Shower timer switch

All your electrical questions regarding electrics from within the United Kingdom

Moderator: Moderators

Post Reply
Hinton Heating
Gas/Heating Expert
Posts: 4382
Joined: Mon Jan 16, 2006 9:40 pm
Location: Bournemouth
Has thanked: 0
Been thanked: 9 times

Shower timer switch

Post by Hinton Heating »

I have been asked by a customer to replace his old 7.2kw shower.

It currently has either 4mm or 6mm braided cable supplying it.

I was thinking of putting in a 9kw shower.

what size cable would be recommended, is the old one ok?

Also the customer wants one remote timed switch, that is just switched on, then cuts the power off to the shower after say 20mins.

I can only see 16amp versions, but I guess a 9kw is going to draw more than that?

any thoughts?
Hinton Heating
Gas/Heating Expert
Posts: 4382
Joined: Mon Jan 16, 2006 9:40 pm
Location: Bournemouth
Has thanked: 0
Been thanked: 9 times

Post by Hinton Heating »

any thoughts?
User avatar
sparkydude
Senior Member
Posts: 2253
Joined: Sat Aug 13, 2005 7:11 pm
Location: Staffordshire
Has thanked: 2 times
Been thanked: 149 times

Post by sparkydude »

I would doubt that the existing cable is upto the job Hinton, but it depends on length of run, if it goes through insulation or is enclosed by trunking or conduit. It might be better to change the cable for a new 10.00mm cable and dont forget you will have to upgrade the bonding in the bathroom if there is nothing present at the moment. As for the timer , its possible but would be a bit expensive, using a boost timer, contactor and other bits . Why does he want the shower timed??


Nick
If it isnt broke dont bloody touch it until it bloody well is and if it is broke then make drawing of the connections before you remove the broken one and replace with a new one LoL
Hinton Heating
Gas/Heating Expert
Posts: 4382
Joined: Mon Jan 16, 2006 9:40 pm
Location: Bournemouth
Has thanked: 0
Been thanked: 9 times

Post by Hinton Heating »

Its for his elderly mother, who is forgetful, hes worried she'll leave it running all night.

if the timer cust off the power after say 30 mins, then it'll stop the water too.
User avatar
sparkydude
Senior Member
Posts: 2253
Joined: Sat Aug 13, 2005 7:11 pm
Location: Staffordshire
Has thanked: 2 times
Been thanked: 149 times

Post by sparkydude »

Oh right, yes it is possible to do . Is the airing cupboard near to the proposed shower location? as you will need somewhere to pick up a low amperage feed, from the immersion supply would be ideal. Basically you need a contactor rated to your shower load. All a contactor is like an industrial relay. You would use the boost switch or timer you spoke of earlier, but instead of the shower being controlled directly , you would use the timers output to control the A1 and A2 terminals on the contactor, theis will energise the coil of the contactor. The shower feed would connect in one side of the contactor and the other side of the contactor for the load. Basically the low wattage supply from the timer energises the coil in the contactor pulling the contacts in and letting the electricity through.

Hope this helps

Nick
If it isnt broke dont bloody touch it until it bloody well is and if it is broke then make drawing of the connections before you remove the broken one and replace with a new one LoL
Hinton Heating
Gas/Heating Expert
Posts: 4382
Joined: Mon Jan 16, 2006 9:40 pm
Location: Bournemouth
Has thanked: 0
Been thanked: 9 times

Post by Hinton Heating »

thats what I was thinking... will probably suggest a spring light switch like they use in the hallways of flats, which can connect to the contactor.

Its a bungalow, so its not so bad. I'm going to pass it to a spark, as its beyond my scope, and I'm a bit worried about the cable sizing, and no idea about sourcing a contactor box! 8-)
User avatar
sparkydude
Senior Member
Posts: 2253
Joined: Sat Aug 13, 2005 7:11 pm
Location: Staffordshire
Has thanked: 2 times
Been thanked: 149 times

Post by sparkydude »

Its not too hard, if you feel confident about it then go for it. Only problem is that Part P thing LoL You wont be able t o use a push to make switch without adding a timer relay to it as well , to keep the contacts on the contactor closed. If you want any help sizing the shower cable just shout as well as any help with connections etc,


Nick
If it isnt broke dont bloody touch it until it bloody well is and if it is broke then make drawing of the connections before you remove the broken one and replace with a new one LoL
Hinton Heating
Gas/Heating Expert
Posts: 4382
Joined: Mon Jan 16, 2006 9:40 pm
Location: Bournemouth
Has thanked: 0
Been thanked: 9 times

Post by Hinton Heating »

Cheers for the offer... As you say the Part P will cause an issue, as altering a circuit in a bathroom.

I'd rather let the spark do it, to be honest, I understand how a relay works, and the principles of switching a high current circuit, by using a "relay" and a low curent timer switch.
User avatar
Jaeger_S2k
Pro Handyman
Posts: 3423
Joined: Sun Nov 19, 2006 4:31 pm
Location: North West, England, United Kingdom
Has thanked: 21 times
Been thanked: 27 times

Post by Jaeger_S2k »

You could always use a second hand 3 way motorised valve switch? :lol:
Jaeger.
Senior Member doesn't mean I'm OLD!
Post Reply

Return to “Electric Forum UK”