ Intergas
- ↳ Keston
- ↳ Myson
- ↳ Potterton
- ↳ Protherm
- ↳ Ravenheat
- ↳ Saunier Duval
- ↳ Sime
- ↳ Thorn
- ↳ Vaillant
- ↳ Viessmann
- ↳ Vokera
- ↳ warmflow
- ↳ Worcester Bosch
- ↳ Shower Manuals
- ↳ Tiling Forum
- ↳ Metalworking Forum
- General
- ↳ The Lounge
- ↳ The games corner
- ↳ The Grumpy corner
- ↳ The Sport corner
- ↳ The Cookery corner
- ↳ The Music Corner
- ↳ BUY - SELL - FREE