110v USA tools with petrol generator

Post by D4np »

Hi everyone , will USA 110v power tools run off of a UK 110v petrol generator if I change the plug ?

Thanks
User avatar
kellys_eye
Senior Member
Posts: 12309
Joined: Mon Mar 15, 2010 11:49 pm
Location: Oban
Has thanked: 357 times
Been thanked: 1790 times

Re: 110v USA tools with petrol generator

Post by kellys_eye »

Yes but they might get a little hot as they are designed for 60Hz whereas ours is 50Hz.

Check your generator for any adjustment to change between 50/60Hz.
Don't take it personally......
D4np
Newly registered Member
Posts: 89
Joined: Sun Mar 05, 2017 8:23 pm
Has thanked: 8 times
Been thanked: 1 time

Re: 110v USA tools with petrol generator

Post by D4np »

kellys_eye wrote:Yes but they might get a little hot as they are designed for 60Hz whereas ours is 50Hz.

Check your generator for any adjustment to change between 50/60Hz.
Thank you for your reply , I will have a look to see if it says anywhere on the generator . A lot of tools say 50hz-60hz on them


Sent from my iPhone using Tapatalk
User avatar
Job and Knock
Old School Chippie
Posts: 6667
Joined: Mon Sep 12, 2011 3:27 pm
Has thanked: 742 times
Been thanked: 1573 times

Re: 110v USA tools with petrol generator

Post by Job and Knock »

I run a number of US sourced tools on a 110volt site transformer and I can't see much difference (they don't appear to run hotter BTW) with one very important caveat, namely that the output from a genny is often all over the place in terms of voltage so if you run tools with electronic speed control (e.g. Festool OF2200 router, etc) they may refuse to run on the genny output or you could end up damaging's the tool. This particularly applies to small gennys and battery chargers - a potentially expensive combination
"The person who never made a mistake, never made anything" - Albert Einstein

"I too will something make, And joy in the making" - Robert Bridges, 1844~1930

"The fundamental cause of the trouble is that in the modern world the stupid are cocksure while the intelligent are full of doubt.” - Bertrand Russell from The Triumph of Stupidity", 1933
User avatar
kellys_eye
Senior Member
Posts: 12309
Joined: Mon Mar 15, 2010 11:49 pm
Location: Oban
Has thanked: 357 times
Been thanked: 1790 times

Re: 110v USA tools with petrol generator

Post by kellys_eye »

The additional heat comes from the eddy current losses in the motor laminations that are designed for 60Hz rather than 50Hz - barely noticeable in most cases and certainly negligible in items run for short periods. It's probably more specific to household items (hi-fi's and the like) that may be run constantly.

The comment on poor voltage regulation is well made - something I forgot to mention :oops: - and the smaller, non-regulated, gennies also have 'dirty' outputs (i.e. not true sinewave) which is definitely troublesome for 'electronic' tools and chargers etc.
Don't take it personally......
D4np
Newly registered Member
Posts: 89
Joined: Sun Mar 05, 2017 8:23 pm
Has thanked: 8 times
Been thanked: 1 time

Re: 110v USA tools with petrol generator

Post by D4np »

Thank you both for your replies - I brought a 110 plug , swapped it over and it works . Hooray ! I have run both 1/2 and 1/4 inch routers off of my generator for years with no problems . It's a good generator - pramec I believe it's called . The wires inside the US lead were different colours (black ,green and white ) but after a bit of googling it was clear what went where . The tool I have put the uk plug on is a chop saw so won't be running constantly for long periods

Thank you all for your replies and to kel for giving me the confidence to give it a go haha


Sent from my iPhone using Tapatalk
Dave54
Senior Member
Posts: 5063
Joined: Wed Feb 25, 2015 7:20 pm
Has thanked: 1300 times
Been thanked: 1175 times

Re: 110v USA tools with petrol generator

Post by Dave54 »

kellys_eye wrote:The additional heat comes from the eddy current losses in the motor laminations that are designed for 60Hz rather than 50Hz - barely noticeable in most cases and certainly negligible in items run for short periods. It's probably more specific to household items (hi-fi's and the like) that may be run constantly.

The comment on poor voltage regulation is well made - something I forgot to mention :oops: - and the smaller, non-regulated, gennies also have 'dirty' outputs (i.e. not true sinewave) which is definitely troublesome for 'electronic' tools and chargers etc.
A lot of power tools are universal motors, so the frequency isn't that important is it? It's more to do with the commutation speed than the supply I'd have thought. The voltage matters for sure.
Long time since I did motor theory though. I wonder if the lam packs are any different for the different frequencies.?
D4np
Newly registered Member
Posts: 89
Joined: Sun Mar 05, 2017 8:23 pm
Has thanked: 8 times
Been thanked: 1 time

Re: 110v USA tools with petrol generator

Post by D4np »

Job and Knock wrote:I run a number of US sourced tools on a 110volt site transformer and I can't see much difference (they don't appear to run hotter BTW) with one very important caveat, namely that the output from a genny is often all over the place in terms of voltage so if you run tools with electronic speed control (e.g. Festool OF2200 router, etc) they may refuse to run on the genny output or you could end up damaging's the tool. This particularly applies to small gennys and battery chargers - a potentially expensive combination
Ah that's would explain why a friend of mine couldn't use his festool chop saw off of a genny



