Fused Spur

Post by Hinton Heating »

I recently installed a cylinder & boiler. I asked the customer to get a spark in to supply 2 fused outlets in the airing cupboard.

He ran a cable from the old immersion spur, to the two new patress boxes, which he joined in series from the same cable, effectivily running two outlets from the one cable, I thought you could only have one outlet on each spur?

can a spark confirm this, or say what would be the correct way of supplying two fused oulets in an airing cupboard?
User avatar
ultimatehandyman
Site Admin
Posts: 24426
Joined: Sat Jul 16, 2005 7:06 pm
Location: Darwen, Lancashire
Has thanked: 1012 times
Been thanked: 918 times

Post by ultimatehandyman »

I'm not a spark, so can't confirm it- But as long as the cable is the correct thickness then it is quite acceptable I believe :wink:
User avatar
sparkydude
Senior Member
Posts: 2253
Joined: Sat Aug 13, 2005 7:11 pm
Location: Staffordshire
Has thanked: 2 times
Been thanked: 149 times

Post by sparkydude »

Morning Hinton, just got in from a night shift so checking in to see whats happening. Are you saying he has just used the circuit for the immersion to supply your two outlets? if so than as long as the immersion circuit is a radial, ie on its own feed from the fuse board , then it can feed as many outlets as you like. If however the immersion is a spur from the ring main already , then it cannot be used to supply two outlets, as the second would in effect be a spur from a spur which is not acceptable and contravenes the wiring regulations.

Off to beddy byes now i feel , 14 hour shift is enough for me.

Night Night



:grin: :grin:

Nick
If it isnt broke dont bloody touch it until it bloody well is and if it is broke then make drawing of the connections before you remove the broken one and replace with a new one LoL
Hinton Heating
Gas/Heating Expert
Posts: 4382
Joined: Mon Jan 16, 2006 9:40 pm
Location: Bournemouth
Has thanked: 0
Been thanked: 9 times

Post by Hinton Heating »

I think its a radial from diectly from the CU... I knew there was an issue with spuring a spur from a spur!