Posted: Sat Oct 14, 2006 11:50 am
by Blueboy4ever
Hi Guys hope you can help. I have bought a replacement light fitting and cannot get my head around the wiring. On removing my old light there was;
Black and red cable together
Two reds together
Two blacks together
Three yellow/ green together
On the new fitting there is only two wiring points, two marked neutral and two marked live? Please help.
Posted: Sat Oct 14, 2006 1:21 pm
by ultimatehandyman
Hi,
and welcome to the forum.
Is there no earthing point on the light fitting?
What type of light fitting is it? For example is it a fan light etc.
when you say that the wires are together, what exactly do you mean?
Do you mean they were terminated in the same terminal?
Posted: Sat Oct 14, 2006 1:22 pm
by markysparky
The 2 blacks put into the neutrals
the red wire and black wire put into the live
The 2 reds put into a strip connector and that is it. do not connect into the light in any way
Green and yellows go into earth.
Posted: Sat Oct 14, 2006 1:29 pm
by markysparky
I'm assuming that the extra wire for the live is to do another light.
Does the light you are fitting come on with another light by any chance
:
Posted: Sat Oct 14, 2006 2:14 pm
by Blueboy4ever
The light is connected to an extractor fan.
Posted: Sat Oct 14, 2006 2:21 pm
by Blueboy4ever
......and the instructions say that the light does not need to be earthed
Posted: Sat Oct 14, 2006 2:26 pm
by Blueboy4ever
Have tried what you said MarkySparky, but nothing is happening (no light comes on and the seperate extractor fan is not running).
Posted: Sat Oct 14, 2006 2:32 pm
by ultimatehandyman
Is there no instruction manual with it?
Are you sure there are no other markings on the fitting besides 2* neutrals and lives?
Is there no symbol that looks like a switch ___/ ___ or similar?
Posted: Sat Oct 14, 2006 2:51 pm
by Blueboy4ever
There are some very brief instructions which state
' If a wiring loop system is used within your home there may be several cables coming out of your ceiling. Before disconnecting your existing light please make a note which cables it is connected to and connect your new fitting to thses wires.'
There are definetly just the four connection points, two Live Terminals and two Neutral terminals.
Posted: Sat Oct 14, 2006 5:04 pm
by honeymonster
It sounds like there is a terminal for the permanent live and switched live on the new light, so that the fan can continue to run once the light is switched off.
The instructions seem very poor!
The terminals in the light fitting-
do the two neutrals wire to the same bit inside of the light or are they definately two individual terminals?
Posted: Sat Oct 14, 2006 5:08 pm
by honeymonster
It may be a good idea to post a picture if possible?
Posted: Sat Oct 14, 2006 5:57 pm
by markysparky
The red and black wire! are they in the same terminal? They are not in seperate terminals by any chance?
If they are seperate put them together into the L terminal and see what happens
Posted: Sun Oct 15, 2006 8:38 am
by Blueboy4ever
Tried to put the red and black wires in the same terminal - still nothing. I am going to rip my hair out soon :!:
Posted: Sun Oct 15, 2006 9:01 am
by Blueboy4ever
Sod it, i have just found a direct replacement for the light that i had originally in my bathroom on Screwfix - so i have ordered it! Can't be doing with that other bloody thing any longer ! Its free to a good home if anybody wants it!
Posted: Sun Oct 15, 2006 9:28 am
by Hinton Heating
generally a light on a loop circuit will have the following connections
earth - all the earths in a terminal block
Neutral - The loop circuit Neutral (normally 2 blacks) + the bulb Neutral + the fan neural
Perm Live - The loop circuit live (normally 2 reds) + supply to switch (normally red) + live to fan
Switch live - return from light (normally black) + the bulb live + the switch live to fan
There are your 3 terminals on your light! 8-)