WALL SHOWER STOPPED WORKING
HI EVERYONE,
I HAVE AN ELECTRIC SHOWER AT HOME.
WENT TO GET A SHOWER THIS MORNING. SWITCHED IT ON AND WATER CAME OUT INITIALLY BUT THEN IT STARTED TO SPLUTTER, CAME OUT IN DRIBS AND DRABS AND THEN THE SHOWER POWER LIGHT WENT OFF.
I PULLED THE POWER CORD TO OFF AND SWITCHED THE SHOWER OFF ALSO.
WENT TO PULL ON/OFF CORD AGAIN TO TURN BACK ON BUT THIS TIME IT WOULDN'T LET ME PULL CORD DOWN TO SWITCH ON!
I WENT AND CHECKED THE MAINS AND THE SHOWER SWITCH HAD TRIPPED. I FLICKED THAT TO ON (ENSURING THE MAINS SWITCH WAS BACK ON ALSO!) BUT THE POWER CORD IN BATHROOM WON'T PULL DOWN TO ON.
CAN ANYONE PLEASE ADVISE HOW TO RECTIFY THIS?
THANKS IN ADVANCE TO ALL WHO REPLY.
REGARDS,
MARK.
I HAVE AN ELECTRIC SHOWER AT HOME.
WENT TO GET A SHOWER THIS MORNING. SWITCHED IT ON AND WATER CAME OUT INITIALLY BUT THEN IT STARTED TO SPLUTTER, CAME OUT IN DRIBS AND DRABS AND THEN THE SHOWER POWER LIGHT WENT OFF.
I PULLED THE POWER CORD TO OFF AND SWITCHED THE SHOWER OFF ALSO.
WENT TO PULL ON/OFF CORD AGAIN TO TURN BACK ON BUT THIS TIME IT WOULDN'T LET ME PULL CORD DOWN TO SWITCH ON!
I WENT AND CHECKED THE MAINS AND THE SHOWER SWITCH HAD TRIPPED. I FLICKED THAT TO ON (ENSURING THE MAINS SWITCH WAS BACK ON ALSO!) BUT THE POWER CORD IN BATHROOM WON'T PULL DOWN TO ON.
CAN ANYONE PLEASE ADVISE HOW TO RECTIFY THIS?
THANKS IN ADVANCE TO ALL WHO REPLY.
REGARDS,
MARK.
diymark
- ultimatehandyman
- Site Admin
- Posts: 24426
- Joined: Sat Jul 16, 2005 7:06 pm
- Location: Darwen, Lancashire
- Has thanked: 1012 times
- Been thanked: 918 times
Post by ultimatehandyman »
Mark, I will move this to the electrical forum as it seems like an electrical fault!
ultimatehandyman
diymark
- ultimatehandyman
- Site Admin
- Posts: 24426
- Joined: Sat Jul 16, 2005 7:06 pm
- Location: Darwen, Lancashire
- Has thanked: 1012 times
- Been thanked: 918 times
Post by ultimatehandyman »
No worriesdiymark wrote:Thank you very much, apologies for putting it into the wrong forum.

It sounds like the pull switch may be faulty, but there could also be another fault and so it is best to see what some of the pro's say

ultimatehandyman
-
- Senior Member
- Posts: 986
- Joined: Sat Feb 24, 2007 11:50 am
- Location: Cotswolds
- Has thanked: 0
- Been thanked: 0
This is strange...
It sounds like there is a problem with the shower and one with the isolator switch.
Unless you mean the light went out on the isolator switch.
I'm trying to remember how my old lecy shower worked. I know there was a pressure sensing valve that would cut the juice if the pressre / flow rate fell to the point the element would cook, but I can't remember if the shower flow would cut if the electrical supply was interrupted.
If the flow is stopped when power is cut the fault could be with the isolator switch.
DIYMark, what's the make and model of the shower?
It sounds like there is a problem with the shower and one with the isolator switch.
Unless you mean the light went out on the isolator switch.
I'm trying to remember how my old lecy shower worked. I know there was a pressure sensing valve that would cut the juice if the pressre / flow rate fell to the point the element would cook, but I can't remember if the shower flow would cut if the electrical supply was interrupted.
If the flow is stopped when power is cut the fault could be with the isolator switch.
DIYMark, what's the make and model of the shower?
Slugster
- sparkydude
- Senior Member
- Posts: 2253
- Joined: Sat Aug 13, 2005 7:11 pm
- Location: Staffordshire
- Has thanked: 2 times
- Been thanked: 149 times
Post by sparkydude »
Turn off the power to your shower . open up the pullcord and look for the loose conection. If the pullcord will not click on or off anymore it sounds like a loose connection in the pullcord has burnt out, or arced itself open and will not allow you to turn it on. Also check the final connections at the shower end to confirm its not them.
