spur from cooker socket?
All your electrical questions regarding electrics from within the United Kingdom
Moderator: Moderators
- Dean123
- Newly registered Member
- Posts: 17
- Joined: Thu Mar 15, 2007 1:49 pm
- Location: Cheshire
- Has thanked: 0
- Been thanked: 0
spur from cooker socket?
I was busily smashing plaster of our bedroom the other day wasnt quite sure where the cables would run in our walls so switched the power to all the sockets off.
my wife came up with a hot cup of tea that she had made for me! a little confused as to how she had done this with no electricity i found that a random double socket (which our kettle uses) seems to be connected to the oven socket.
is this safe?
ive stoped using it for the time being
thanks
my wife came up with a hot cup of tea that she had made for me! a little confused as to how she had done this with no electricity i found that a random double socket (which our kettle uses) seems to be connected to the oven socket.
is this safe?
ive stoped using it for the time being
thanks
Dean123
-
- Senior Member
- Posts: 17626
- Joined: Fri Jan 20, 2006 5:51 pm
- Location: Essex
- Has thanked: 833 times
- Been thanked: 3636 times
Post by dewaltdisney »
It is usual to have a cooker isolator switch with a socket in a dual plate. Is this what you mean??
DWD
DWD
dewaltdisney
skiking
-
- plumbing and property
- Posts: 202
- Joined: Mon Jan 16, 2006 8:25 pm
- Location: Stockport
- Has thanked: 0
- Been thanked: 0
Post by BobProperty »
I'm assuming what skiking said, there's a double socket spurred off the cooker point. Now, I'm not an electrician, but I think if you do this, there should be a fuse (13a?) protecting the socket otherwise you have 2.5mm cable and a socket designed to take no more than 13a off a 6mm(?) cable protected by say a 45a fuse. That last bit being the big problem, anything wrong at the socket needs 50a-ish to blow the fuse.
Treat everyone like they are a rich distant relative, in whose will you'd like to be remembered.
BobProperty
- sparkydude
- Senior Member
- Posts: 2253
- Joined: Sat Aug 13, 2005 7:11 pm
- Location: Staffordshire
- Has thanked: 2 times
- Been thanked: 149 times
Post by sparkydude »
Unless the socket is incorporated into the cooker switch plate then this is a potentially dangerous situation . The socket should be run off the ring main of the house , and most definitley not off the cooker circuit. Cooker circuits are designed to feed an oven and hob , and not anything else.
Nick
Nick
If it isnt broke dont bloody touch it until it bloody well is and if it is broke then make drawing of the connections before you remove the broken one and replace with a new one LoL
sparkydude
- Dean123
- Newly registered Member
- Posts: 17
- Joined: Thu Mar 15, 2007 1:49 pm
- Location: Cheshire
- Has thanked: 0
- Been thanked: 0
sorry probably didnt give the best description to begin with.
Yes it appears that there is a double socket which is spured from the oven socket.
presumably if i just dont use this then that will be safe? the kitchen is reasonable functional (apart from some dodgy electrics) and id rather not start removing things without finishing what i have started upstairs.
thanks for your replys
Yes it appears that there is a double socket which is spured from the oven socket.
presumably if i just dont use this then that will be safe? the kitchen is reasonable functional (apart from some dodgy electrics) and id rather not start removing things without finishing what i have started upstairs.
thanks for your replys
Dean123
- Rich-Ando
- Pro Tradesman
- Posts: 7138
- Joined: Sat Mar 24, 2007 12:24 pm
- Location: Spondon, Derby
- Has thanked: 135 times
- Been thanked: 304 times
as sparkydude stated m8. you should not have a socket spurred off the cooker circuit.
a cooker circuit will be backed by a 30amp fuse/MCB and the cable will be 6mm which can easily handle the current. if somebody has spurred a single 2.5mm cable from the cooker circuit in theory you could overload the 2.5mm cable (would have to be an extreme and highly unlikely)
you should disconnect that socket from the cooker circuit as people that tend to do this make a bad job of the connections when they fit a 2.5mm cable with a 6mm cable as one is far smaller than the other they do not clamp properly together in the terminal and usually are loose.
a typical example of bad workmanship that gets hidden when somebody buys a house because no surveyor inspects electrical work properly.
a cooker circuit will be backed by a 30amp fuse/MCB and the cable will be 6mm which can easily handle the current. if somebody has spurred a single 2.5mm cable from the cooker circuit in theory you could overload the 2.5mm cable (would have to be an extreme and highly unlikely)
you should disconnect that socket from the cooker circuit as people that tend to do this make a bad job of the connections when they fit a 2.5mm cable with a 6mm cable as one is far smaller than the other they do not clamp properly together in the terminal and usually are loose.
a typical example of bad workmanship that gets hidden when somebody buys a house because no surveyor inspects electrical work properly.
