Earthing
All your electrical questions regarding electrics from within the United Kingdom
Moderator: Moderators
Earthing
I have just moved into a new house. Underneath the sink in the kitchen I have what looks like some earth wires that are not attached to anything. It appears that they may have removed their washing machine in a hurry.
I know that these wires used to have to be attached to something metal usually the pipework, but not sure that is the case with plastic pipework etc these days. Am I in danger what should I attach the wires too.
help please for a diy doughnut.
regards
I know that these wires used to have to be attached to something metal usually the pipework, but not sure that is the case with plastic pipework etc these days. Am I in danger what should I attach the wires too.
help please for a diy doughnut.
regards
TH
- sparkydude
- Senior Member
- Posts: 2253
- Joined: Sat Aug 13, 2005 7:11 pm
- Location: Staffordshire
- Has thanked: 2 times
- Been thanked: 149 times
Post by sparkydude »
They are probably cross bonding cables which would be connected via an earth clamp to the copper hot and cold water pipes. if yours are plastic then these do not need to be connected to anything. A picture would be helpful if you can .
Nick
Nick
If it isnt broke dont bloody touch it until it bloody well is and if it is broke then make drawing of the connections before you remove the broken one and replace with a new one LoL
sparkydude
TH
TH
- ultimatehandyman
- Site Admin
- Posts: 24426
- Joined: Sat Jul 16, 2005 7:06 pm
- Location: Darwen, Lancashire
- Has thanked: 1012 times
- Been thanked: 918 times
Post by ultimatehandyman »
I have enlarged that picture and I think that the wires are both Green, is this correct?
They look like old bonding wires from the sink pipes, like sparkydude says!
There is no requirement to bond the kitchen pipes anymore, apart from the main bond from the incoming water main to the main earthing terminal.
They look like old bonding wires from the sink pipes, like sparkydude says!
There is no requirement to bond the kitchen pipes anymore, apart from the main bond from the incoming water main to the main earthing terminal.
ultimatehandyman
- sparkydude
- Senior Member
- Posts: 2253
- Joined: Sat Aug 13, 2005 7:11 pm
- Location: Staffordshire
- Has thanked: 2 times
- Been thanked: 149 times
Post by sparkydude »
Can you see where both ends of the cable go? you say one goes to the radiator pipe, does the other appear from the wall somewhere behind the sink . It looks like they need to be attached to your hot and cold copper pipes with the use of earth clamps.
Nick
Nick
If it isnt broke dont bloody touch it until it bloody well is and if it is broke then make drawing of the connections before you remove the broken one and replace with a new one LoL
sparkydude
- sparkydude
- Senior Member
- Posts: 2253
- Joined: Sat Aug 13, 2005 7:11 pm
- Location: Staffordshire
- Has thanked: 2 times
- Been thanked: 149 times
Post by sparkydude »
Currently there is still a requirement to bond the pipes in a kitchen, but not the kitchen sink. All you have to make sure is that the cable is a continual loop between the hot, cold and radiator pipes.
Nick
Nick
If it isnt broke dont bloody touch it until it bloody well is and if it is broke then make drawing of the connections before you remove the broken one and replace with a new one LoL
sparkydude
-
- Senior Member
- Posts: 986
- Joined: Sat Feb 24, 2007 11:50 am
- Location: Cotswolds
- Has thanked: 0
- Been thanked: 0
Sparky,
Can you go into a bit more detail about the bonding requirements?
Currently I've got the hot and cold and gas pipes all individually earthed back to the main earth block. This then goes to the earth spike and fuse box.
I've not got anything to the rad pipes. Do I need to bond every rad pipe or just the supply / return? Hoping it's just the supply because they are all one big lump of copper but best to check
Thanks
Can you go into a bit more detail about the bonding requirements?
Currently I've got the hot and cold and gas pipes all individually earthed back to the main earth block. This then goes to the earth spike and fuse box.
