16mm2 conductor terminals

Post by bleicker »

Hi guys, I'm trying to find a good quality terminal to connect 16mm2 conductors. The ones I have found are those white plastic terminal blocks that just by looking at it may spark and catch fire. I'm used to wago connectors which are a wonder but I can't find anything above 6mm2. What do you guys use/recommend?

I'm getting a SWA cable across the garden, but inside the house I'm using T&E 16mm2, so hence the reason to connect the 2 together :)
User avatar
Someone-Else
Senior Member
Posts: 14628
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 47 times
Been thanked: 2575 times

16mm2 conductor terminals

Post by Someone-Else »

How much will the load be?
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
User avatar
kellys_eye
Senior Member
Posts: 12309
Joined: Mon Mar 15, 2010 11:49 pm
Location: Oban
Has thanked: 357 times
Been thanked: 1790 times

16mm2 conductor terminals

Post by kellys_eye »

I'd get a small Consumer Unit and fit either a 2-pole isolator or an MCB (RCD) as you'll need one 'somewhere' anyway.
These users thanked the author kellys_eye for the post:
LadySpark (Wed Nov 17, 2021 5:30 am)
Rating: 7.14%
Don't take it personally......
Neelix
Senior Member
Posts: 1311
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 117 times
Been thanked: 214 times

16mm2 conductor terminals

Post by Neelix »

Replace the 2 bits of cable with 1 new one?
User avatar
Someone-Else
Senior Member
Posts: 14628
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 47 times
Been thanked: 2575 times

16mm2 conductor terminals

Post by Someone-Else »

Neelix wrote: Mon Nov 15, 2021 5:23 pmReplace the 2 bits of cable with 1 new one?
Looks like it is a new install
bleicker wrote: Mon Nov 15, 2021 5:07 pmI'm getting a SWA cable across the garden, but inside the house I'm using T&E 16mm2
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
User avatar
Someone-Else
Senior Member
Posts: 14628
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 47 times
Been thanked: 2575 times

16mm2 conductor terminals

Post by Someone-Else »

bleicker, why not run the SWA outside to roughly where the consumers unit is, then come through the wall, no joints then.
These users thanked the author Someone-Else for the post:
LadySpark (Fri Nov 19, 2021 4:07 am)
Rating: 7.14%
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
Neelix
Senior Member
Posts: 1311
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 117 times
Been thanked: 214 times

16mm2 conductor terminals

Post by Neelix »

Why 16 mm ?
User avatar
arco_iris
Senior Member
Posts: 2285
Joined: Sat Apr 19, 2014 5:27 pm
Location: SW Wales
Has thanked: 184 times
Been thanked: 535 times

16mm2 conductor terminals

Post by arco_iris »

kellys_eye wrote: Mon Nov 15, 2021 5:19 pm I'd get a small Consumer Unit and fit either a 2-pole isolator or an MCB (RCD) as you'll need one 'somewhere' anyway.
That sounds like a sensible solution, (Wylex REC2S Isolator is neat) an alternative might be three Henley Blocks mounted neatly?

16mm2 is meter tails, isn't it?
Neelix
Senior Member
Posts: 1311
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 117 times
Been thanked: 214 times

16mm2 conductor terminals

Post by Neelix »

arco_iris wrote: Mon Nov 15, 2021 6:49 pm
kellys_eye wrote: Mon Nov 15, 2021 5:19 pm I'd get a small Consumer Unit and fit either a 2-pole isolator or an MCB (RCD) as you'll need one 'somewhere' anyway.
That sounds like a sensible solution, (Wylex REC2S Isolator is neat) an alternative might be three Henley Blocks mounted neatly?

