Earthing the cable protection
All your electrical questions regarding electrics from within the United Kingdom
Moderator: Moderators
-
- Senior Member
- Posts: 986
- Joined: Sat Feb 24, 2007 11:50 am
- Location: Cotswolds
- Has thanked: 0
- Been thanked: 0
Earthing the cable protection
If I've chased out channels for electrical cabling and covered them with steel to prevent damage to the cables, should I earth the steel?
The steel is quite thick about 1mm and it's firmly screwed to the wall. Folk have said that if somebody does manage to get a drill though it they deserve to get fried.
But being more serious about it, is there a small chance that the drill bit would only knick the live core and not the earth as well thus leaving the drill bit live?
If I earthed the plating, this should trip the RCD when the drill touches the current.
Thanks
The steel is quite thick about 1mm and it's firmly screwed to the wall. Folk have said that if somebody does manage to get a drill though it they deserve to get fried.
But being more serious about it, is there a small chance that the drill bit would only knick the live core and not the earth as well thus leaving the drill bit live?
If I earthed the plating, this should trip the RCD when the drill touches the current.
Thanks
Slugster
- ultimatehandyman
- Site Admin
- Posts: 24426
- Joined: Sat Jul 16, 2005 7:06 pm
- Location: Darwen, Lancashire
- Has thanked: 1012 times
- Been thanked: 918 times
Post by ultimatehandyman »
Is the steel Galvanised?
I'd earth it to be on the safe side, you should be able to do this with a couple of rust resistant bolts and some wire.
I'd earth it to be on the safe side, you should be able to do this with a couple of rust resistant bolts and some wire.
ultimatehandyman
Slugster
- sparkydude
- Senior Member
- Posts: 2253
- Joined: Sat Aug 13, 2005 7:11 pm
- Location: Staffordshire
- Has thanked: 2 times
- Been thanked: 149 times
Post by sparkydude »
was this protection , proper cable capping or did you just buy some galv steel sheet?
If it isnt broke dont bloody touch it until it bloody well is and if it is broke then make drawing of the connections before you remove the broken one and replace with a new one LoL
sparkydude
Slugster
- sparkydude
- Senior Member
- Posts: 2253
- Joined: Sat Aug 13, 2005 7:11 pm
- Location: Staffordshire
- Has thanked: 2 times
- Been thanked: 149 times
Post by sparkydude »
i see, hope you protected the edges of the sheet with galvanising paint or else the rust might bleed through your plaster. There is no reason to bond this protection as it is not an exposed conductive part. Nothing like a bit of over engineering a solution to a problem is there
Nick
Nick
If it isnt broke dont bloody touch it until it bloody well is and if it is broke then make drawing of the connections before you remove the broken one and replace with a new one LoL
sparkydude
-
- Senior Member
- Posts: 986
- Joined: Sat Feb 24, 2007 11:50 am
- Location: Cotswolds
- Has thanked: 0
- Been thanked: 0
Sparky,
I wish there was a "Oh b*llox" smilie
but this is the closest I could find.
You know I didn't do that LOL...
I hope that because the house is dry and I've blobed the board on instead of a wet plaster job I'll get away with it.
Again I'll take this away for the next time - if I live that long
Thanks for clearing up about earthing the plates.
Cheers
I wish there was a "Oh b*llox" smilie

You know I didn't do that LOL...
I hope that because the house is dry and I've blobed the board on instead of a wet plaster job I'll get away with it.
Again I'll take this away for the next time - if I live that long

Thanks for clearing up about earthing the plates.
Cheers
Slugster
- ultimatehandyman
- Site Admin
- Posts: 24426
- Joined: Sat Jul 16, 2005 7:06 pm
- Location: Darwen, Lancashire
- Has thanked: 1012 times
- Been thanked: 918 times
Post by ultimatehandyman »
You should get away with it as you have dot and dabbed over it
It's unlikely that the plasterboard is actually touching the steel and so it should not show through if it rusts.

It's unlikely that the plasterboard is actually touching the steel and so it should not show through if it rusts.
ultimatehandyman
-
- Gas/Heating Expert
- Posts: 4382
- Joined: Mon Jan 16, 2006 9:40 pm
- Location: Bournemouth
- Has thanked: 0
- Been thanked: 9 times
Post by Hinton Heating »
this has always surprised me, why cables arn't protected in such a manner as standard, but a flimsy plastic nail over cover is good enough...
thats never gonna stop anything... guess they hope the earthing will protect against shock, but doesn't help with repairing the cable after someone has drilled thro it!
thats never gonna stop anything... guess they hope the earthing will protect against shock, but doesn't help with repairing the cable after someone has drilled thro it!
Last edited by Hinton Heating on Sat Mar 03, 2007 8:23 pm, edited 1 time in total.
Hinton Heating
- ultimatehandyman
- Site Admin
- Posts: 24426
- Joined: Sat Jul 16, 2005 7:06 pm
- Location: Darwen, Lancashire
- Has thanked: 1012 times
- Been thanked: 918 times
Post by ultimatehandyman »
Capping is only there to protect the cable whilst plastering over the cables.Hinton Heating wrote:this has always suprised me, why cables arn't peotected in such a manner as standard, but a flimsy plastic nail over cover is good enougth...
thats never gonna stop anything... guess they hope the earthing will protect against shock, but doesn't help with repairing the cable after someone has drilled thro it!
Electricians and most tradesmen have a good idea of where the permitted zones are and where cables are likely to run. Most diyer's don't unfortunately.
The next time I do any serious wiring ( I will inform BC ) I am going to use the oval shaped plastic conduit, it looks like a damn good idea to me

ultimatehandyman
-
- Gas/Heating Expert
- Posts: 4382
- Joined: Mon Jan 16, 2006 9:40 pm
- Location: Bournemouth
- Has thanked: 0
- Been thanked: 9 times
Post by Hinton Heating »
I must admit, I've only ever drilled through one cable, and that was because it was installed at an angle leading to a wall light! 