Let us know how you get on
Nick
Let us know how you get on
Nick
If it isnt broke dont bloody touch it until it bloody well is and if it is broke then make drawing of the connections before you remove the broken one and replace with a new one LoL
sparkydude
-
- Newly registered Member
- Posts: 25
- Joined: Mon Jan 22, 2007 8:19 pm
- Has thanked: 0
- Been thanked: 0
Thanks Slugster and Sparkydude for your responses.
I am very grateful indeed and your information was beneficial.
I opened up the pullcord and found it completely fried inside.
The black wires (N in) and (N out) are fine
The two Earth (Green & Yellow) wires are fine
Pull cord connections OK
1 x Live (RED) wire is fine
1 x Other wire (I actually cant tell what colour it was) is all black and burnt and the terminal it was connected to has solidified and burnt!
What has happened...has this wire come loose and touched another wire or has water got in? Least I know why shower stopped and think I just need to get new box and reconnect all wires.
Any further comments would be grateful and thanks again everyone for your assistance.
regards,
Mark.
I am very grateful indeed and your information was beneficial.
I opened up the pullcord and found it completely fried inside.
The black wires (N in) and (N out) are fine
The two Earth (Green & Yellow) wires are fine
Pull cord connections OK
1 x Live (RED) wire is fine
1 x Other wire (I actually cant tell what colour it was) is all black and burnt and the terminal it was connected to has solidified and burnt!
What has happened...has this wire come loose and touched another wire or has water got in? Least I know why shower stopped and think I just need to get new box and reconnect all wires.
Any further comments would be grateful and thanks again everyone for your assistance.
regards,
Mark.
diymark
-
- Newly registered Member
- Posts: 25
- Joined: Mon Jan 22, 2007 8:19 pm
- Has thanked: 0
- Been thanked: 0
Thanks Slugster and Sparkydude for your responses.
I am very grateful indeed and your information was beneficial.
I opened up the pullcord and found it completely fried inside.
The black wires (N in) and (N out) are fine
The two Earth (Green & Yellow) wires are fine
Pull cord connections OK
1 x Live (RED) wire is fine
1 x Other wire (I actually cant tell what colour it was) is all black and burnt and the terminal it was connected to has solidified and burnt!
What has happened...has this wire come loose and touched another wire or has water got in? Least I know why shower stopped and think I just need to get new box and reconnect all wires.
Any further comments would be grateful and thanks again everyone for your assistance.
regards,
Mark.
I am very grateful indeed and your information was beneficial.
I opened up the pullcord and found it completely fried inside.
The black wires (N in) and (N out) are fine
The two Earth (Green & Yellow) wires are fine
Pull cord connections OK
1 x Live (RED) wire is fine
1 x Other wire (I actually cant tell what colour it was) is all black and burnt and the terminal it was connected to has solidified and burnt!
What has happened...has this wire come loose and touched another wire or has water got in? Least I know why shower stopped and think I just need to get new box and reconnect all wires.
Any further comments would be grateful and thanks again everyone for your assistance.
regards,
Mark.
diymark
-
- BANNED
- Posts: 2136
- Joined: Wed Jan 18, 2006 10:48 pm
- Location: Leicestershire
- Has thanked: 0
- Been thanked: 1 time
Post by tim'll fix it »
the wire was loose and has burnt out with the arcing
isolate the shower at the fuse board
buy a new switch and connect it all back up again.
Hopefully there will be enough slack cable in the attic to pull the burnt out wire throught a bit more to strip it back to an unburnt bit of cable
Its a common fault
isolate the shower at the fuse board
buy a new switch and connect it all back up again.
Hopefully there will be enough slack cable in the attic to pull the burnt out wire throught a bit more to strip it back to an unburnt bit of cable
Its a common fault
tim'll fix it
diymark
- sparkydude
- Senior Member
- Posts: 2253
- Joined: Sat Aug 13, 2005 7:11 pm
- Location: Staffordshire
- Has thanked: 2 times
- Been thanked: 149 times
Post by sparkydude »
i am sure you will be able to gain enough slack to re terminate it. if not then as you say you will need a 30A junction box , and some replacement cable to extend the three cores of the cable to your pullcord.
Nick
Nick
If it isnt broke dont bloody touch it until it bloody well is and if it is broke then make drawing of the connections before you remove the broken one and replace with a new one LoL
sparkydude
-
- Newly registered Member
- Posts: 25
- Joined: Mon Jan 22, 2007 8:19 pm
- Has thanked: 0
- Been thanked: 0
Hi, thanks to everyone who gave me adviceon this initial problam - cut out all burnt wires, stripped back and fitted new pull cord switch and heh presto! I have my shower back.
Small problem and I think it's a wiring one - when I turned pullcord switch to off, light stays on! - Does this mean my black neutral wires are wired wrong way round?