16mm2 is meter tails, isn't it?
Except you can’t terminate SWA into the rec2 with any finesse
Chippo1
Senior Member
Posts: 1073
Joined: Mon Sep 14, 2015 7:36 pm
Location: Cambridgeshire
Has thanked: 10 times
Been thanked: 194 times

16mm2 conductor terminals

Post by Chippo1 »

Galv knockout box , Armour glands with Henley blocks inside or even DIN rail and terminals
These users thanked the author Chippo1 for the post:
LadySpark (Fri Nov 19, 2021 4:08 am)
Rating: 7.14%
bleicker
Newly registered Member
Posts: 57
Joined: Sun Aug 14, 2011 10:02 pm
Has thanked: 11 times
Been thanked: 3 times

16mm2 conductor terminals

Post by bleicker »

Someone-Else wrote: Mon Nov 15, 2021 5:18 pm How much will the load be?
Possibly 7-10Kw to charge a car, but also I'm converting the garage into a home office, so due to the long run and future proof plus I like being overkill with specs, I decided for 16mm
kellys_eye wrote: Mon Nov 15, 2021 5:19 pm I'd get a small Consumer Unit and fit either a 2-pole isolator or an MCB (RCD) as you'll need one 'somewhere' anyway.
The garage will have a small CU with RCBOs already for future expansion if needed.
Neelix wrote: Mon Nov 15, 2021 5:23 pm Replace the 2 bits of cable with 1 new one?
Not sure I follow, one is outdoor armoured cable, the other one is indoor.
Someone-Else wrote: Mon Nov 15, 2021 5:39 pm bleicker, why not run the SWA outside to roughly where the consumers unit is, then come through the wall, no joints then.
I could do that, I've ordered a bit more just in case. The other end will to go the house, but then has 20m of run from the rear side all the way to the consumer unit, so I'll have to join them anyway.
Neelix wrote: Mon Nov 15, 2021 6:05 pmWhy 16 mm ?
Not much difference in price compared to 10mm considering it would be more future proof, plus long run. Everything I do is a bit overkill as I do it myself
arco_iris wrote: Mon Nov 15, 2021 6:49 pm
kellys_eye wrote: Mon Nov 15, 2021 5:19 pm I'd get a small Consumer Unit and fit either a 2-pole isolator or an MCB (RCD) as you'll need one 'somewhere' anyway.
That sounds like a sensible solution, (Wylex REC2S Isolator is neat) an alternative might be three Henley Blocks mounted neatly?

16mm2 is meter tails, isn't it?
heley blocks are quite chunky, I would not be able to fit them inside a small junction box. I think 20-25mm would be tail ends normally.
Chippo1 wrote: Tue Nov 16, 2021 7:42 pm Galv knockout box , Armour glands with Henley blocks inside or even DIN rail and terminals
that seems to be the most interesting way so far, I need to find a box that has DIN rails, I saw the terminals now and they look pretty cool. I want to try that.
Neelix
Senior Member
Posts: 1311
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 117 times
Been thanked: 214 times

16mm2 conductor terminals

Post by Neelix »

Don't forget that new circuits fall under Part P of the building regs .........
User avatar
Someone-Else
Senior Member
Posts: 14628
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 47 times
Been thanked: 2575 times

16mm2 conductor terminals

Post by Someone-Else »

bleicker wrote: Tue Nov 16, 2021 11:40 pmI need to find a box that has DIN rails
You can get any box and add your own DIN rail, then add what ever terminals you like to it.
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
User avatar
kellys_eye
Senior Member
Posts: 12309
Joined: Mon Mar 15, 2010 11:49 pm
Location: Oban
Has thanked: 357 times
Been thanked: 1790 times

16mm2 conductor terminals

Post by kellys_eye »

bleicker wrote: Tue Nov 16, 2021 11:40 pm kellys_eye wrote: ↑Mon Nov 15, 2021 5:19 pm
I'd get a small Consumer Unit and fit either a 2-pole isolator or an MCB (RCD) as you'll need one 'somewhere' anyway.
The garage will have a small CU with RCBOs already for future expansion if needed.
Adding additional isolation afforded by fitting a small Consumer Unit with double-pole breaker indoors (where the two forms of cable meet) isn't problematic (electrically) but offers the necessary cable termination/coupling point in a neat and accessible fashion. This is the equivalent of 'terminal rails' but with the added functionality of isolation of the cable run/out building at a convenient location.

Your decision obviously......