Hinton Heating
-
- Senior Member
- Posts: 986
- Joined: Sat Feb 24, 2007 11:50 am
- Location: Cotswolds
- Has thanked: 0
- Been thanked: 0
Again this is an example of my anal retentiveness.
I know where the cables are so I'm actually doing this for the benefit of the next lot who buy the place
Here's a typical installation. The isolator switch is for the underfloor heating.
I use an angle grinder to cut a 2" wide channel an 1" deep. I thne dig it out with the mutli hammer.
I like to have plenty of space for the cables.
I know where the cables are so I'm actually doing this for the benefit of the next lot who buy the place

Here's a typical installation. The isolator switch is for the underfloor heating.
I use an angle grinder to cut a 2" wide channel an 1" deep. I thne dig it out with the mutli hammer.
I like to have plenty of space for the cables.
- Attachments
-
- capping.jpg (28.76 KiB) Viewed 4529 times
Slugster
- ultimatehandyman
- Site Admin
- Posts: 24426
- Joined: Sat Jul 16, 2005 7:06 pm
- Location: Darwen, Lancashire
- Has thanked: 1012 times
- Been thanked: 918 times
Post by ultimatehandyman »
To be fair you have done a good job there, with the best of intentions!
Not many people will go to that kind of trouble!
There is no chance of anyone accidentally drilling through those cables.
If you were dot and dabbing it, you could of just clipped the cable to the brick, there would of been no need to chase out the channels.
I like what you have done to be honest, it looks pretty good to me
Not many people will go to that kind of trouble!
There is no chance of anyone accidentally drilling through those cables.
If you were dot and dabbing it, you could of just clipped the cable to the brick, there would of been no need to chase out the channels.
I like what you have done to be honest, it looks pretty good to me

ultimatehandyman
Slugster
- sparkydude
- Senior Member
- Posts: 2253
- Joined: Sat Aug 13, 2005 7:11 pm
- Location: Staffordshire
- Has thanked: 2 times
- Been thanked: 149 times
Post by sparkydude »
Yep typical OTT approach to DIY wiring LOL But i must admit a lot better than a hell of a lot of other jobs i have seen done by diyers. Well done even if it is WAY WAY WAY WAY OTT LoL
Nick



Nick
If it isnt broke dont bloody touch it until it bloody well is and if it is broke then make drawing of the connections before you remove the broken one and replace with a new one LoL
sparkydude
Jump to
- Ultimate Handyman DIY forum
- ↳ Welcome to the Ultimate Handyman DIY Forum
- WELCOME
- ↳ WELCOME
- ↳ About the forums
- UltimateHandyman Discounts
- ↳ Ultimatehandyman Discounts
- ULTIMATE HANDYMAN COMPETITIONS
- ↳ UHM Forum competitions
- SHOW CASE- A place to show us your work
- ↳ Show Case Gallery
- ↳ Rogues Gallery
- TOOL FORUM
- ↳ Power Tool Reviews
- ↳ Bosch
- ↳ budget power tools
- ↳ Dewalt
- ↳ Festool
- ↳ Hikoki/Hitachi
- ↳ Makita
- ↳ Metabo
- ↳ Milwaukee
- ↳ Ryobi
- ↳ Tool Talk
- ↳ Bargain Tools
- ↳ Hand tool reviews
- ↳ Power Tool Manuals
- ↳ Bosch
- ↳ Dolmar
- ↳ ELEKTRA BECKUM
- ↳ Hitachi
- ↳ Husqvarna
- ↳ Jonsered
- ↳ Makita
- ↳ Stihl
- Other DIY
- ↳ Computers
- ↳ communications and broadband
- ↳ Gardeners World
- ↳ Money Saving
- ↳ Vehicle maintenance & Repair
- ↳ Energy Saving
- DIY Forum/Home improvement
- ↳ General DIY forum
- ↳ Acrylic Forum
- ↳ DIY Disasters
- ↳ Stoves
- ↳ Building Forum
- ↳ Carpentry/Joinery Forum
- ↳ Kitchen Fitting
- ↳ Damp Proofing and Remedial problems
- ↳ Electric Forum UK
- ↳ Lighting
- ↳ Alarm Manuals
- ↳ Painting & Decorating Forum
- ↳ Plastering Forum
- ↳ Plumbing Forum
- ↳ Central Heating & Boilers
- ↳ Boiler Manuals
- ↳ Alpha
- ↳ Ariston
- ↳ ATAG
- ↳ Atmos
- ↳ Baxi
- ↳ Biasi
- ↳ Broag
- ↳ Chaffoteux
- ↳ Ferroli
- ↳ Glow-worm
- ↳ Halstead
- ↳ Ideal
- ↳ Intergas
- ↳ Keston
- ↳ Myson
- ↳ Potterton
- ↳ Protherm
- ↳ Ravenheat
- ↳ Saunier Duval
- ↳ Sime
- ↳ Thorn
- ↳ Vaillant
- ↳ Viessmann
- ↳ Vokera
- ↳ warmflow
- ↳ Worcester Bosch
- ↳ Shower Manuals
- ↳ Tiling Forum
- ↳ Metalworking Forum
- General
- ↳ The Lounge
- ↳ The games corner
- ↳ The Grumpy corner
- ↳ The Sport corner
- ↳ The Cookery corner
- ↳ The Music Corner
- ↳ BUY - SELL - FREE