I've not got anything to the rad pipes. Do I need to bond every rad pipe or just the supply / return? Hoping it's just the supply because they are all one big lump of copper but best to check
Thanks
Slugster
TH
- ultimatehandyman
- Site Admin
- Posts: 24426
- Joined: Sat Jul 16, 2005 7:06 pm
- Location: Darwen, Lancashire
- Has thanked: 1012 times
- Been thanked: 918 times
Post by ultimatehandyman »
As sparkydude says you can re-attach them to the hot and cold copper pipes- http://www.ultimatehandyman.co.uk/earth_clamp.htm
ultimatehandyman
- sparkydude
- Senior Member
- Posts: 2253
- Joined: Sat Aug 13, 2005 7:11 pm
- Location: Staffordshire
- Has thanked: 2 times
- Been thanked: 149 times
Post by sparkydude »
Basically the requirements for earthing in general in domestic properties are as follows:-
Main earth from suppliers facility to fuseboard or MET (main earth terminal) 10 or 16mm dependant upon main tails size
Main equipotential bond to gas,oil,water,structural steel and any other metallic incoming services 10mm to MET or fuseboard
cross bonding cable in airing cupboard or at combi boiler links all pipes at this point with earth clamps and cable 4mm
cross bonding cables at kitchen sinks 4mm and link hot and cold.
Cross bonding in bathrooms, to link , hot and cold, electric shower earth if fitted, metallic light fitting on ceiling, shaver point and radiator
all in one circuit of 4mm earth.
hope this helps slugster
Nick
Main earth from suppliers facility to fuseboard or MET (main earth terminal) 10 or 16mm dependant upon main tails size
Main equipotential bond to gas,oil,water,structural steel and any other metallic incoming services 10mm to MET or fuseboard
cross bonding cable in airing cupboard or at combi boiler links all pipes at this point with earth clamps and cable 4mm
cross bonding cables at kitchen sinks 4mm and link hot and cold.
Cross bonding in bathrooms, to link , hot and cold, electric shower earth if fitted, metallic light fitting on ceiling, shaver point and radiator
all in one circuit of 4mm earth.
hope this helps slugster
Nick
If it isnt broke dont bloody touch it until it bloody well is and if it is broke then make drawing of the connections before you remove the broken one and replace with a new one LoL
sparkydude
- sparkydude
- Senior Member
- Posts: 2253
- Joined: Sat Aug 13, 2005 7:11 pm
- Location: Staffordshire
- Has thanked: 2 times
- Been thanked: 149 times
Post by sparkydude »
As for your problem TH , as long as your bonding circuit covers hot ,cold and as yours is already done , the radiator then you have done what you need to do. There is no requirement to bond radiators in other parts of the house other than in a bathroom. As for why you have two earths coming from your radiator, its a mystery. If they come from the same pipe and earth clamp then perhaps they just had it so you had one earth cable in each earth clamp, on hot and cold.
any chance of a pic of the radiator connection ?
Nick
any chance of a pic of the radiator connection ?
Nick
If it isnt broke dont bloody touch it until it bloody well is and if it is broke then make drawing of the connections before you remove the broken one and replace with a new one LoL
sparkydude
- ultimatehandyman
- Site Admin
- Posts: 24426
- Joined: Sat Jul 16, 2005 7:06 pm
- Location: Darwen, Lancashire
- Has thanked: 1012 times
- Been thanked: 918 times
Post by ultimatehandyman »
sparkydude wrote:Currently there is still a requirement to bond the pipes in a kitchen, but not the kitchen sink. All you have to make sure is that the cable is a continual loop between the hot, cold and radiator pipes.
Nick

I'm confused about this!
In my on site guide it says -
There is no specific requirement in BS 7671 to supplementary bond to the following-
Kitchen pipes, sinks or draining boards.
Metal furniture in Kitchens.
Metal pipes and wash hand basins in domestic locations other than bathrooms.
I don't want to appear to be one of those argumentative tossers that quote this reg and that reg

ultimatehandyman
- sparkydude
- Senior Member
- Posts: 2253
- Joined: Sat Aug 13, 2005 7:11 pm
- Location: Staffordshire
- Has thanked: 2 times
- Been thanked: 149 times
Post by sparkydude »
Well i know that in the new 17th edition they are removing the need to bond sinks and a certain amount of cross bonding. But i have always had it drummed into me that you cross bond pipes at kitchen sinks unless they have plastic supply pipes.