Sent from my iPhone using Tapatalk
User avatar
Job and Knock
Old School Chippie
Posts: 6667
Joined: Mon Sep 12, 2011 3:27 pm
Has thanked: 742 times
Been thanked: 1573 times

Re: 110v USA tools with petrol generator

Post by Job and Knock »

All I'll say is that I try to avoid cheap little sites which only have little petrol generators. The big diesel sets on some the jobs I do, which kick out a healthy 100kVA or more, generally have a big enough flywheel (and have been sized by an engineer) that you just don't see voltage fluctuations, brown-outs, surges, dropped cycles, etc As for stuff like my various Festool kit (OF2200e, TS55, Kapex, Domino, etc) as well as some of my other stuff withe electronics inside - they aren't allowed near anywhere that can't be bothered to give me a clean, reliable power supply. Fortunately these days (for me) there's no lugging site trannies around until the finishing stages because any decent main contractor worth his salt will have a 3-phase armoured cable coming into the building with a distribution box and one or more 110 volt transformers (the 10kVA type) on each floor for the majpority of the job. In any case on those sites 230 volt is never available until the finishing stages - when lugging a 5kVA box around becomes a pain (but easier to bear if you have a folding sack truck)

I suppose the moral is: don't let anyone push you into using expensive gear which requires a good quality power supply on some cheap, nasty, underpowered piece of tat (i.e. a petrol genny, any petrol genny)
"The person who never made a mistake, never made anything" - Albert Einstein

"I too will something make, And joy in the making" - Robert Bridges, 1844~1930

"The fundamental cause of the trouble is that in the modern world the stupid are cocksure while the intelligent are full of doubt.” - Bertrand Russell from The Triumph of Stupidity", 1933
D4np
Newly registered Member
Posts: 89
Joined: Sun Mar 05, 2017 8:23 pm
Has thanked: 8 times
Been thanked: 1 time

Re: 110v USA tools with petrol generator

Post by D4np »

Job and Knock wrote:All I'll say is that I try to avoid cheap little sites which only have little petrol generators. The big diesel sets on some the jobs I do, which kick out a healthy 100kVA or more, generally have a big enough flywheel (and have been sized by an engineer) that you just don't see voltage fluctuations, brown-outs, surges, dropped cycles, etc As for stuff like my various Festool kit (OF2200e, TS55, Kapex, Domino, etc) as well as some of my other stuff withe electronics inside - they aren't allowed near anywhere that can't be bothered to give me a clean, reliable power supply. Fortunately these days (for me) there's no lugging site trannies around until the finishing stages because any decent main contractor worth his salt will have a 3-phase armoured cable coming into the building with a distribution box and one or more 110 volt transformers (the 10kVA type) on each floor for the majpority of the job. In any case on those sites 230 volt is never available until the finishing stages - when lugging a 5kVA box around becomes a pain (but easier to bear if you have a folding sack truck)

I suppose the moral is: don't let anyone push you into using expensive gear which requires a good quality power supply on some cheap, nasty, underpowered piece of tat (i.e. a petrol genny, any petrol genny)
I hear what your saying, I presume your not self employed and on day rate / on the books ? I don't know any sub contractor who would refuse getting tools out because there isn't "clean" power .


Sent from my iPhone using Tapatalk
User avatar
Job and Knock
Old School Chippie
Posts: 6667
Joined: Mon Sep 12, 2011 3:27 pm
Has thanked: 742 times
Been thanked: 1573 times

Re: 110v USA tools with petrol generator

Post by Job and Knock »

D4np wrote:I hear what your saying, I presume your not self employed and on day rate / on the books ? I don't know any sub contractor who would refuse getting tools out because there isn't "clean" power .
Self-employed since 1978. If I need a specialised piece of it that requires a clean power supply (e.g a Rotex for Corian) then the main contractor either supplies it or I don't bring the it. Period. I'm not wrecking a £1500 Kapex because the guy who wants me to use it is a cheapskate moron - he'll have to be satisfied with lesser tools, or hire the gear himself. As it happens I find it's only the smaller firms who don't want to spend the money on stuff like power or lighting
"The person who never made a mistake, never made anything" - Albert Einstein

"I too will something make, And joy in the making" - Robert Bridges, 1844~1930

"The fundamental cause of the trouble is that in the modern world the stupid are cocksure while the intelligent are full of doubt.” - Bertrand Russell from The Triumph of Stupidity", 1933
D4np
Newly registered Member
Posts: 89
Joined: Sun Mar 05, 2017 8:23 pm
Has thanked: 8 times
Been thanked: 1 time

Re: 110v USA tools with petrol generator

Post by D4np »

Job and Knock wrote:
D4np wrote:I hear what your saying, I presume your not self employed and on day rate / on the books ? I don't know any sub contractor who would refuse getting tools out because there isn't "clean" power .
Self-employed since 1978. If I need a specialised piece of it that requires a clean power supply (e.g a Rotex for Corian) then the main contractor either supplies it or I don't bring the it. Period. I'm not wrecking a £1500 Kapex because the guy who wants me to use it is a cheapskate moron - he'll have to be satisfied with lesser tools, or hire the gear himself. As it happens I find it's only the smaller firms who don't want to spend the money on stuff like power or lighting
Each to there own mate


Sent from my iPhone using Tapatalk