Look forward to your assistance.
Regards,
Mark.
Small problem and I think it's a wiring one - when I turned pullcord switch to off, light stays on! - Does this mean my black neutral wires are wired wrong way round?
Look forward to your assistance.
Regards,
Mark.
diymark
- ultimatehandyman
- Site Admin
- Posts: 24426
- Joined: Sat Jul 16, 2005 7:06 pm
- Location: Darwen, Lancashire
- Has thanked: 1012 times
- Been thanked: 918 times
Post by ultimatehandyman »
Does the shower work when the switch is in the on or off position?diymark wrote:Hi, thanks to everyone who gave me adviceon this initial problam - cut out all burnt wires, stripped back and fitted new pull cord switch and heh presto! I have my shower back.
Small problem and I think it's a wiring one - when I turned pullcord switch to off, light stays on! - Does this mean my black neutral wires are wired wrong way round?
Look forward to your assistance.
Regards,
Mark.
ultimatehandyman
diymark
- ultimatehandyman
- Site Admin
- Posts: 24426
- Joined: Sat Jul 16, 2005 7:06 pm
- Location: Darwen, Lancashire
- Has thanked: 1012 times
- Been thanked: 918 times
Post by ultimatehandyman »
DOH, yes silly me for asking that
It sounds like the supply and feed are wired the wrong way around!
The feed or supply terminals are for the wire that comes from the consumer unit and the load terminals are for the wires going to the shower unit, If it is illuminated when switched off then these wires are the wrong way around!

It sounds like the supply and feed are wired the wrong way around!
The feed or supply terminals are for the wire that comes from the consumer unit and the load terminals are for the wires going to the shower unit, If it is illuminated when switched off then these wires are the wrong way around!
ultimatehandyman
Jump to
- Ultimate Handyman DIY forum
- ↳ Welcome to the Ultimate Handyman DIY Forum
- WELCOME
- ↳ WELCOME
- ↳ About the forums
- UltimateHandyman Discounts
- ↳ Ultimatehandyman Discounts
- ULTIMATE HANDYMAN COMPETITIONS
- ↳ UHM Forum competitions
- SHOW CASE- A place to show us your work
- ↳ Show Case Gallery
- ↳ Rogues Gallery
- TOOL FORUM
- ↳ Power Tool Reviews
- ↳ Bosch
- ↳ budget power tools
- ↳ Dewalt
- ↳ Festool
- ↳ Hikoki/Hitachi
- ↳ Makita
- ↳ Metabo
- ↳ Milwaukee
- ↳ Ryobi
- ↳ Tool Talk
- ↳ Bargain Tools
- ↳ Hand tool reviews
- ↳ Power Tool Manuals
- ↳ Bosch
- ↳ Dolmar
- ↳ ELEKTRA BECKUM
- ↳ Hitachi
- ↳ Husqvarna
- ↳ Jonsered
- ↳ Makita
- ↳ Stihl
- Other DIY
- ↳ Computers
- ↳ communications and broadband
- ↳ Gardeners World
- ↳ Money Saving
- ↳ Vehicle maintenance & Repair
- ↳ Energy Saving
- DIY Forum/Home improvement
- ↳ General DIY forum
- ↳ Acrylic Forum
- ↳ DIY Disasters
- ↳ Stoves
- ↳ Building Forum
- ↳ Carpentry/Joinery Forum
- ↳ Kitchen Fitting
- ↳ Damp Proofing and Remedial problems
- ↳ Electric Forum UK
- ↳ Lighting
- ↳ Alarm Manuals
- ↳ Painting & Decorating Forum
- ↳ Plastering Forum
- ↳ Plumbing Forum
- ↳ Central Heating & Boilers
- ↳ Boiler Manuals
- ↳ Alpha
- ↳ Ariston
- ↳ ATAG
- ↳ Atmos
- ↳ Baxi
- ↳ Biasi
- ↳ Broag
- ↳ Chaffoteux
- ↳ Ferroli
- ↳ Glow-worm
- ↳ Halstead
- ↳ Ideal
- ↳ Intergas
- ↳ Keston
- ↳ Myson
- ↳ Potterton
- ↳ Protherm
- ↳ Ravenheat
- ↳ Saunier Duval
- ↳ Sime
- ↳ Thorn
- ↳ Vaillant
- ↳ Viessmann
- ↳ Vokera
- ↳ warmflow
- ↳ Worcester Bosch
- ↳ Shower Manuals
- ↳ Tiling Forum
- ↳ Metalworking Forum
- General
- ↳ The Lounge
- ↳ The games corner
- ↳ The Grumpy corner
- ↳ The Sport corner
- ↳ The Cookery corner
- ↳ The Music Corner
- ↳ BUY - SELL - FREE