Rich-Ando
-
- Senior Member
- Posts: 268
- Joined: Wed Feb 28, 2007 12:17 pm
- Location: Newcastle T&W
- Has thanked: 0
- Been thanked: 1 time
Post by uncle buck »
Whilst on this topic can someone explain why an incorporated socket is still allowed?
Fair enough when a 30 amp fuse was used to feed cooker circuits as this is the same value as a ring main….but cooker circuits are now quite often 45 amps.
Fair enough when a 30 amp fuse was used to feed cooker circuits as this is the same value as a ring main….but cooker circuits are now quite often 45 amps.

uncle buck
-
- Gas/Heating Expert
- Posts: 4382
- Joined: Mon Jan 16, 2006 9:40 pm
- Location: Bournemouth
- Has thanked: 0
- Been thanked: 9 times
Post by Hinton Heating »
I would guess because the socket is built in, its ok, its the fact that spuring off in 2.5 mm cable will mean the cable could melt/arc before the 45amp protection device (fuse) blows.
Hinton Heating
- sparkydude
- Senior Member
- Posts: 2253
- Joined: Sat Aug 13, 2005 7:11 pm
- Location: Staffordshire
- Has thanked: 2 times
- Been thanked: 149 times
Post by sparkydude »
A cooker switch with socket is allowed because the maximum assumed demand from the socket outlet is 13A , and by the regulations, there is diversity to be applied to cooking appliances as you are not going to be using all the rings all the time so never loading the circuit to its maximum.
Nick
Nick
If it isnt broke dont bloody touch it until it bloody well is and if it is broke then make drawing of the connections before you remove the broken one and replace with a new one LoL
sparkydude
Jump to
- Ultimate Handyman DIY forum
- ↳ Welcome to the Ultimate Handyman DIY Forum
- WELCOME
- ↳ WELCOME
- ↳ About the forums
- UltimateHandyman Discounts
- ↳ Ultimatehandyman Discounts
- ULTIMATE HANDYMAN COMPETITIONS
- ↳ UHM Forum competitions
- SHOW CASE- A place to show us your work
- ↳ Show Case Gallery
- ↳ Rogues Gallery
- TOOL FORUM
- ↳ Power Tool Reviews
- ↳ Bosch
- ↳ budget power tools
- ↳ Dewalt
- ↳ Festool
- ↳ Hikoki/Hitachi
- ↳ Makita
- ↳ Metabo
- ↳ Milwaukee
- ↳ Ryobi
- ↳ Tool Talk
- ↳ Bargain Tools
- ↳ Hand tool reviews
- ↳ Power Tool Manuals
- ↳ Bosch
- ↳ Dolmar
- ↳ ELEKTRA BECKUM
- ↳ Hitachi
- ↳ Husqvarna
- ↳ Jonsered
- ↳ Makita
- ↳ Stihl
- Other DIY
- ↳ Computers
- ↳ communications and broadband
- ↳ Gardeners World
- ↳ Money Saving
- ↳ Vehicle maintenance & Repair
- ↳ Energy Saving
- DIY Forum/Home improvement
- ↳ General DIY forum
- ↳ Acrylic Forum
- ↳ DIY Disasters
- ↳ Stoves
- ↳ Building Forum
- ↳ Carpentry/Joinery Forum
- ↳ Kitchen Fitting
- ↳ Damp Proofing and Remedial problems
- ↳ Electric Forum UK
- ↳ Lighting
- ↳ Alarm Manuals
- ↳ Painting & Decorating Forum
- ↳ Plastering Forum
- ↳ Plumbing Forum
- ↳ Central Heating & Boilers
- ↳ Boiler Manuals
- ↳ Alpha
- ↳ Ariston
- ↳ ATAG
- ↳ Atmos
- ↳ Baxi
- ↳ Biasi
- ↳ Broag
- ↳ Chaffoteux
- ↳ Ferroli
- ↳ Glow-worm
- ↳ Halstead
- ↳ Ideal
- ↳ Intergas
- ↳ Keston
- ↳ Myson
- ↳ Potterton
- ↳ Protherm
- ↳ Ravenheat
- ↳ Saunier Duval
- ↳ Sime
- ↳ Thorn
- ↳ Vaillant
- ↳ Viessmann
- ↳ Vokera
- ↳ warmflow
- ↳ Worcester Bosch
- ↳ Shower Manuals
- ↳ Tiling Forum
- ↳ Metalworking Forum
- General
- ↳ The Lounge
- ↳ The games corner
- ↳ The Grumpy corner
- ↳ The Sport corner
- ↳ The Cookery corner
- ↳ The Music Corner
- ↳ BUY - SELL - FREE