Nick
Nick
If it isnt broke dont bloody touch it until it bloody well is and if it is broke then make drawing of the connections before you remove the broken one and replace with a new one LoL
sparkydude
- ultimatehandyman
- Site Admin
- Posts: 24426
- Joined: Sat Jul 16, 2005 7:06 pm
- Location: Darwen, Lancashire
- Has thanked: 1012 times
- Been thanked: 918 times
Post by ultimatehandyman »
I totally agree with what you are saying, I still bond kitchen pipes when I install a new kitchensparkydude wrote:Well i know that in the new 17th edition they are removing the need to bond sinks and a certain amount of cross bonding. But i have always had it drummed into me that you cross bond pipes at kitchen sinks unless they have plastic supply pipes.
Nick

Do you know when the 17th edition is supposed to be coming out?
ultimatehandyman
Jump to
- Ultimate Handyman DIY forum
- ↳ Welcome to the Ultimate Handyman DIY Forum
- WELCOME
- ↳ WELCOME
- ↳ About the forums
- UltimateHandyman Discounts
- ↳ Ultimatehandyman Discounts
- ULTIMATE HANDYMAN COMPETITIONS
- ↳ UHM Forum competitions
- SHOW CASE- A place to show us your work
- ↳ Show Case Gallery
- ↳ Rogues Gallery
- TOOL FORUM
- ↳ Power Tool Reviews
- ↳ Bosch
- ↳ budget power tools
- ↳ Dewalt
- ↳ Festool
- ↳ Hikoki/Hitachi
- ↳ Makita
- ↳ Metabo
- ↳ Milwaukee
- ↳ Ryobi
- ↳ Tool Talk
- ↳ Bargain Tools
- ↳ Hand tool reviews
- ↳ Power Tool Manuals
- ↳ Bosch
- ↳ Dolmar
- ↳ ELEKTRA BECKUM
- ↳ Hitachi
- ↳ Husqvarna
- ↳ Jonsered
- ↳ Makita
- ↳ Stihl
- Other DIY
- ↳ Computers
- ↳ communications and broadband
- ↳ Gardeners World
- ↳ Money Saving
- ↳ Vehicle maintenance & Repair
- ↳ Energy Saving
- DIY Forum/Home improvement
- ↳ General DIY forum
- ↳ Acrylic Forum
- ↳ DIY Disasters
- ↳ Stoves
- ↳ Building Forum
- ↳ Carpentry/Joinery Forum
- ↳ Kitchen Fitting
- ↳ Damp Proofing and Remedial problems
- ↳ Electric Forum UK
- ↳ Lighting
- ↳ Alarm Manuals
- ↳ Painting & Decorating Forum
- ↳ Plastering Forum
- ↳ Plumbing Forum
- ↳ Central Heating & Boilers
- ↳ Boiler Manuals
- ↳ Alpha
- ↳ Ariston
- ↳ ATAG
- ↳ Atmos
- ↳ Baxi
- ↳ Biasi
- ↳ Broag
- ↳ Chaffoteux
- ↳ Ferroli
- ↳ Glow-worm
- ↳ Halstead
- ↳ Ideal
- ↳ Intergas
- ↳ Keston
- ↳ Myson
- ↳ Potterton
- ↳ Protherm
- ↳ Ravenheat
- ↳ Saunier Duval
- ↳ Sime
- ↳ Thorn
- ↳ Vaillant
- ↳ Viessmann
- ↳ Vokera
- ↳ warmflow
- ↳ Worcester Bosch
- ↳ Shower Manuals
- ↳ Tiling Forum
- ↳ Metalworking Forum
- General
- ↳ The Lounge
- ↳ The games corner
- ↳ The Grumpy corner
- ↳ The Sport corner
- ↳ The Cookery corner
- ↳ The Music Corner
- ↳ BUY - SELL - FREE